Question: As you can only use / re-identify the white insulation/neutral in an NM cable as the supply to a switch loop per 200.7(C)(2), so then I assume you can not (example) use a 10/2 NM cable, with black / white conductors, for 240v branch circuit by identifying the white as an ungrounded conductor. So I thought the workaround was using a 10/3 NM cable and capping off the white wire both ends & just using the black/red (no EVSE outlet, say perhaps HVAC). Except I read(?)that 300.3(B) prohibits this too.But then we get into 404.4(C) and the neutral is capped, not terminated, at the switch box and intended for future use. So why can’t an unused neutral in my 10/3NM 240v circuit be categorized as a functional spare?
You've hit on some common points of confusion in the NEC. Let's break it down
Your Core Question: Can I use a 10/3 NM cable (black/red/white) for a 240V circuit (like HVAC), capping off the white wire, and treating it as a spare?
The answer is generally NO, even though it might seem logically similar to the "future neutral" allowance in 404.2(C). Here's why: 300.3(B) is Key
This section requires that all conductors of a circuit be run in the same raceway, cable, or otherwise run together. The intent of this rule is to maintain equal impedance in the circuit, which helps with voltage drop and performance of overcurrent protection. Simply capping the white conductor does not meet this requirement, as it is not providing any useful service.
200.7(C)(2) is Very Specific
This is the only exception where you can re-identify the white wire as hot (ungrounded) within NM Cable, and it strictly applies to
switch loops. It is written exactly as it is for safety, so that the next guy doesn't kill himself trying to fix your incorrect wiring. 404.2(C) doesn't apply here
This section specifically addresses situations at
switch locations where a neutral conductor is brought to the box for possible future use. It applies where you might want to add smart switches that need a neutral for their internal circuitry. It does not provide a loophole to circumvent the rules against using a 10/3 NM cable for a dedicated 240V circuit and simply "capping off" the white wire.
Why the Difference?
The "future neutral" at a switch is intended for very specific use cases (smart switches). The NEC is concerned about maintaining proper circuit integrity and safety. Using a 10/3 with a capped neutral for a 240V load is not the intended use of the cable and introduces potential problems: Misinterpretation
A future electrician could see the capped white wire and incorrectly assume it's a neutral, potentially creating a dangerous situation.*
Circuit Integrity
While not carrying current, the presence of the unused conductor changes the electrical characteristics of the cable compared to a cable designed for that purpose.
Your Alternatives (Correct Ways to Wire a 240V Circuit with NM Cable)
Use the Correct Cable
The best and safest approach is to use a cable designed for the circuit's intended voltage and conductor needs. In your case, a 10/2 NM cable is the right choice for a simple 240V circuit without a neutral.2.
Run Individual Conductors in Conduit
If for some reason you really need to run individual conductors, use the appropriate conduit and wiring methods (e.g., THHN/THWN conductors) and run both ungrounded wires together in the same conduit. This allows you to select the right color coding and wire size for the specific application.
In summary: while you may be able to get a circuit powered using 10/3 and capping off the neutral, this isn't compliant with current electrical code and introduces significant hazards. Follow the NEC and don't improvise to stay safe! Flag for review