Question: Hello,I work in the temporary power industry and am seeking advice on our current power plant setup in California. We have eight 500 kW generators paralleled at an 8000 A paralleling cabinet. The output branches off into two 4000 A breakers, which feed two 2.5 MVA transformers stepping up the voltage from 480 V to 12,470 V.My question is: Should we place the bond at the paralleling cabinet or at the transformers, rather than at the generators?
Okay, let's break down the grounding requirements for your temporary power plant setup in California and address the best location for the system bonding jumper. This is a critical safety issue.
Understanding the Key Concepts Grounding vs. Bonding
It's important to differentiate between grounding and bonding. Grounding connects a conductive object to the earth to provide a path for fault current. Bonding connects non-current-carrying metallic parts to create a low-impedance path for fault current, facilitating the operation of overcurrent protective devices (breakers).
System Bonding Jumper (SBJ)
This is the connection between the grounded conductor (neutral) and the equipment grounding conductor (typically the enclosure or frame). It's the critical connection for safety.
Separately Derived System (SDS)
Your transformers create a separately derived system. According to the NEC, an SDS must be grounded as close as practical to the source.
Why Not at the Generators? With eight generators paralleled and the neutral points connected at the paralleling cabinet, you effectively have one neutral point. Bonding at each generator would create multiple, undesirable ground paths, which can lead to circulating currents, voltage distortion, and potentially nuisance tripping. The generator frames themselves should be bonded to each other and the paralleling cabinet. The earth grounding from the generators will not create a low impedance path for fault current in the event of a fault.
Why at the Paralleling Cabinet? This is generally the correct approach for a paralleled generator system, but ONLY if you are NOT using transformers. Here's why: Central Point
The paralleling cabinet is the central point where all the generator neutrals are connected. Placing the SBJ here provides a single point of connection for the grounded (neutral) conductor and the equipment grounding conductors.
Fault Current Path
It ensures that fault current from any of the generators has a clear, low-impedance path back to the source (the generators).
NEC Compliance (Likely)
This setup would meet the intent of the NEC if you didn't have the step-up transformers involved.
Bonding the Enclosure
The metal enclosure of the paralleling cabinet
MUST be bonded to the equipment grounding conductor system. Ground Electrode Conductor (GEC)
A Ground Electrode Conductor (GEC) must connect the grounding system at the paralleling cabinet to a suitable grounding electrode (e.g., ground rod, water pipe, building steel).
Why at the Transformers? Separately Derived System (SDS) Rules
Because you are stepping up the voltage with transformers, you now have a separately derived system, as defined in the NEC. NEC 250.30 (2023 NEC) dictates the grounding requirements for SDS.
NEC 250.30 states the following
(A) Grounded Systems
For an SDS, the system must be grounded where the grounded conductor (usually the neutral) is connected to a grounding electrode conductor (GEC).
(1) System Bonding Jumper
The location of the SBJ is critical. It MUST be installed at the source of the SDS, which in your case is the secondary of EACH transformer. It connects the grounded conductor (neutral) to the equipment grounding conductors.
(2) Grounding Electrode Conductor
Connect the grounded conductor (neutral) at each transformer to a grounding electrode.
Improved Fault Protection
Grounding at the transformers ensures that a ground fault on the 12.47 kV side will have a very low impedance path back to the transformer secondary neutral, facilitating rapid clearing of the fault by the appropriate overcurrent protection.
The Correct Setup: A Hybrid Approach
Based on your description, here's the recommended approach to ensure safety and NEC compliance:1. Paralleling Cabinet
Bond the frames of ALL generators to each other, to the paralleling cabinet enclosure, and to the grounding electrode system (using a GEC to ground rod(s), etc.). This is equipment grounding. This doesn't create a system ground; it ensures all equipment is at the same potential and provides a path for fault current. Connect the generator neutrals to the neutral bus in the paralleling cabinet. Monitor the paralleling cabinet neutral for current. This can help detect circulating currents which could be caused by improper bonding or grounding.2.
Transformers
System Bonding Jumper (SBJ)
Install a separate system bonding jumper at the secondary (12.47 kV) of each transformer. This is the main system bonding point for each transformer's SDS. Connect the grounded conductor (neutral) to the transformer enclosure and the equipment grounding conductor (EGC).
Grounding Electrode Conductor (GEC)
Run a separate grounding electrode conductor (GEC) from the secondary neutral of each transformer to a grounding electrode (e.g., ground rod, building steel). These GECs MUST be sized per NEC Table 250.66.
Bonding the Enclosure
Make sure the transformer enclosure is securely bonded to the equipment grounding conductor system.
Important Considerations & Recommendations California Specifics
California uses the NEC with amendments. Always check with your local electrical inspector for any specific local requirements that may supersede the general NEC guidelines.
Neutral Grounding Resistor (NGR)
Consider using a Neutral Grounding Resistor (NGR) on the secondary (12.47 kV) side of each transformer. This limits the ground fault current to a predetermined value, reducing stress on equipment and improving safety. This is common practice in medium-voltage systems. This is especially important for temporary installations.
Qualified Personnel
This is a complex electrical installation. Ensure that all work is performed by qualified electricians who are familiar with generator paralleling, transformer grounding, and the NEC.
Engineering Review
Have your complete design reviewed by a qualified electrical engineer. This is especially important for temporary power systems, where safety and reliability are paramount.
Load Calculations
Verify your load calculations to ensure your generators and transformers are adequately sized.
Coordination Study
Perform a coordination study to ensure that your overcurrent protection devices (breakers, fuses) are properly coordinated to selectively clear faults. This will prevent widespread power outages due to a single fault.
Documentation
Maintain thorough documentation of your grounding and bonding system, including wiring diagrams, connection details, and testing results.
Testing
Perform thorough testing of the grounding and bonding system after installation and periodically thereafter. This includes verifying the integrity of the grounding electrode conductor (GEC) connections and measuring ground impedance.
Marking/Labeling
Clearly label all grounding and bonding connections.
In summary: Bond the generator frames and paralleling cabinet together and to a suitable grounding electrode system. Then, treat EACH transformer secondary as a Separately Derived System. Each transformer secondary should have its own System Bonding Jumper and Grounding Electrode Conductor connected to a suitable grounding electrode.
By following these guidelines, you can create a safe and reliable temporary power plant that meets the requirements of the NEC and protects personnel and equipment. Please consult with qualified professionals to ensure that your specific installation meets all applicable codes and standards. Good luck! Flag for review