Question: Anyone here ever take the legs and the removable gland plate off of larger outdoor transfer switches and set them on a concrete pad directly over your conduits with ground bushings instead of nippling up with the legs on and use meters hubs?
Yes, I've heard of electricians doing this, and there are a few considerations to keep in mind
Pros:
Cost Savings
Eliminates the need for meter hubs, nipples, and sometimes a section of conduit.
Easier Conduit Bending
Potentially easier to bend conduits to match the relatively low entry point of the transfer switch enclosure.
Lower Profile
The installation sits closer to the pad, potentially less obtrusive and subject to wind loading.
Cons/Things to Consider
Code Compliance
This is the most important point. You absolutely must ensure this method complies with the NEC (National Electrical Code) and any local codes. Specific areas of concern include: Weatherproofness
The transfer switch is designed to be weatherproof with its original configuration. Removing the legs and gland plate and directly attaching it to the pad introduces a potential point of water ingress. You'll need to ensure a completely weatherproof seal between the enclosure and the concrete pad. High-quality caulking and sealing methods are essential. Consider the long-term durability of the sealant against UV exposure and temperature variations.
Corrosion
Direct contact with concrete can sometimes accelerate corrosion of the enclosure. Consider using a non-corrosive barrier between the enclosure and the pad.
Grounding
Pay very close attention to grounding. Using ground bushings is a good start, but ensure the entire system is properly bonded according to NEC requirements (Article 250). Consider the potential for dissimilar metal corrosion where the grounding connections are made.
Manufacturer's Instructions
The transfer switch manufacturer's instructions are paramount. Deviating from their approved installation methods could void the warranty and, more importantly, create an unsafe installation. Check if the manufacturer allows for this type of installation and if they have specific recommendations. Sometimes, manufacturers offer alternative mounting options for specific situations.
Working Space
Ensure adequate working space around the transfer switch as required by the NEC. The lower mounting position might affect access.
Mechanical Protection
The legs provide some degree of protection against accidental damage from lawnmowers, vehicles, or other equipment. A low-mounted transfer switch is more vulnerable.
Serviceability
Working on the transfer switch might be more difficult due to the low position. Think about how easily the unit can be accessed for maintenance, repairs, or future upgrades.
Pad Height
The concrete pad must be tall enough to keep the bottom of the transfer switch above the ground and any potential water pooling.
Conduit Support
Ensure the conduits are properly supported to prevent stress on the enclosure. The conduits should not be solely supporting the weight of the transfer switch.
Inspection
Be prepared for extra scrutiny from electrical inspectors. They will likely be very cautious about any deviations from the standard installation method.
Alternatives to Consider
Short Nipples and Meter Hubs
While more expensive than direct mounting, using very short nipples and meter hubs provides a more secure and weatherproof connection while still keeping the transfer switch relatively low.
Custom Bases
Some electricians fabricate custom steel or aluminum bases that are designed to be bolted to the concrete pad and provide a secure and weatherproof mounting surface for the transfer switch.
Larger Concrete Pad
Making the concrete pad bigger so the legs will fit on the pad.
In Summary
Directly mounting a transfer switch to a concrete pad without legs can be done, but it requires careful planning, meticulous execution, and a thorough understanding of electrical codes and best practices. You must* address weatherproofness, grounding, mechanical protection, and serviceability. It is strongly recommended to consult with a qualified electrical engineer or inspector to ensure the installation is safe and code-compliant.
Always prioritize safety and compliance with the NEC and local regulations. If there's any doubt, stick to the manufacturer's recommended installation methods. Flag for review