Question: I’ll try to give as much detail as possible for this project bare with me and let me hear your inputNote; this specific cooler manufacturer says not to penetrate roof only through side walls.This is an exterior walk-in that sits about 3 foot away from the building on a concrete pad. I stubbed out the circuits on the side of the building and will plan on going into back of a WP box then liquid tight from there to the necessary locations. Prints call for a 120v circuit for the cooler light/door heat. A 208v circuit for the condenser on the rooftop and a 208v circuit for the evaporator inside. So I stubbed out those 3 circuits. My plan was this: liquid tight from WP box to a disconnect mounted on the side of the building, then from disconnect straight to the condenser. Next I was gonna liquid tight from WP box down to the exterior of the cooler wall to a WP box then through the wall from back of box to the inside of the cooler to another WP box to get the other 2 circuits inside. And install a WP single pole switch as disconnecting means for the light/door heat. Then from that box, liquid tight to the already provided light that is integrated to the door heat already. And then another liquid tight to the evaporator and mount another WP box where I’ll install the disconnect (double pole switch)If anyone has suggestions please iM open and humble enough to learn new things and try them out thanks
Okay, let's break down your plan and see if we can optimize it for efficiency, code compliance, and serviceability. Your initial plan is a good starting point, and we can refine it. Here's a breakdown of your plan with considerations and suggestions
General Considerations:
Code Compliance
Always remember to adhere to the NEC and any local amendments. Double-check wire sizing, conduit fill, grounding, and disconnecting means requirements.
Corrosion Resistance
Given this is an exterior application, ensure all materials, including enclosures, fittings, and conductors, are rated for the environment. Stainless steel or appropriately coated boxes and hardware are good choices.
Serviceability
Think about how easy it will be to troubleshoot and repair the system in the future. Well-placed disconnects, clearly labeled wiring, and accessible components are crucial.
Sealants
Properly seal any penetrations through the walk-in cooler walls to prevent moisture ingress and maintain insulation integrity.
Detailed Analysis and Suggestions
1. Power Entry to the Building & WP Box
Your Plan
Sounds solid. Sticking out your circuits on the side of the building into a WP box is a good starting point.
Suggestion
Ensure the WP box is appropriately sized to handle all the conductors and connections. Consider using a larger box than you initially think you need, as it's easier to work in a spacious enclosure. A junction box is also an option if that serves your purpose better.
2. Condenser Circuit (Rooftop Unit)
Your Plan
Liquidtight from the WP box to a disconnect, then from the disconnect to the condenser.
Suggestion
Disconnect Location
Consider the distance from the condenser to the disconnect. The NEC requires the disconnect to be within sight of the condenser, and readily accessible. Verify the AHJ (Authority Having Jurisdiction) has no local amendments about this requirement.
Disconnect Type
Choose a suitable disconnect, such as a fused disconnect or a non-fused disconnect with a circuit breaker back at the panel. Fused disconnects offer additional protection.
Conduit/Wiring Method
Liquidtight is fine for the short run from the building to the disconnect. From the disconnect to the condenser, consider using rigid metal conduit (RMC) for better physical protection, especially if the run is exposed to potential damage or traffic. Seal the conduit where it enters the condenser. Consider grounding with a properly sized equipment grounding conductor (EGC) run within the conduit.
Listing and Labeling
Ensure the conductors, disconnect, and any other associated equipment are rated for the voltage and amperage of the condenser, and that all is correctly labeled with permanent, legible marking.
3. Power to the Walk-In Cooler (Interior Circuits)
Your Plan
Liquidtight from WP box down the exterior of the cooler wall to another WP box, through the wall to an interior WP box.
Important Note on Penetrations
This is where the manufacturer's prohibition against roof penetrations is critical. Sticking to sidewall penetrations is key.
Suggestion
Penetration Method
This is crucial. Carefully drill the hole through the wall. Use a properly sized drill bit for the conduit you're using. After pulling the wires through the conduit, use a sealant specifically designed for walk-in cooler walls (often a food-grade silicone sealant) to completely seal around the conduit both inside and outside the box to prevent air leakage and moisture infiltration. This is important for energy efficiency and sanitation.
WP Box Location (Exterior)
Ensure the exterior WP box is located in a protected area if possible, away from direct sunlight and rain.
WP Box Location (Interior)
Position the interior WP box where it's accessible but out of the way of normal cooler operations. Consider the food storage area and prevent any potential contamination.
4. Interior Circuits (Light/Door Heat, Evaporator)
Your Plan
WP single-pole switch for light/door heat, liquidtight to the light/door heat unit. Liquidtight to a WP box with a double-pole switch for the evaporator.
Suggestion
Light/Door Heat Circuit
Disconnect Location
Ensure the switch for the light/door heat is readily accessible and clearly labeled.
Wiring
Ensure the liquidtight conduit and wiring are appropriate for the amperage of the light and door heater.
GFCI Protection
Consider the requirement for GFCI protection for receptacles or equipment within the walk-in cooler. Door heaters are often wet-location applications. Check the NEC for the latest requirements.
Evaporator Circuit
Disconnect Location
The double-pole switch should be readily accessible and clearly labeled as the evaporator disconnect.
Wiring
Ensure the liquidtight conduit and wiring are sized appropriately for the evaporator's current draw.
Fused Disconnect
Consider using a fused disconnect for the evaporator for additional protection.
5. Disconnecting Means
General Requirements
Ensure all disconnecting means meet the requirements of NEC Article 440 (for air-conditioning and refrigeration equipment) and Article 430 (for motors, if applicable). The disconnects must be rated for the voltage and amperage of the equipment they serve.
Accessibility
All disconnects must be readily accessible.
6. Grounding
Run a proper sized equipment grounding conductor with all circuits. This should be bonded at the source and terminated properly at all equipment.
Additional Tips
Drawings
Keep detailed drawings of your wiring runs and component locations. This will be invaluable for future troubleshooting and maintenance.
Testing
After completing the installation, thoroughly test all circuits to ensure proper operation and verify that all grounding connections are secure.
Inspection
Schedule an inspection with your local electrical inspector. Be prepared to answer their questions and demonstrate that your installation complies with all applicable codes.
Revised Plan Summary (Taking Suggestions into Account)
Power Entry
3 circuits from building to exterior WP box.2.
Condenser
Liquidtight from WP box to disconnect (located within sight and readily accessible). RMC from disconnect to condenser, sealed properly at the condenser.3.
Walk-In Cooler Penetration
Liquidtight from WP box down the wall to another exterior WP box. Carefully drill holes and pull liquidtight from exterior WP box to interior WP box. Thoroughly seal penetrations with food-grade silicone sealant.4.
Interior: Light/Door Heat: Liquidtight from interior WP box to single-pole switch, then to light/door heat unit. Verify GFCI requirements.* Evaporator: Liquidtight from interior WP box to double-pole switch (or fused disconnect), then to the evaporator.By carefully considering these details and suggestions, you'll create a safe, code-compliant, and reliable electrical installation for the walk-in cooler. Remember to consult the NEC and local codes, and don't hesitate to ask for clarification from your electrical inspector if needed. Good luck! Flag for review