Asked on: Wednesday, September 17, 2025 at 11:59 pm EDT
Answered on: Thursday, September 18, 2025 at 12:00 am EDT

Question: Just a sanity check here. So on this 2000A breaker, i can turn thr long time down to .4 and use 800 A conductors yes?

Okay, let's break this down carefully. You're talking about a 2000A circuit breaker with an adjustable long-time pickup setting, and you want to know if you can use 800A conductors on that circuit if you adjust the long-time pickup to 0.4.

Understanding the Components 2000A Breaker

The maximum current the breaker is designed to carry.


Long-Time Pickup (LTR) Setting

A setting that determines the current level that, when exceeded for a sustained period, will cause the breaker to trip. In this case, you want to set it to 0.4.

800A Conductors

Wires that are rated to safely carry a continuous current of 800 amps.

Calculation


The long-time pickup setting is a
multiplier of the breaker's rating. So, with a 2000A breaker and a long-time pickup setting of 0.4, the actual trip point is:2000A (Breaker Rating) 0.4 (LTR Setting) = 800ANEC Considerations

The National Electrical Code (NEC) governs electrical installations. Here's how the relevant sections come into play: NEC 240.4(B)

This section deals with the protection of conductors. The general rule is that conductors must be protected at their ampacity. There are some specific cases, though. The rule is that the next standard size device above the conductor rating
is permitted. However the conductors must also be rated for at least 800 amps.



NEC 240.4(C)

This section prohibits using the "next higher standard overcurrent device" rule when the overcurrent protection is a circuit breaker with adjustable trip settings.

AnswerBased on the information you provided, using 800A conductors with the 2000A breaker set to a long time pickup of 0.4

is permissible, so long as you do not upsize the breaker based on the conductor ampacity per 240.4(B). The long-time pickup setting effectively reduces the tripping current of the breaker to match the conductor's ampacity. The conductors would have to be rated for at least 800 amps. You would not be able to then use NEC 240.4(B) to upsize the breaker.

Important Considerations and Cautions



Manufacturer's Instructions



Always consult the manufacturer's documentation for the specific breaker you're using. They will have detailed information about the adjustable settings and proper application.


Coordination Study

For larger electrical systems, a coordination study is highly recommended. This study analyzes the entire system to ensure that overcurrent protective devices (OCPDs) like breakers will trip selectively, minimizing outages.

Qualified Electrician

All electrical work should be performed by a qualified and licensed electrician who is familiar with the NEC and local codes.


Marking

Ensure the adjusted long-time pickup setting is clearly marked on the breaker or panel schedule. This helps prevent accidental changes.

Disclaimer: This information is for general understanding only and should not be used as a substitute for the guidance of a qualified electrician or engineer. Always consult with qualified professionals for your specific situation. Flag for review