User: zander, Location: W238N1087 Sherwood Dr. Waukesha, WI 53188
Asked on: Thursday, September 18, 2025 at 12:28 pm EDT
Answered on: Thursday, September 18, 2025 at 12:28 pm EDT
Question: Hello Everyone,I'm installing a 320 amp service, 2x 200 amp breakers in the pedestal, 2x separate 4/0, 4/0, 4/0, 2/0 SER cables run to 2x separate 200 amp panels in the basement, 2x ground rods tied together with #4 bare (I know I could have gotten away with #6) run back to both panels.Here is the question.Table 250.66 says that the GEC is based on the size of the largest ungrounded conductor or equivalent area for PARALLEL CONUCTORS. Taking that word for word, I came to the conclusion that a #4 bare copper wire would meet those requirements. The inspector, however, is saying that the size of the GEC should be based on the 320 amp service rating. I don't agree with this because the 2x 200 amp feeds going to the panels are by definition individual, and not parallel. What is the general consensus on this? Thank you in advance.
Okay, let's break this down. This is a common point of confusion with 320A services and parallel conductors.
The Core Issue: Are These "Parallel Conductors" in the Code Sense?
This is the pivotal question. The inspector's argument likely hinges on the intent of the NEC to ensure adequate grounding capacity for the entire service being delivered, regardless of how it's distributed to the panels. Your Argument
You're reasoning that because each 200A feed is separate and goes to a separate panel, they are not truly "parallel" in the NEC's defined use of the term. Each feed is its own circuit, with its own overcurrent protection. Therefore, each feed's GEC size should be determined by the 4/0 conductors feeding that panel.
Inspector's Argument
The inspector is likely interpreting the system as a single 320A service, and the NEC is designed to protect the entire service. Even though the conductors are separate, they are functioning as parallel conductors to deliver the total service capacity. The NEC wants a GEC capable of handling a fault current from the entire service.
NEC Considerations & Analysis Article 250.24(A): Service Grounding. This section is the overarching guide to service grounding. It states the service shall be grounded as per 250.4(A)(1). That means you need to establish a ground at the service equipment. Table 250.66
This is where the debate lies. It sizes the GEC based on the size of the largest service entrance conductor or equivalent area for parallel conductors. Your interpretation is based on treating the two 4/0 sets individually.
Parallel Conductors
NEC Article 310.10(H) outlines the conditions for paralleling conductors. This section generally applies to conductors operating in parallel as phase conductors, not necessarily to separate service entrance conductors feeding different panels from a single service disconnect. However, the intent of providing adequate fault current capacity for parallel conductors might be applied by the inspector.
Informational Note to 250.66
The Informational Note is key. It advises consideration of the maximum ground-fault current that could flow. This is where the inspector's argument gains strength. A larger service capacity (320A) means potentially higher fault current.
NEC 250.64(D)(1): Single GEC for Multiple Services
This is NOT your situation, as you have a single service. However, it highlights that the NEC recognizes that multiple services can be fed from a single source and need appropriately sized GECs.
The Strongest Argument Against Your Position (and Why the Inspector May Be Right)
The most compelling argument against your position is the overall fault current capability. While each panel is protected by a 200A breaker, a fault upstream of those breakers could potentially draw a significant current, even beyond 200A per leg, until the utility's upstream protection operates. The GEC needs to be able to handle that. The inspector is likely concerned about the worst-case scenario: a ground fault before the two 200A breakers, and on the service conductors themselves, and thus wants to size the GEC for the overall service rating, not the individual breaker sizes.
Recommendation
Unfortunately, based on prevailing interpretations, the inspector has a strong argument. While you might technically be correct in your reading of the "parallel conductors" section, the intent of the code to ensure adequate fault current protection for the entire service seems to favor sizing the GEC based on the 320A service rating. Calculate the GEC size based on the 320A service using Table 250.66. Using the equivalent area of the two sets of 4/0 conductors to determine the required GEC size. With two sets of 4/0 copper conductors the equivalent area is 424,400 circular mils. Table 250.66 would indicate a GEC size of #2 AWG copper. Politely discuss your interpretation with the inspector. Explain your reasoning and ask for clarification on their interpretation. You can even ask them to point to the specific section in the NEC that supports their position. Consider using a larger GEC. In the end, a larger GEC is never a bad thing (within reason). It provides a more robust grounding path and could potentially save headaches with the inspector. Using a #2 copper wire would be sufficient.
Important Considerations
Local Amendments
Be aware that your local jurisdiction may have amendments to the NEC that specifically address this type of situation.
AHJ (Authority Having Jurisdiction): The inspector is the AHJ. Their interpretation, however correct or incorrect, ultimately prevails unless you can successfully appeal it through the proper channels.In short, while your argument has some technical merit, the inspector's position aligns more closely with the overall intent of the NEC to provide adequate fault current protection for the entire service. I would recommend working with the inspector to find a solution that satisfies their concerns and meets the code requirements. A #2 GEC conductor is likely the most reasonable approach. Flag for review