Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: How much electric power is needed for HOT commissioning for a HV Substation

User: Joao, Location: portugal

Asked on: Thursday, September 18, 2025 at 1:14 pm EDT
Answered on: Thursday, September 18, 2025 at 1:15 pm EDT

Question: How much electric power is needed for HOT commissioning for a HV Substation?For example:1 x 400 kV GIS with 10 bays2 x power transformers 600 MVA, 400/225 kV1 x 225 kV GIS with 10 baysControl Room with P&R System + SCADA + DC System + UPS

Estimating the electrical power needed for HOT commissioning a high-voltage (HV) substation like the one you described is complex and depends on various factors. However, we can break it down into the major components and estimate the power requirements for each.

Key Considerations



Simultaneous Testing

Are you testing all equipment simultaneously, or are you staggering the tests? This has a huge impact on the peak power demand.


Testing Equipment

Specific test equipment used will greatly affect power draw. Knowing the nameplate ratings of all planned test equipment is crucial.

Duration

The power demand will vary depending on which testing activities are ongoing at a given time. A load profile can be constructed which shows the peak power demand at any given time.


HV Power Requirement

For HOT commissioning, a HV power supply is necessary. A temporary power supply with adequate capacity to supply the peak demand load shall be setup.

Load Profile

Developing a load profile is the best approach for estimating power requirements for HOT commissioning. The load profile is based on a timeline of testing activities, expected load demand for each activity and the corresponding duration. The highest value in the load profile represents the peak power demand during HOT commissioning.

Power Estimation Breakdown (Estimates Only)

Here is a power estimation for each component of your substation.1.

GIS (400 kV and 225 kV)



Primary Injection Testing

Requires specialized HV test equipment. Power needed to supply high-current AC power for injecting into the GIS primary circuit. This is typically the highest power demand during the entire commissioning process. Current Source: 100 - 500 kVA (depending on the system requirements)

Control and Protection Testing

Testing circuit breaker operation and protection schemes.
Low voltage power supply: 10 kVA

Overall GIS Estimate

Assume

100-500 kVA
(intermittent peak during primary injection) + 10 kVA (continuous for control/protection)2. Power Transformers (600 MVA x 2)



Turns Ratio Test

Requires a low-voltage power supply. 5 - 10 kVA

Winding Resistance Test

Requires a DC power supply. This can be substantial, depending on the transformer size and winding resistance. 5 - 20 kW (DC) (this can be sourced from the DC system if properly sized)

Insulation Resistance Test (Megger)

Very low power, negligible.


Partial Discharge Test

Requires a high-voltage power supply for energizing the transformer. This can be a significant load. 50-200 kVA

Transformer Protection Testing

Requires specialized test equipment
Low voltage power supply: 10 kVA

Overall Transformer Estimate (per transformer)



50-200 kVA
(intermittent peak during partial discharge) + 10kVA (continuous for protection testing) + 5 - 20 kW (DC)3. Control Room



Protection & Control (P&C) System

Relays, metering, communication equipment. Powered primarily by the DC system (see below). Assume 5 kVA continuous

SCADA System

Servers, workstations, communication equipment. 5-10 kVA continuous

DC System (Charger and Batteries)

Charging the batteries requires a significant AC input. This will be the primary load on the control room AC supply. A typical DC system might be 110V or 220V DC, and the charger needs to supply enough current to float charge the batteries and supply the connected DC loads (P&C, tripping circuits, etc.) Estimate charger capacity: 20-50 kVA (depending on battery size and loads)

UPS System

Similar to the DC system charger, the UPS charger will draw power to maintain battery charge. The UPS is likely supporting critical SCADA and communication equipment. 10-20 kVA

Lighting, HVAC, General Outlets

This depends on the size of the control room, but can be significant. Assume 10-30 kVA

Overall Control Room Estimate



50-100 kVA
continuous, potentially more depending on HVAC and lighting.

Putting It All Together (Rough Estimate)



Peak Intermittent Power (HV Testing)

GIS (Primary Injection): 100-500 kVA Transformers (Partial Discharge): 50-200 kVA (x 2) = 100-400 kVA

Total Peak: 200-900 kVA
Continuous Power (Control Room, Protection Testing, etc.)

GIS (Control/Protection): 10 kVA Transformers (Protection Testing): 10 kVA x 2 = 20 kVA Control Room: 50-100 kVA

Total Continuous: 80-130 kVA
Overall Estimate



Peak Power Demand: 200-900 kVA
(This is a wide range! Requires detailed planning.)* Continuous Power Demand: 80-130 kVAImportant Considerations and Next Steps


Detailed Test Plan

The most important step is to develop a very detailed test plan outlining all commissioning activities, test equipment to be used, and the estimated power requirements for each activity.2.

Test Equipment Specifications

Gather the nameplate ratings (kVA, voltage, current) for all test equipment. Confirm the equipment actually performs according to the nameplate.3.

Load Profile Development

Create a load profile, charting the power demand over time, taking into account which tests will be performed simultaneously and their duration. This will give you a much more accurate estimate of the peak power demand.4.

Power Factor

Consider the power factor of the loads, especially for inductive loads like transformers and motors. The kVA demand will be higher than the kW demand if the power factor is low.5.

Voltage Requirements

Be sure to consider the voltage requirements of all equipment (LV, MV, HV) and ensure the temporary power supply can provide the correct voltages.6.

Redundancy

Consider having some redundancy in the temporary power supply in case of failure.7.

Safety

Ensure all temporary power installations are done by qualified electricians and meet all safety standards.8.

Coordination

Careful coordination with the test equipment vendors and commissioning engineers is essential for accurate power estimation.

In summary, while a rough estimate is 200-900 kVA peak and 80-130 kVA continuous, the best approach is to develop a detailed test plan, gather equipment specifications, and create a load profile to get a more accurate power requirement estimate.
It's better to overestimate and have excess capacity than to underestimate and experience delays or equipment damage. Flag for review

Previous Question Next Question