User: Circuit_Jerk, Location: USA

Asked on: Thursday, September 18, 2025 at 3:05 pm EDT
Answered on: Thursday, September 18, 2025 at 3:14 pm EDT

Question: Hi, I'm doing some electrical homework and ran across this question."The hot water for the heating system for a small factory is supplied by a single boiler. The boiler is located in a small building separate from the factory. The power supplied to the boiler is 240V single-phase without a neutral conductor. At the present time, the small building housing the boiler has no inside lighting. The business owner desires that four 100W lamps be installed inside the building. All lamps are to be connected to a single switch. The lamps are to be connected to the present 240V service inside the building. How would you accomplish this task? Explain your answer."Here's what I got this far, I don't think I'm right but I can't figure out where I went wrong:240V power supply 4(100W) = 400W lamps wired to single switchWire all lamps in parallel with the switch so that the switch turns on all lights but if one light burns out, it won’t affect the other lights. Wire the switch in series with the 240V power supply.I = 100W/240V = 0.417A per bulb. Total current is summed in parallel circuits.0.417A * 4 = 1.668A needed through switch into lights.240V/ 0.417A = 575.54ohms resistance per bulb.Rtotal= 1/ (1/575.54 + 1/575.54 + 1/575.54 + 1/575.54)Total resistance of bulbs using reciprocal formula = 143.885ohmsSQRT (P X R) = VSQRT ( 143.885 * 100 ) = 119.952V240V – 119.952 = 120.048V drop needed.P = (1202/36.029) = 399.678 rating for resistor.R = (120.0482 / 400W ) = 36.029 ohms resistor needed to add with 400W power rating.So the major issue I've been having is I can't figure out why I'm wrong, I know I am but I can't figure out how to think about this issue differently.Any advice is helpful. Thanks.

You're on the right track with wiring the lamps in parallel with a switch, but the resistance and voltage drop calculations are unnecessary and incorrect for this simple circuit. You're overcomplicating the problem by trying to introduce a resistor. Let's break down why

The Key Issue: You don't need a resistor!

The problem states you have a 240V power supply, and you want to use 240V lamps. You don't need to drop the voltage! You're simply wiring 240V lamps to a 240V supply. The lamps are designed to operate at 240V and dissipate 100W at that voltage.

Here's how to solve the problem

1.

Parallel Wiring

As you correctly identified, wire the four 100W, 240V lamps in parallel. This ensures that if one lamp fails, the others will continue to operate. Parallel wiring also means each lamp receives the full 240V.2.

Switch in Series

Place the single switch in series with the parallel lamp circuit. This allows you to control all four lamps with a single switch.3.

Current Calculation (Important for Wire Sizing)

You correctly calculated the current per lamp: I = P/V = 100W / 240V = 0.417A (approximately). Total current: I_total = 4 0.417A = 1.668A (approximately).
4.


Wire Sizing and Overcurrent Protection (Fuse or Circuit Breaker)

This is the crucial practical consideration!


Wire Size

You need to choose a wire gauge that can safely handle at least 1.668A. Consult a wire ampacity chart (easily found online or in the National Electrical Code if in the US) to determine the appropriate wire size for the installation conditions (e.g., temperature rating of the wire). You'll likely need at least 14 AWG, and possibly 12 AWG depending on the wire type.

Always err on the side of caution and use a larger gauge wire if you're unsure.
Overcurrent Protection

The wiring needs to be protected by a fuse or circuit breaker. A 3-amp or 5-amp fuse or circuit breaker would be appropriate. Using an overcurrent device is
crucial to protect the wiring from overheating in case of a short circuit.

Why your resistance and voltage drop calculations were wrong



Ohm's Law and Lamp Resistance

While you can calculate the resistance of a lamp when it's lit, that's not the information you need to solve this problem. You are directly applying the correct voltage to the lamps that they are meant for, so the resistance is an unneeded value.

Voltage Drop

There's no need for a resistor to drop the voltage because you're already using 240V lamps on a 240V supply.

Final Answer/How to Accomplish the Task


Wire the four 240V, 100W lamps in parallel.
Connect one side of each lamp to one wire from the 240V supply, and the other side of each lamp to the other wire from the 240V supply.2. Place a single-pole switch in series with one of the 240V supply wires, before it connects to the parallel lamp circuit. This switch will control all the lamps simultaneously.3. Use appropriately sized wire (at least 14 AWG, possibly larger) that is rated for the installation conditions (temperature, etc.).4. Install a fuse or circuit breaker (3-amp or 5-amp) in the circuit to protect the wiring from overcurrent.Important Considerations and Disclaimer



Safety First

Working with electricity can be dangerous. If you are not comfortable or familiar with electrical wiring,

hire a qualified electrician
to perform the work. Local Codes

Always comply with all local electrical codes and regulations.


Proper Enclosure

Use appropriate electrical boxes and enclosures for the switch and wiring connections to ensure safety and prevent damage.*

Overcurrent Protection:
This is critical. Do not omit the fuse or circuit breaker.By following these steps, you can safely and effectively install the lighting system for the boiler building. Remember to prioritize safety and consult with a qualified electrician if you have any doubts or concerns. Flag for review