Topic: Class 2 div one, can my box just be dusttight?

User: kjroller, Location: Dawson Mn

Asked on: Thursday, September 18, 2025 at 6:02 pm EDT
Answered on: Thursday, September 18, 2025 at 6:03 pm EDT

Question: Can my box be dustight so I can drill my own hole and use meyers hub or does it need a threaded boss?

Whether you can use a Meyers hub directly with a drilled hole in your box depends on several factors, including

Factors:
NEMA Rating

A NEMA 4 or 4X box needs a much tighter seal than a NEMA 1 box. If you want to maintain a NEMA 4/4X rating, just drilling a hole and using a Meyers hub might not be sufficient to keep out water.


Box Material

Metal boxes generally allow for better grounding through the Meyers hub if it's properly tightened. Plastic boxes might need grounding wires.

Hub Size and Hole Size

Precise hole size is critical. The hole must be sized correctly for the Meyers hub you're using. Too small, and you can't install it. Too large, and you won't get a good seal.


Tightening

The hub needs to be tightened adequately.

Here's a breakdown



When you can likely use a Meyers hub with a drilled hole (with precautions)



NEMA 1 or similar dry-location enclosures

If you're not concerned about water tightness and only need to keep out dust and protect wiring in a dry environment, a drilled hole and Meyers hub
might be sufficient. However, consider using a knockout to create a clean hole.

When you are willing to use additional sealant

If you're willing to use a sealant or O-ring between the box and the hub, you can potentially achieve a better seal in a drilled hole.

When you should NOT use a drilled hole with just a Meyers hub



NEMA 4/4X (water-tight/water-resistant) enclosures

Simply drilling a hole and using a Meyers hub will almost certainly
not maintain the NEMA 4/4X rating. Water can easily get in.

Hazardous Locations

In hazardous locations, you MUST use appropriately rated and installed fittings. A drilled hole and standard Meyers hub is unlikely to meet the requirements.

When you need a very robust and reliable connection

A factory-threaded boss is always preferable for strength and reliability, especially in applications where the hub will be subjected to vibration or stress.

Why a threaded boss is better in many cases



Maintains NEMA Rating

Enclosures with factory-threaded bosses are designed to maintain their NEMA rating when appropriate fittings are installed.

Stronger Connection

A threaded connection is mechanically stronger than relying solely on the hub's clamping force.


Better Grounding

Threaded connections provide a more reliable ground path in metal enclosures.

Alternatives to Drilling & Meyers Hub



Use an enclosure with a pre-threaded hub or knockout

This is the preferred option, especially for NEMA 4/4X applications.


Use a proper fitting with gasket/O-ring
: Ensure that the fitting is rated for the NEMA rating of the box.

Recommendations


For NEMA 4/4X or any situation where water tightness is critical, DO NOT simply drill a hole and use a Meyers hub.
Use an enclosure with pre-threaded hubs, knockouts, or use proper rated fittings with gaskets or O-rings.2. If you must drill a hole

Drill the hole exactly the right size for the hub. Err on the side of slightly smaller and then carefully ream it out until the hub fits snugly. Use a high-quality Meyers hub. Use sealant or an O-ring between the box and the hub. Test for leaks after installation.3.

For dry locations where dust protection is the main concern

A drilled hole and Meyers hub might be acceptable, but it's still best practice to use an enclosure with knockouts or pre-threaded hubs.

In summary,
while technically you can drill a hole and use a Meyers hub in some situations, it's generally not recommended unless you're willing to take extra precautions and ensure a tight seal. For NEMA 4/4X applications, it's essential to use enclosures and fittings specifically designed to maintain the enclosure's rating. If in doubt, consult with a qualified electrician. They can assess your specific application and advise you on the best approach. Flag for review