Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Bonding Flexible Metal Conduit used for PV wire protection on the roof

User: tilden, Location: Chapel Hill, NC, USA

Asked on: Friday, September 19, 2025 at 3:58 pm EDT
Answered on: Friday, September 19, 2025 at 4:05 pm EDT

Question: We have a PV system with inverters that are adjacent to our array and are planning to use a short piece of flexible metal conduit to protect the PV conductors for the final few feet from when they leave the bottom of the array until they enter the inverter. Each end has a connector with plastic bushing inside for cable protection, and the end at the inverter will bond to the inverter via a lock-nut listed as capable of piercing paint to create a bond, so will qualify as bonded per NEC 2023 250.97 exception 3. This FMC will also contain a #6 bare ground wire to bond the inverter to the racking.My question is whether we need to add a ground bushing to the distal end of the FMC underneath the array. This distal end of the FMC is not connected to any box or other metal component, so there is nothing that is being made continuous by bonding here.We commonly use flexible nonmetallic conduit for this where no bonding is required at all, however this particular customer required all conduit to be metal.Photo attached, and for anyone wondering - the fill and ampacity of those PV wires just barely works in that 1.5" FMC.

Okay, let's break down the grounding requirements for your flexible metal conduit (FMC) application according to the NEC, particularly focusing on the 2023 edition, and consider your specific setup.

Understanding the Grounding Requirements for FMC

The key question is whether the FMC needs to be considered an equipment grounding conductor (EGC). If it's not, then you don't need to worry about special grounding bushings at both ends. NEC 250.118 lists the types of raceways that are permitted to be used as EGCs. FMC is on this list, but it has limitations. Crucially, FMC can be used as an EGC only under specific conditions and only where run with circuit conductors. In your case, where the bare #6 equipment grounding conductor is enclosed in the FMC along with the PV source circuit conductors, the FMC does not have to be bonded at both ends, it will have a low impedance fault return path regardless. If you are using the metal conduit as the equipment ground: NEC 250.97 covers bonding for over 250V to Ground. Exception 3 allows the use of listed locknuts and bushings to bond the metal conduit to the metal enclosure as long as the metal enclosure is listed for the purpose. Article 690: Solar Photovoltaic (PV) Systems Generally points back to the regular grounding rules in Chapter 250, but emphasizes the importance of a solid, low-impedance ground fault path. 250.4(A)(3)

This section emphasizes the need for an effective ground-fault current path. The path needs to be permanent, continuous, and have the capacity to carry fault current safely.

Analysis of Your Specific Situation


Let's analyze your scenario with the photo and details you provided:1. The #6 Bare Ground Wire

You are running a #6 bare copper ground wire inside the FMC. This is a critical factor. You are already providing a dedicated, code-compliant EGC. The presence of this conductor significantly simplifies the grounding requirements for the FMC itself.2.

FMC Length

Short length is good. Less impedance.3.

Inverter Bonding

You are bonding the FMC to the inverter using a listed locknut deemed suitable for paint-piercing, satisfying 250.97 Exception 3.
4.


Distal End Under the Array

This is the key point. You stated that the distal end of the FMC is NOT connected to any box or metal component. It's essentially "floating" at the array end.

Conclusion


Based on the information you've provided, you do NOT need a ground bushing at the distal (array) end of the FMC. Here's why: Redundant Grounding

You already have a dedicated #6 AWG bare copper EGC running
within the FMC. This is the primary means of ensuring a low-impedance fault current path. The #6 will easily outperform the metallic conduit in clearing a fault.

No Connection at Distal End

The distal end is not connected to any metal enclosure or other equipment that needs to be bonded. There's nothing to make electrically continuous at that end.

Purpose of Bonding

Bonding aims to create a low-impedance path for fault currents. Since you're already providing this with the #6 ground wire, additional bonding at the "floating" end of the FMC is not required and doesn't serve a practical purpose.

Why This Differs from Standard FMC Grounding


Standard FMC grounding rules often require bonding at both ends
when the FMC is relied upon as the sole EGC. In those situations, the goal is to ensure the entire raceway is electrically continuous and can carry fault current back to the source. Because you are running a dedicated ground wire, that requirement is satisfied by the ground wire. The FMC is essentially acting as physical protection for the wiring.

Important Considerations and Recommendations
Inspect Connectors

Double-check that the FMC connectors are properly tightened to the FMC and provide a secure mechanical connection.

Wire Sizing

You mentioned fill and ampacity being "just barely" compliant. Ensure you've performed all necessary calculations according to NEC 310.15 and Chapter 9. Err on the side of caution, especially in a PV application where temperature can be a factor.


Documentation

Keep records of your calculations and the rationale for your grounding approach. This will be helpful for inspections.

AHJ

While this analysis is based on the NEC, always confirm your interpretation with your local Authority Having Jurisdiction (AHJ). They have the final say.


Torque

Use a torque wrench to tighten all electrical connections, including the bonding locknut at the inverter. Use the manufacturer's specified torque values.

In summary, your design using the #6 AWG equipment grounding conductor inside the FMC, along with the listed bonding locknut at the inverter, appears to meet the NEC requirements without the need for an additional ground bushing at the distal end under the array because the FMC does not need to be used as the EGC for your PV system.
Flag for review

Previous Question Next Question