Topic: Unmetered wire way bonding

User: Kyle Miller, Location: Houston, Tx

Asked on: Friday, September 19, 2025 at 4:35 pm EDT
Answered on: Friday, September 19, 2025 at 4:43 pm EDT

Question: When installing a unmetered tap box and wireway, do I bond my neutral in the tap box for the entire system? Or do I bond each service disconnect as tenants move in? I can’t find anything clear cut and specific on this.

Okay, this is a common point of confusion and it's important to get right. The answer is nuanced and depends on a few factors, but here's a breakdown of the principles and how they generally apply to an unmetered tap box and wireway scenario

Key Principles:
Neutral-Ground Bond

The NEC (National Electrical Code)
only allows the neutral conductor to be bonded to ground at the service equipment. This is a critical safety feature to ensure proper operation of overcurrent protection devices (breakers and fuses) in case of ground faults.

Separated Neutrals and Grounds

After the service equipment, the neutral and grounding conductors must be kept separate. This prevents neutral current from flowing on the equipment grounding conductors, which could create a shock hazard.

Service Equipment

The "service equipment" is defined as the equipment that serves as the main control and cutoff of the electrical supply and provides overcurrent protection for the premises wiring. In your scenario, this is likely the individual tenant service disconnects (or panels)
after the tap box and wireway.

Unmetered Tap Box and Wireway Scenario

In an unmetered tap box and wireway arrangement, you have a main service (typically supplied by the utility) feeding the tap box. The tap box distributes power, often via individual breakers or fuses, through the wireway to multiple tenant spaces. Each tenant space then has its own service disconnect/panel.

Here's the breakdown of where to bond the neutral


At the Main Service

The utility typically establishes the neutral-ground bond
at the transformer supplying your building. There may also be a grounding electrode conductor connected to the neutral at your main service disconnect before the tap box.2.

Inside the Tap Box?
No. You should not bond the neutral to ground inside the tap box itself. The tap box is simply a distribution point, not the service equipment. Treat it as a raceway extension of the service conductors.3. Wireway

No. The wireway is also just a pathway for the conductors. Do not bond the neutral to the wireway.4.

At Each Tenant's Service Disconnect (Panel)

Yes. This is where you establish the required neutral-ground bond for that specific tenant's electrical system. This is considered the service equipment for that tenant.

Practical Steps During Installation



Tap Box and Wireway

Properly ground the tap box and wireway itself to the building's grounding electrode system (e.g., using a grounding electrode conductor to a ground rod, water pipe, etc.). Ensure all metal enclosures are bonded together to create a continuous, low-impedance ground fault path. Run separate neutral and equipment grounding conductors through the tap box and wireway to each tenant's service disconnect. Do not connect the neutral to the tap box or wireway enclosure. The only connection should be the grounding conductor to the enclosure.

Tenant Service Disconnect (Panel) Installation

When a tenant moves in (or during the initial installation), you connect the neutral conductor from the tap box/wireway to the neutral busbar in their service disconnect panel. This is where you make the neutral-ground bond within that panel. You'll use a main bonding jumper (typically a pre-made strap) to connect the neutral busbar to the panel enclosure, which is also bonded to the equipment grounding busbar. The equipment grounding conductors from the circuits within that tenant's space are connected to the equipment grounding busbar in the panel.

Important Considerations



NEC Article 250

This article covers grounding and bonding. Review it carefully. Sections like 250.24 and 250.30 are especially relevant.


AHJ (Authority Having Jurisdiction)

Your local electrical inspector (AHJ) has the final say. Consult with them during the planning and installation stages to ensure compliance with local codes and interpretations. They may have specific requirements or preferences.

Engineering Design

For larger or more complex systems, it's highly recommended to have a qualified electrical engineer design the system to ensure proper grounding and bonding.


Labeling

Clearly label the tap box and wireway to indicate that they are not the service equipment and that the neutral-ground bond must be established at each tenant's service disconnect.

In Summary:


You do not bond the neutral in the tap box or wireway. You bond the neutral at each individual tenant's service disconnect/panel. This ensures proper operation of overcurrent protection devices and helps prevent shock hazards. Always consult the NEC and your local AHJ for specific requirements. Flag for review