User: WHayward, Location: California
Asked on: Saturday, September 20, 2025 at 4:44 pm EDT
Answered on: Saturday, September 20, 2025 at 4:45 pm EDT
Question: I have customer who called me for an unrelated project. While there I found that the contractor who built a “Tiny house” for an AirB&B ran a single 12/2 Romex in flexible nonmetallic 1/2 PVC conduit from the panel over the roof of the primary home down the back side, under ground and came up under the tiny house. Then out of the pvc “bare Romex for a single circuit to run the whole place.The customer mentioned that guest trip the breaker often and the owner had to remove the provided hairdryer prevent tripping.Going over the roof is still the most practical route to bring the new feeder over. The roof is flat tar and gravel. Planning to use 1” EMT.I have not encountered this specific situation before. From what I have read, EMT conduit with rain tight fittings is acceptable, but the question is how to secure the 40 ft run. Do I need to secure the EMT to the roof every 10ft or secure the EMT to blocks that can move to allow for expansion?Secondly, is a pressure treated 4x4 block of wood acceptable or should a listed support device be used?
Okay, this is a tricky situation with a lot of code violations (past and present!) that need to be addressed. Let's break it down
Addressing the Existing Problem (Before Adding Anything)
Immediate Danger
The existing installation is a major fire and safety hazard. Bare Romex in conduit, especially buried directly, is a HUGE NO-NO. This needs to be addressed immediately. It's not rated for that type of installation and is likely already damaged. The fact that it's tripping is a good sign something is severely overloaded or faulty.
NEC Violations Galore
Romex (NM-B Cable) Use
NM-B cable is never allowed in wet locations, underground, or in conduit that is likely to hold water. The existing install violates NEC 300.3(B), 300.5, 300.8 and Article 334.
Improper Burial Depth
Even if it were rated for underground use, Romex needs significantly more burial depth than likely provided.
Overcurrent Protection
A single 12 AWG circuit is very likely insufficient for a tiny house, especially with appliances like hairdryers.
Conduit Fill
Running only 1 circuit of Romex through 1/2" PVC is fine, but the Romex type being directly exposed is a safety and fire concern.
Unapproved modification
The owner has modified the installation by removing the hairdryer to "fix" a tripping issue.
Your Proposed Solution: EMT Conduit Over the Roof EMT with Raintight Fittings
Yes, EMT with raintight compression fittings is a good choice for this application, assuming you use proper conductors inside and follow code requirements.
Wire Type
You must use individual conductors rated for wet locations inside the EMT conduit.
THHN/THWN-2 is the most common and appropriate type. Do not use Romex inside the conduit. Calculate the required wire gauge based on the load and distance, considering voltage drop. If the tiny house uses a lot of electricity, you might need to upsize.
Securing the EMT Conduit on a Flat Tar and Gravel Roof
This is where it gets a little nuanced. You have to balance code compliance with the realities of the roof type. Here's the breakdown:
Code Requirements
NEC 358.30 dictates EMT support. Generally, EMT must be securely fastened within 3 feet of every box, fitting, or termination and at least every 10 feet thereafter.
The Problem with Direct Attachment
Attaching directly to a tar and gravel roof is problematic for a few reasons:
Roof Damage
Penetrating the roofing membrane creates a leak risk.
Expansion/Contraction
EMT will expand and contract with temperature changes. Rigidly fixing it to the roof could stress the conduit, fittings, or even the roof itself.
Acceptable Solutions
Non-Penetrating Supports (Best Option)
These are weighted supports designed to sit on the roof without penetrating it. They often have a channel or clamp for securing the conduit. These are specifically designed for rooftop applications and allow for thermal expansion and contraction. Look for brands like "RoofTop Anchors," "Erico Caddy," or similar.
Spacing
Follow the manufacturer's instructions for spacing these supports. They are designed to handle the weight and environmental factors.2.
Blocks with Straps (Acceptable with Careful Planning)
If using blocks, use a durable, weatherproof material. Pressure-treated lumber can be used, but it's crucial to select lumber treated with the correct chemicals for electrical applications.
CAUTION
Some older pressure-treating chemicals can corrode aluminum conduit. Use ACQ-treated lumber or, better yet, consider using composite lumber or plastic blocks specifically designed for this purpose.
Straps
Use approved conduit straps (e.g., EMT straps) to secure the EMT to the blocks. Make sure the straps are compatible with EMT and the block material.
Block Attachment
The key is to not rigidly attach the blocks to the roof. The blocks should be able to move slightly to accommodate expansion/contraction. Use rubber pads or similar materials underneath the blocks to protect the roof membrane and provide a bit of give. You could glue the pads to the blocks.
Spacing
Even with blocks, follow the 10-foot maximum spacing rule.
Why Listed Supports are Preferred
Listed supports have been tested and certified to meet specific safety standards, including load-bearing capacity, resistance to environmental factors, and compatibility with electrical materials. They provide a more reliable and code-compliant solution than improvised methods.
Important Considerations
Roof Load
Make sure the roof can handle the additional weight of the conduit, supports, and wiring.
Local Codes
Check with your local building department for any specific requirements or restrictions on rooftop conduit installations.
Additional Considerations Disconnect
Install a readily accessible disconnect (circuit breaker or fused disconnect) at the tiny house, as required by code. This allows for safe servicing.
Grounding
Proper grounding is critical. Run a separate grounding conductor (green or bare) inside the conduit along with the circuit conductors. Bond the EMT conduit at both ends. Also make sure the tiny house has a grounding electrode system (ground rod, etc.) if required by the NEC.
GFCI Protection
Ensure all circuits in the tiny house that serve receptacles or appliances in wet locations (kitchen, bathroom, exterior) are GFCI protected.
Load Calculation
Perform a thorough load calculation to determine the correct size of the feeder. Consider all the appliances and equipment in the tiny house.*
Permitting and Inspection
Obtain the necessary permits and have the installation inspected by a qualified electrical inspector.
In Summary1. Immediately address the existing hazardous wiring. Disconnect it entirely and inform the customer of the extreme safety risk.2. Plan a code-compliant installation using EMT conduit, THHN/THWN-2 wire, and proper support methods. Non-penetrating supports are highly recommended.3. Ensure proper grounding and overcurrent protection.4. Perform a load calculation to size the feeder appropriately.5. Obtain permits and inspections.
This is a complex project that requires careful planning and execution. Consult with a licensed electrical engineer or experienced electrician if you are unsure about any aspect of the installation. Flag for review