Question: I'm powering an IT server rack on an inverter generator, through UPSs. The transfer from mains to generator will be manual (unplugging equipment from home and plugging into generator; there will never be any connection between mains and generator). For safety, I know I should bond neutral to "ground" at the generator. This system should run nominally and be safe from "ground faults" inadvertently making equipment cases live/hot.But the whole system is now floating. Should I connect the generator "ground" to earth ground in order to put the whole system at a known potential?Note that there is equipment like cable modems within the rack that have earth ground connected to them via their coaxial inputs. But I don't think the ground potential gets from them to the balance of the equipment through ethernet cables and such. Nor are any of these cables heavy copper in any way.What think you?

Okay, let's break this down. You've got a good understanding of the core issues and potential problems. Here's a comprehensive assessment and recommendation

Understanding the Setup and Concerns
Inverter Generator + UPS + IT Rack

This is a fairly common off-grid or backup power scenario. Inverter generators provide cleaner power (THD/voltage stability) than older, conventional generators. The UPS units act as buffers, smoothing out any generator fluctuations and providing seamless transfer in case of brief outages.


Manual Transfer

This avoids the complexities (and dangers) of automatic transfer switches and potential backfeeding. It does require diligence to ensure no connection ever exists between the generator and mains simultaneously.

Neutral-Ground Bonding at Generator

You're correct; this is generally recommended and is
required by code in most jurisdictions when using a generator as a separately derived system (SDS). It's done to provide a return path for fault currents, allowing breakers to trip and clear faults. Without it, a ground fault can energize equipment chassis without tripping a breaker, creating a shock hazard.

Floating System

With the generator neutral bonded to its frame ("ground"), and no other connection to earth ground, the entire rack and its connected equipment are essentially floating at an undefined voltage relative to earth.

Coaxial Cable Ground

This is the key sticking point, and the core of your question. You're correct that the coax
does create a connection to earth ground.

Analysis and Recommendations


You're right to be concerned about the floating system. While it might seem "safer" because there's no direct path to ground, the reality is that it can create unpredictable voltage potentials and increased risk of shock.Here's a breakdown of the risks and benefits of grounding, and my ultimate recommendation

Risks of NOT Grounding (Floating System):

Increased Shock Hazard

A floating system can build up static charge or be influenced by capacitive coupling to other grounded objects. If a ground fault occurs, the chassis of equipment could become energized to a high voltage relative to earth. Touching that chassis and earth ground simultaneously could deliver a dangerous shock.

Difficult Fault Clearing

While neutral-ground bonding at the generator
does allow for some fault clearing, it's less effective without a connection to earth ground. The impedance of the neutral-ground bond at the generator may limit the fault current, slowing down breaker tripping and increasing the potential for damage.

Unpredictable Voltage Potentials

The floating system can drift to random voltages relative to earth, making troubleshooting difficult and potentially causing erratic equipment behavior.

Susceptibility to EMI/RFI

A properly grounded system provides a low-impedance path for noise and interference, reducing susceptibility to electromagnetic and radio frequency interference (EMI/RFI). This can be important for sensitive IT equipment.

Risks of Grounding (and How to Mitigate Them)



Ground Loops

This is the primary concern with grounding a floating system that already has a ground connection (coaxial cable). Ground loops occur when multiple paths to ground exist, creating circulating currents that can induce noise, hum, and even damage sensitive equipment.

Mitigation of Ground Loops
Ground Lift Adapters: Absolutely NOT. Do not use "ground lift" adapters (cheaters). They are a dangerous workaround that removes the safety ground and increases the risk of shock. Never do this.

My Recommendation



Bond the generator frame to earth ground, BUT do it carefully and deliberately to minimize ground loop risks.


Here's how:1. Single Point Ground

This is the key to avoiding ground loops. Establish a
single point where the generator "ground" (the generator frame, which is bonded to the neutral) is connected to earth ground. Ideally, this connection should be made at the rack itself, where your equipment is located.2.

Grounding Electrode

Use a proper grounding electrode (ground rod) driven into the earth near the rack. Follow local electrical codes for the size and type of grounding electrode.3.

Heavy Gauge Ground Wire

Use a
heavy gauge copper grounding wire (e.g., #6 AWG or larger, depending on your local code requirements) to connect the generator frame (or the designated grounding point on the rack that's bonded to the generator neutral) to the grounding electrode. Keep this wire as short and direct as possible.4.

Additional safety measure

A single point ground can only mitigate ground loops; it cannot remove them completely. Because of this, I strongly recommend only using network cables with galvanic isolation at each end. These use electronic components (usually transformers) to isolate the grounds between connected devices. A ground loop will be stopped cold at this point. Do this.

Why this approach?
Safety

It provides a safe path for fault currents, allowing breakers to trip quickly and preventing equipment chassis from becoming dangerously energized relative to earth.

Known Potential

It establishes a defined voltage potential relative to earth, preventing the system from drifting to unpredictable voltages.


Ground Loop Mitigation

The single point ground minimizes the risk of ground loops. By ensuring there's only one intentional connection to earth ground, you prevent circulating currents from flowing through multiple ground paths.

EMI/RFI Reduction

It provides a low-impedance path for noise, improving the performance and reliability of your IT equipment.

Important Considerations



Local Electrical Codes

Always comply with your local electrical codes and regulations. These codes are designed to ensure safety and may have specific requirements for grounding generators and IT equipment. Consult with a qualified electrician if you're unsure.

Surge Protection

Consider installing surge protection devices (SPDs) at the generator output and at the rack to protect your equipment from voltage surges and spikes.


Testing

After making the ground connection, test the system to ensure that everything is working correctly. Use a multimeter to check the voltage between the equipment chassis and earth ground. It should be close to zero. Use a ground fault tester to verify that the grounding system is working as intended.

Generator Placement

Place the generator on a level surface and ensure it's properly ventilated. Protect it from the elements (rain, snow, etc.).

In summary:
Bond neutral to "ground" at the generator, and then establish a single-point* connection from the generator "ground" (or a ground bus bar within the rack that's bonded to the generator neutral) to a dedicated earth ground rod. Use heavy gauge wire and keep the connection as short as possible. Galvanically isolate ethernet connections. Follow local electrical codes, and test the system thoroughly. This will provide the safest and most reliable grounding solution for your IT rack powered by an inverter generator. Flag for review