Topic: 210.23 (A) (1)

User: Mr.electric, Location: Minneapolis

Asked on: Saturday, September 20, 2025 at 10:09 pm EDT
Answered on: Saturday, September 20, 2025 at 10:10 pm EDT

Question: I have an issue were I have two small refrigerators on the same circuit on an engineered print. My question is do both of the appliances combined have to be no more than 80% of ampacity. Or can it be 100 of ampacity as long as individually both appliances are both under the 80% ampacity.

This is a common question and it's important to get it right for safety. Here's the breakdown based on the National Electrical Code (NEC), which is the standard for electrical installations in the US

The 80% Rule and Continuous Loads

The 80% rule applies to continuous loads. A continuous load is defined as a load where the maximum current is expected to continue for 3 hours or more. Refrigerators are generally considered continuous loads because they cycle on and off frequently for extended periods.

NEC Requirements 210.20(A) Overcurrent Protection. Branch-circuit conductors and overcurrent protection devices shall have an ampacity not less than the noncontinuous load plus 125 percent of the continuous load. This means you must calculate the total continuous load and multiply that total by 1.25 (equivalent to 80% of the circuit's ampacity).

How to Apply it to Your Refrigerators1. Determine the Amp Draw of Each Refrigerator

Look at the nameplate on each refrigerator. It will list the running amps (sometimes called "full load amps" or FLA). This is the number you'll use in your calculation.2.

Calculate the Continuous Load

Since refrigerators are continuous loads, you need to treat their entire amp draw as continuous.3.

Calculate the Required Circuit Ampacity

Add the amp draw of both refrigerators together. Multiply that total by 1.25. This is the minimum circuit ampacity you need.4.

Select the Correct Breaker and Wire

Choose a breaker and wire size that meet or exceed the required circuit ampacity calculated in step 3.

Example
Refrigerator 1: 5 amps Refrigerator 2: 6 amps1. Total Load: 5 + 6 = 11 amps2. Continuous Load Multiplier: 11 amps 1.25 = 13.75 amps3. Minimum Circuit Ampacity: 13.75 amps. You would need a circuit with at least 13.75 amps capacity.

Common Circuit Sizes and Limitations
15-amp circuit

After applying the 80% rule (15 0.8 = 12 amps), you can only safely load it to 12 amps with continuous loads.

20-amp circuit

After applying the 80% rule (20 0.8 = 16 amps), you can only safely load it to 16 amps with continuous loads.

In the above example, a 15-amp circuit would be insufficient. A 20-amp circuit would be required.
Important Considerations Starting Amps

Refrigerators draw significantly more current when they first start up (inrush current or locked rotor amps - LRA). The breaker needs to be able to handle this surge without tripping. Standard breakers are usually fine for this, but if you're having nuisance tripping, you might need a slow-blow breaker or a larger circuit. However, the continuous load calculation MUST be followed.

Other Loads on the Circuit

If there are any other outlets or lights on the same circuit as the refrigerators, you need to factor in their potential loads as well. Treat anything that could run for 3 hours or more as a continuous load.


Local Codes

Always check your local electrical codes, as they may have more stringent requirements than the NEC.

Engineering Judgment

As an engineer, you have the responsibility to make sound judgments. If you have any doubts, err on the side of caution and specify a larger circuit.

In Summary

You
cannot simply assume that as long as each refrigerator is under 80% individually, you are okay. You MUST calculate the total* continuous load (including both refrigerators) and ensure that the circuit has enough ampacity to handle 125% of that total. This means you cannot exceed 80% of the breaker rating with the combined refrigerator load (after the 1.25 multiplier is applied).

Disclaimer:
This information is for general guidance only. Always consult with a qualified electrical engineer or electrician to ensure your electrical installations meet all applicable codes and safety standards. Improper wiring can lead to fire and electrocution hazards. Flag for review