Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: NEC Demand Factors- Main panel vs Sub panels, Lighting Loads

User: MEP246, Location: Barbados

Asked on: Sunday, September 21, 2025 at 2:47 pm EDT
Answered on: Sunday, September 21, 2025 at 2:56 pm EDT

Question: There are many examples online of calculations to find the service size based on the NEC.I am unsure, however, about how the demand factors should be applied to panel schedules, especially in the case of subpanels.How are the calculated demand factors applied to a panel schedule when there is a subpanel? Would the following example be correct? There are 4 Fastened in place appliances in a dwelling. A 75% reduction to the Fastened in place appliance load would be made to size the main breaker and wire. Two of these appliances are on a sub-panel. When sizing the breaker and cable for this subpanel, do we take this fastened in place load at 100%?In terms of the lighting loads, would you need tohave a specific square footage associated with each subpanelcalculate the minimum lighting load based on Table 220.12 and this fractional sqft of the whole buildingFind the demand from the calculated minimum lighting load (if the actual lighting load on the panel is less than the calculated value) and any other applicable loadsThanks

Okay, let's break down how demand factors are applied to panel schedules, especially when dealing with subpanels, and address your specific questions about fastened-in-place appliances and lighting loads.

General Principles NEC Focus

The National Electrical Code (NEC) aims to ensure electrical systems are safely sized for the
expected maximum load. Demand factors are tools to avoid over-sizing systems based on the likelihood that not all connected loads will operate at their maximum simultaneously.

Cumulative Approach

You generally work from the point of use (the appliance, light fixture) up to the service entrance. Each level (subpanel, distribution panel, service) needs to be adequately sized to handle the calculated demand from the level below.

Accurate Records

Proper panel schedules and load calculations are essential for documenting the system's capacity and future expansion.

Addressing Your Example (Fastened-in-Place Appliances)


Your scenario involves 4 fastened-in-place appliances in a dwelling unit, with two of these on a subpanel.1. Service (Main Panel) Calculation

Calculate the total nameplate load of all 4 fastened-in-place appliances. Apply the 75% demand factor to this total per NEC 220.53. This reduced load is then added to the other calculated loads (lighting, general receptacles, etc.) to determine the overall service (main panel) demand. You use this total demand to size the service entrance conductors and the main overcurrent protective device (main breaker).2.

Subpanel Calculation



Yes, you generally take the fastened-in-place load at 100% on the subpanel.
The 75% demand factor for fastened-in-place appliances is typically only applied once at the service (or a main distribution panel that feeds multiple subpanels). Here's the rationale: The NEC assumes that the subpanel is dedicated to serving the loads connected to it. While it's possible that those appliances won't all run at full load simultaneously, the code doesn't provide a specific demand factor to apply again at the subpanel level for those same appliances. It is conceivable that the loads on a sub-panel would be in constant or near-constant use. Therefore, calculate the total nameplate load of the two fastened-in-place appliances on the subpanel. Add this load to any other loads (e.g., lighting, receptacles) served by the subpanel to determine the total subpanel load. Use this total subpanel load to size the subpanel's conductors and overcurrent protection.

Important Considerations Regarding Fastened-in-Place Appliances

What counts as fastened in place? It is generally intended to mean that a appliance is installed permanently, and connected to the buildings electrical system, and is expected to remain. A portable air conditioner is generally not "fastened in place" but a built-in, window-mounted air conditioner, may be considered so.

Addressing Lighting Loads and Subpanels


Your question about lighting loads and subpanels is also important. Here's how to approach it:1. Minimum General Lighting Load (Table 220.12)

Yes, you do need to determine the square footage served by each subpanel. This is often the trickiest part. You need to carefully consider which areas of the building are powered by each subpanel. Apply the volt-ampere (VA) per square foot requirement from NEC Table 220.12 to the square footage served by each subpanel. This gives you the minimum general lighting load for that subpanel. You must always have a sufficient feeder for any lighting load.2.

Actual Lighting Load vs. Minimum

Calculate the actual connected lighting load on each subpanel (based on the wattage of the installed fixtures). If the actual lighting load is greater than the minimum calculated load (from Table 220.12), use the actual load in your subpanel calculations. If the actual lighting load is less than the minimum calculated load, use the minimum load in your subpanel calculations. The NEC wants you to account for potential future expansion of lighting.3.

Lighting Demand Factors (Table 220.42)

Once you have determined the appropriate lighting load (either actual or minimum) for each subpanel, you might be able to apply a demand factor from NEC Table 220.42. However, this demand factor is typically only applied to the general lighting load for the entire service (main panel) calculation. Applying it at the subpanel level is usually not appropriate.

Key Points and Example


Let's illustrate with a simplified example: Dwelling Size

2000 sq ft


Appliance 1

Water Heater (4500W on subpanel A)

Appliance 2

Electric Range (8000W on subpanel A)


Appliance 3

Dryer (5000W on subpanel B)

Appliance 4

Electric Furnace (10000W on Main Panel Only)


Subpanel A serves

500 sq ft of living space

Subpanel B serves

500 sq ft of living space


Main Panel serves

1000 sq ft of living space

Calculations


Main Panel

Minimum General Lighting Load: 1000 sq ft 3 VA/sq ft = 3000 VA Fastened in Place Appliances Load: 4500 + 8000 + 5000 + 10000 = 27,500 VA Demand Factor (Fastened in Place): 27,500 0.75 = 20,625 VA Total Minimum Demand Load: 3000 + 20,625 VA = 23,625 VA.2.

Subpanel A

Minimum General Lighting Load: 500 sq ft 3 VA/sq ft = 1500 VA Fastened-in-Place Appliances Load: 4500 VA + 8000 VA = 12,500 VA (No further demand factor applied here for the appliances) Total Subpanel A Load: 1500 VA + 12,500 VA = 14,000 VA3.

Subpanel B

Minimum General Lighting Load: 500 sq ft 3 VA/sq ft = 1500 VA Fastened-in-Place Appliances Load: 5000 VA (No further demand factor) Total Subpanel B Load: 1500 VA + 5000 VA = 6500 VA

Summary
Apply demand factors at the appropriate level (usually the service entrance or a main distribution panel). Subpanels generally receive the full calculated load of the equipment they serve. Accurately determine the square footage served by each subpanel for lighting load calculations. Prioritize safety by ensuring all components are sized adequately for the expected maximum load.* When in doubt, consult with a qualified electrician or electrical engineer, and always refer to the latest edition of the NEC and local amendments.Remember that this information is for educational purposes and should not be considered a substitute for professional advice. Always consult with a qualified electrician or electrical engineer for specific project needs and to ensure compliance with all applicable codes and regulations. Flag for review

Previous Question Next Question