Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Assistance with wire ampacity

User: jcrafty, Location: New York

Asked on: Monday, September 22, 2025 at 9:22 am EDT
Answered on: Monday, September 22, 2025 at 9:28 am EDT

Question: Hello,Looking at coming up with the maximum ampacity for a #6 MTW wire rated at 105 degrees C. Bit confusing with all the different NEC ampacity tables. 3 conductors will originate on a distribution block in a large custom control cabinet ( about 4' x3') with breakers and relays for a piece of machinery. Cabinet door will have a door mounted load actuator disconnect switch on it. About 6 ' of wire will extend from the block inside to the switch and then back to another distribution block in the cabinet. The distribution blocks are rated at 120 degrees C but i dont see a temp rating of the load switch. Anyways trying to determine which table to use for this application. The load switch and fusing for the new setup is rated at 80 amps so i want to make sure #6 would be rated for 80 or if i have to go up in size. Thx

Okay, let's break down this situation and determine the correct ampacity for your #6 MTW wire.

Understanding the Key Factors Wire Type

#6 MTW (Machine Tool Wire) rated 105°C. This is crucial because it allows us to potentially use a higher ampacity than other common wire types.


Conductor Count

You have 3 current-carrying conductors (CCCs) together in the cabinet.

Termination Temperature

This is the limiting factor. You stated your blocks are rated for 120C but the switch is unknown, we need to assume 75C.

NEC Article Considerations
Article 310: Conductors for General Wiring

This is the main article that contains the ampacity tables.

Article 404: Switches
Article 300: Wiring Methods - Installation methods and their impact on ampacity (e.g., conduit fill). Article 310.15: Ampacity Adjustment Factors

This is where you'll find the rules for derating ampacity due to the number of conductors in a raceway or cable.


Article 110.14(C): Termination Temperature Limitations

This is extremely important! It states that the temperature rating of the equipment terminals (breakers, switches, etc.) must be considered. You must use the lowest rated termination when determining the allowed ampacity.

Step-by-Step Analysis
1. Identify the Limiting Termination Temperature

Your distribution blocks are rated for 120°C, that's good!

The Load Switch is the unknown



THIS IS THE MOST IMPORTANT THING TO DETERMINE.
Since you don't know the temperature rating of the load switch, you must assume a maximum termination temperature of 75°C. This is a common and conservative approach when the termination temperature is not explicitly marked. If you can determine the actual temperature rating of the switch, it could potentially change the outcome.2. Find the Base Ampacity in Table 310.16

This table is for conductors rated 60°C through 90°C. It provides ampacities based on the termination temperature. You will need to base this on either 60C, 75C, or 90C rating of the wire based on the termination temp limits. For #6 AWG copper conductors: 60°C Column: 55 Amps 75°C Column: 65 Amps 90°C Column: 75 Amps3.

Apply Termination Temperature Correction (if necessary)

Since you've already determined the termination temperature limitation (75°C), you

MUST
use the ampacity value from the 75°C column of Table 310.16. This is because of 110.14(C). Therefore, #6 copper wire is rated for 65 Amps maximum.4. Check for Adjustment/Derating Factors (Number of Conductors)

You have 3 current-carrying conductors. Because you have only 3 conductors you are not required to derate the ampacity per table 310.15(C)

Conclusion


Based on the information provided and assuming a 75°C termination temperature for the load switch, #6 MTW copper wire is NOT suitable for an 80-amp load. The maximum ampacity for #6 copper under these conditions is 65 amps.

Recommendations1. Verify Load Switch Termination Temperature

Absolutely essential. Look for markings on the switch itself or consult the manufacturer's documentation. If it is rated for 90°C, this changes the calculations and could make #6 acceptable, but you would still need to verify the suitability of other components.2.

Increase Wire Size

The safest and most straightforward solution is to increase the wire size to #4 AWG copper. This will provide more than adequate ampacity even with derating and termination temperature limitations. This provides you with 85 amps and eliminates any question.

Important Considerations and Cautions
Local Codes and Regulations

Always consult local electrical codes and regulations, as they may have additional requirements.


Voltage Drop

While ampacity is critical, also calculate voltage drop, especially over longer runs. Undersized conductors can cause excessive voltage drop, leading to equipment malfunction.

Overcurrent Protection

The overcurrent protection (breaker or fuse) must be sized appropriately to protect the conductors, but not larger than the equipment it's feeding is rated for.


Safety First

If you're not a qualified electrician, consult with one to ensure the installation meets all safety standards and codes.

Summary of Answer


Based on the information you provided, you will need to increase to #4 wire to be compliant with code. Flag for review

Previous Question Next Question