Question: What would prevent one from piping directly into these fixture @ one end and out the other? Splicing not allowed in fixture?
You're asking about the possibility of running a continuous length of pipe through a light fixture housing, essentially using the fixture as a junction box without actually connecting to the fixture's electrical components.Here's why that's generally not allowed and what prevents you from doing it: Code Violations (NEC)
The National Electrical Code (NEC), which is adopted in many jurisdictions, heavily restricts how electrical boxes, including light fixture housings, can be used.
Fill Capacity
Electrical boxes are sized for a specific number of conductors and devices. Running pipes through them without accounting for that volume throws off the fill calculations and can lead to overheating and unsafe conditions.
Intended Use
Electrical boxes are designed and listed for making electrical connections. They're not designed or listed for simply being a pass-through for pipes.
Physical Damage Protection
While a fixture housing provides some protection to the wiring/connections inside, it's not intended to provide continuous protection along a pipe run in the way that conduit is.
Access
The NEC requires proper access to junction boxes and splices for inspection and maintenance. If the fixture is covering a splice that should be accessible, that's a violation.
Listing and Labeling
Light fixtures (and their housings) are tested and listed by organizations like UL or ETL. This listing covers their intended use: supporting the fixture, connecting the fixture to the electrical system, and providing a safe enclosure for those connections. Using them as a pass-through would void that listing because it's outside of the manufacturer's design and testing.
Fixture Integrity
The fixture housing is not designed to withstand the stresses associated with continuous pipe runs (expansion, contraction, accidental impacts, etc.). You could damage the fixture housing over time, creating a safety hazard.
Wire Derating
Running conductors near heat producing equipment must be accounted for. More wires requires larger gauge.
Space Constraints
The fixture housing is often too small to accommodate the necessary fittings and the pipes themselves, while also leaving room for the fixture wiring.
Splices
Splices are not always prohibited in fixtures, but they must be made properly, using approved methods, and within the space provided in the fixture designed for that purpose. They are generally avoided as much as possible.
Alternatives
Junction Box
If you need to make a connection point or run a continuous length of pipe, use a proper junction box that is sized appropriately for the number of conductors, wire sizes, and any devices.
Conduit
If you need to protect the conductors along the entire run, install conduit.
In short, don't run pipes directly through light fixture housings. It's against code, unsafe, and can damage the fixture. Use proper junction boxes and conduit as needed. When in doubt, consult a qualified electrician. Flag for review