Question: Even though you need to handle tie or provide multi pole breaker when using MWBC I would still think it would be cheaper than a job where you had to install dedicated neutrals. IMO it would be a lot more copper depending on the magnitude of the work. Agree?
You're right in your core assessment: MWBCs can be cheaper than running dedicated neutrals, especially for larger jobs, primarily due to copper savings. Here's a breakdown of why and some factors to consider
Why MWBCs can be Cheaper (in terms of copper):
Shared Neutral
The whole point of an MWBC is to share a single neutral conductor between two or more circuits operating at 120V. This immediately reduces the amount of copper needed for the neutral runs. In a standard 2-circuit scenario (two 120V circuits), you'd need two hots and two neutrals (4 wires). With an MWBC, you need two hots and one neutral (3 wires).
Long Runs
The longer the circuits are, the more pronounced the savings become. Every foot of wire saved on a long run multiplies the cost reduction significantly.
When Dedicated Neutrals are More Expensive in Copper
Large Projects
The more circuits you run and the longer their runs are, the more you'll notice the copper savings by using MWBCs.
Factors to Consider and Potential Counterarguments
Labor Costs
MWBCs, while saving on copper, can sometimes slightly increase labor. You need to ensure proper phasing on the breaker panel to avoid issues.
Tie/Handle Tie or 2-Pole Breaker
You must have a way to disconnect both (or all) hot legs of the MWBC simultaneously. This usually means a 2-pole breaker or handle ties on two single-pole breakers. The cost of this breaker or handle tie kit needs to be factored in, although it's typically minor compared to copper savings on a decent size job.
Voltage Drop
The neutral in an MWBC carries the unbalanced load. If the loads on the two circuits are very unbalanced, the neutral current can be higher, potentially requiring a larger neutral conductor to avoid voltage drop. This could partially negate some of the copper savings. However, in most residential scenarios, the loads are reasonably balanced, and the standard neutral size is adequate.
Circuit Separation
Dedicated neutrals guarantee complete isolation between circuits. This can be important in sensitive applications or if there's a risk of one circuit interfering with another (e.g., audio equipment). However, this is rarely a concern in typical residential wiring.
Future Flexibility
Dedicated neutrals offer more flexibility in the future. If you decide to add a new circuit, you already have a neutral run to the desired location. With MWBCs, you're "locked in" to sharing the neutral.
Troubleshooting
Some electricians find troubleshooting MWBCs slightly more complex than dedicated neutral circuits.
Conclusion:
In most* residential wiring scenarios, especially for larger projects or longer circuit runs, MWBCs will likely result in lower overall copper costs compared to running dedicated neutrals for each circuit. The cost of the tie/handle tie or 2-pole breaker is usually negligible compared to the copper savings.However, carefully consider the potential increase in labor, the possibility of unbalanced loads requiring a larger neutral, and any specific requirements for circuit isolation or future flexibility before deciding to use MWBCs. Flag for review