Question: I have a job coming up where I'll be changing out the service to a very old duplex, installing meter pack (two meters two main breakers) and re-feeding a interior panel. Its a duplex and right now it has asingle riser to a double meterbase outside and a main service panel in each basement fed with a SE cable (3-wire).There is a ground rod and metal water pipe in the basement of each duplex.Yes I dont know how they drove ground rods in basements here but not the first time I have seen it.There are plans to add a PV system to each roof if that affects your opinions on anything.Is there any way i can keep the SE cable and service disconnects in the basement and call the meter pack a EM disconnect?I rather not mess with the existing panels.Thanks
Okay, this is a common scenario, especially with older duplexes. Let's break down the situation and the code implications, and then discuss the best options for your job, especially considering the future PV installation.
Understanding the Code (NEC Relevant Sections) 230.70 Location of Service Disconnecting Means
This section is critical. It requires that the service disconnecting means be readily accessible, and generally located either inside or outside of the building, and as close as practicable to the point of entrance of the service conductors.
230.71 Maximum Number of Disconnects
Generally, you are allowed a maximum of six service disconnecting means for each service. A meter pack with two main breakers counts as two service disconnects.
230.85 Emergency Disconnects
Now required on all one and two family dwellings. This disconnect must be readily accessible and located outside of the building.
250 Grounding and Bonding
Proper grounding is essential. You'll need to ensure your grounding electrode system meets the requirements.
690 Solar Photovoltaic (PV) Systems
This section addresses the specific requirements for PV systems. It's important to plan for the PV integration upfront.
Analysis of Your Current Situation1. Current Setup
You have a single service drop feeding a double meter base. From each meter, SE cable runs to a main panel in each basement. Each basement also has a ground rod and a metal water pipe for grounding.2.
Problem
The main disconnects are in the basements, which may or may not meet the "readily accessible" and "closest practicable location" requirements of 230.70. Additionally, emergency disconnects are now code for one and two family dwelling.
Can the Meter Pack be Considered an Emergency Disconnect? The key to this working is the location
If the location of the meter pack is considered easily accessible and meets the "as close as practicable" requirement, and emergency disconnect requirement, you may be able to leave the existing panels where they are and call them subpanels.
Grounding and Bonding
If you do this, make sure you properly isolate the neutral from the ground in each panel.
Considerations for PV Systems Increased Load
Adding PV systems increases the overall load on the service. Verify that the existing SE cables and the new meter pack are adequately sized for the combined load. Conduct a load calculation according to Article 220.
Backfeed
The PV systems will feed power back into the grid. The meter pack and service disconnects must be rated to handle this backfeed current.
PV Disconnects
The PV system will require its own disconnecting means, both AC and DC, as outlined in Article 690. These disconnects must be accessible and clearly labeled.
Rapid Shutdown
Many jurisdictions now require rapid shutdown systems for PV arrays. This usually involves a switch near the array that can quickly de-energize the PV conductors.
Point of Connection
Determine where the PV inverters will connect to the electrical system. This may influence the location of the PV disconnects and any required overcurrent protection.
Recommendations
Given the requirements for emergency disconnects and the future addition of PV systems, here's my recommended approach:1. Install the Meter Pack as Service Disconnects
Install the meter pack with two main breakers at a location that is easily accessible and meets the "closest practicable" and "emergency disconnect" requirements. This is generally outside the building, near the existing meter location, where it can be readily accessed by emergency personnel.2.
Treat Existing Panels as Subpanels
After the meter pack, the existing panels in the basements become subpanels. This means:
Separate Neutrals and Grounds
Absolutely critical. In each subpanel, the neutral and ground buses must be separated. The neutral bus should only be bonded at the service disconnect (the meter pack main breakers).
Bonding the Subpanel Enclosure
The subpanel enclosure must be bonded to the grounding electrode conductor system (usually via a wire to the ground bus).
Adequate Grounding
Ensure the grounding electrode system is robust and meets the requirements of Article 250. This might involve supplementing the existing ground rods and metal water pipe electrode with additional electrodes or a grounding ring.
3.
Sizing
Make sure to properly size and overcurrent protect everything according to NEC.
Next Steps1. Consult with the Inspector
Before starting any work, discuss your plan with the local electrical inspector. They can provide guidance on local interpretations of the code and any specific requirements in your area.2.
Load Calculation
Perform a detailed load calculation for each unit, including the anticipated PV system output. This will ensure that the service entrance conductors, meter pack, and subpanels are adequately sized.3.
Detailed Diagram
Create a detailed wiring diagram of the proposed system, including all components, wiring sizes, and grounding connections. This will help you stay organized and ensure that everything is installed correctly.
Important Cautions Never compromise on safety. Ensure that all work is performed by a qualified electrician and meets all applicable codes.* Document everything. Keep accurate records of all work performed, including load calculations, wiring diagrams, and inspection approvals.By following these recommendations, you can ensure that your service upgrade is safe, code-compliant, and ready for the addition of PV systems in the future. Good luck with your project! Flag for review