Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Accessibility - temp const pwr 120/240V sub panelboard

User: Isaiah, Location: Baton Rouge

Asked on: Tuesday, September 23, 2025 at 9:04 am EDT
Answered on: Tuesday, September 23, 2025 at 9:04 am EDT

Question: On this construction site they have several temporary, sub-fed Panelboards with padlocks. I’m assuming the superintendent has the keys. But he’s usually in a trailer several hundred feet away. Is this a NEC accessibility violation?Enviado desde mi iPhone utilizando Tapatalk

Yes, depending on the specific circumstances, it's likely a violation of NEC requirements for accessibility and working space around electrical equipment. Here's a breakdown of why, and the relevant code sections

NEC Concerns and Key Code Sections:
Accessibility for Qualified Persons (110.26(D))

The NEC mandates accessibility for qualified persons to electrical equipment for inspection, maintenance, and operation. This is to ensure safety and efficient troubleshooting/repair. A padlock could be a barrier to accessibility if the qualified person doesn't have immediate access to the key. "Immediate" is the key word.

Working Space (110.26(A))

The NEC requires adequate working space around electrical equipment to permit safe operation and maintenance. If the superintendent with the keys is "several hundred feet away," it significantly increases the time and effort required to access the panel in an emergency. This delay could create a hazardous situation. The required working space (depth, width, and height) depends on voltage, and other factors, and should be maintained clear.

Lockout/Tagout (While Not Directly a Violation, Related Consideration)

While not directly addressed by the above NEC sections, the lockout/tagout procedures are used to prevent inadvertent energizing of equipment during service or maintenance. Padlocks are commonly used for this purpose, but in these situations, the authorized employee would have a key or combination to the lock.

Why It's Likely a Violation


Delayed Access

The superintendent being far away means there's a significant delay in accessing the panelboard in an emergency or for necessary maintenance. Consider these scenarios:
Tripped breaker needs resetting. Someone is getting shocked and power needs to be cut immediately. Equipment is malfunctioning and needs immediate power shutoff. Routine maintenance or inspection is required.Having to walk several hundred feet to get a key adds unacceptable risk.2.

Impractical Accessibility

The accessibility requirement implies that qualified persons can readily access the equipment. A padlock where the key is not readily available significantly hinders this.

Acceptable Alternatives/Solutions



Key Box at the Panelboard

Install a secure key box (like a Knox Box or similar) right at the panelboard location. Only authorized personnel (including qualified electricians on site) should have access to the code or key to the key box.

Multiple Key Holders

Ensure that multiple qualified personnel on site have keys to the padlocks. This provides redundancy.


Electronic Access Control

Use an electronic access control system (keypad, card reader) to control access to the panelboard enclosure. This allows for controlled and readily available access for authorized personnel.

Proper Lockout/Tagout Procedure and Practices

Make sure a proper lockout/tagout procedure is in place if used.

Important Considerations



Qualified Person

The NEC refers to "qualified persons." This means someone who has the skills and knowledge related to the construction and operation of the electrical equipment and installations and has received safety training to recognize and avoid the hazards involved.

Emergency Situations

Think about the worst-case scenario. What happens if there's an electrical fire, a shock incident, or equipment failure that requires immediate power shutoff? The delay in accessing the panelboard could be life-threatening.


AHJ Interpretation

The Authority Having Jurisdiction (AHJ) makes the final determination on code compliance. It's always best to discuss any concerns with the AHJ before implementing a solution.

Recommendation:


Immediately address this issue. The easiest short-term solution is to ensure that multiple qualified personnel on-site have access to the padlock keys. A better long-term solution would be to install a secure key box near the panelboard(s). Consult with a qualified electrical contractor and the AHJ to determine the best approach for your specific situation and to ensure compliance with the NEC. Flag for review

Previous Question Next Question