Question: can anyone tell me why there are two numbers listed for each phase in the panel schedules? I have minimum experience but I've always only seen one value per phase

The two numbers you're seeing on a panel schedule for each phase likely represent the load (Amps or VA) on each leg of that phase. Here's a breakdown of why this is commonly done, and what the numbers likely mean

Understanding the Basics
Panel Schedules

These documents detail the electrical loads (like lighting, outlets, appliances, motors) connected to each circuit breaker within a panelboard. This helps ensure the panel is properly loaded and balanced.


Phases (A, B, C)

In a three-phase system, the power is split into three separate AC waveforms, each offset by 120 degrees. This provides smoother and more efficient power delivery. Most residential panels are single phase, meaning they use two legs of a 3-phase system.

Balanced Load

Ideally, the loads on each phase should be as close to equal as possible. An unbalanced load can lead to:
Increased neutral current (which can overheat conductors) Reduced power efficiency Voltage fluctuations

Why Two Numbers?


The two numbers on a panel schedule per phase (A, B, or C) are likely to show the load on each leg of that phase. Single Phase Example

If you have a 120 volt circuit on phase A, it will use one leg of phase A, and the neutral. The two numbers would show how much load is on each leg of phase A.


Three Phase Example

If you have a 208/120 volt circuit connected to phase A, B, and C, the two numbers would show how much load is on each leg of each respective phase.

Common Scenarios Where You'll See This


Individual Circuits

For example, a single 120V lighting circuit connected to "Phase A" will only draw current from one "leg" of that phase. The other leg would ideally show 0 (or very minimal) load.2.

Shared Neutral Circuits (Multi-Wire Branch Circuits)

In these circuits, multiple 120V circuits share a single neutral conductor. These circuits are often split between two phases (e.g., one on Phase A, one on Phase B, sharing a neutral). You'll see load listed for both legs of both phases.

What the Numbers Represent



Load (Amps or VA)

The units will usually be indicated at the top of the panel schedule (e.g., "Load in Amps," or "Load in VA").


Amps (A)

The actual current draw of the connected loads.

Volt-Amps (VA)

The apparent power, which is a measure of the total power being used, including reactive power (power that is stored and returned to the source). VA is important for sizing transformers and other equipment. You can convert VA to Amps using the formula: `Amps = VA / Voltage`. (Use the appropriate voltage, usually 120V or 240V depending on the circuit).

How to Interpret the Numbers


Check the Units

Ensure you understand whether the numbers are in Amps or VA.2.

Compare Loads Within a Phase

Look at the two numbers for each phase. Are they significantly different? If so, that phase might be unbalanced.3.

Calculate Total Phase Load

If you want to see the total load on each phase (A, B, C), add up the loads on both legs of that phase.4.

Compare Phase Loads to Panel Rating

Compare the total load on each phase to the panel's rated capacity. You want to ensure you are not exceeding the panel's or its main breaker's rating.

Example Panel Schedule Snippet (Illustrative)
| Circuit | Description | Phase A | Phase B | Phase C

---------|------------------------|---------|---------|---------
1 | Lighting - Office 1 | 2.0 0 | 0 | 0
2 | Receptacles - Office 1 | 3.5 0 | |
3 | HVAC Unit 1 | 0 | 10 0 | |In this (simplified) example



Circuit 1 (Lighting)

Phase A, leg 1 has 2 Amps, phase A, leg 2 has 0 Amps.

Circuit 2 (Receptacles)

Phase A, leg 1 has 3.5 Amps, phase A, leg 2 has 0 Amps.


Circuit 3 (HVAC)

Phase B, leg 1 has 10 Amps, Phase B, leg 2 has 0 Amps.

Important Considerations

*

Diversity Factor/Demand Factor

Real-world installations often have a diversity factor or demand factor applied. This acknowledges that not all loads will be running at their maximum simultaneously. Consult the relevant electrical codes and standards (e.g., NEC in the US) for guidance on applying these factors.

If you can provide a snippet or photo of the panel schedule you're looking at, I can give you more specific guidance.