Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: New electric service

User: TnD1w, Location: Wisconsin

Asked on: Tuesday, September 23, 2025 at 10:43 am EDT
Answered on: Tuesday, September 23, 2025 at 11:06 am EDT

Question: I have an off-grid cabin in Northern Wisconsin that is currently powered by solar and generator. There is no power at the road, and due to the high bedrock, the cost to bring in power has been astronomical. Instead of paying the high utility fee, it has been suggested that I install a private lateral instead. The utility will not provide me with any voltage other than 120/240v 1ph. The plan is to set the meter adjacent to an existing transformer and then extend the private service 1,600 feet to the residence, and the utility has blessed the design concept. Due to the long service run, a 600v step-up and step-down transformer will be utilized. In anticipation of pulling the electrical permit, I wanted to create a one-line diagram so I could force myself to size the conductors and conduits. The one-line is still a works in progress, but I sure could use some help verifying a few items:There will be a fused disconnect at the start of the system. I'm torn if this disconnect should have a bonded neutral.The transformers are 2 wire, 1ph, 600v. I suspect a neutral is not needed between the two transformers?If the meter, fused disconnect, and step-up transformer were grounded and the disconnect, step-down transformer, and house panel were grounded; is a ground wire needed between the two installations? I need to set a ground at the meter because this project will be completed in stages.Is the 60a 600v disconnect required before the step-down transformer? I thought the disconnect could be eliminated if the remote location of the fused disconnect was identified. Does the 60a disconnect need fuses?Wisconsin allows 8' before the panel. Is this measured in plan or by wire run? If in plan, the existing house panel will be close enough to the service entry. If it's by wire length, the panel would be too far away. This would be a moot point if the non-fused disconnect stays in the design?The existing house panel has a bonded neutral. Does the presence of the fused disconnect make the panel a subpanel, so the screw should be removed?If there are any other items of criticism that you'd like to share, I'd be open to the feedback.Ok, so how do I attached a pdf of the one-line?

You've got a good grasp of the core issues here. This is a more complex install than usual and requires careful consideration of grounding, overcurrent protection, and voltage drop. Let's break down each question

Regarding the Fused Disconnect at the Start of the System:
Bonded Neutral? This is tricky. Ideally, you would not bond the neutral at this disconnect. You only want one neutral-to-ground bond in the entire system, and that will be at the service entrance (typically in your house panel). The purpose is to provide a low-impedance fault current path back to the source. Multiple bonds can cause circulating neutral currents, which are undesirable. However, the fact that you'll be working on this in stages complicates matters. Since you will be setting the meter first, you may need to provide a separately derived system ground at the transformer. This would be accomplished by bonding the transformer to the ground and the ground wire to the neutral.

Regarding the Transformers and the Neutral



No Neutral Needed Between Transformers

Correct. These are single-phase, two-wire transformers, stepping the voltage up and down. The primary and secondary windings are isolated (except for the ground connection). A neutral conductor is not required between them. You'll have two "hot" wires at 600V running between the transformers.

Regarding Grounding



Grounding at Both Locations and Ground Wire

Yes, a ground wire
is needed between the meter/transformer location and the house/transformer location. While each location will have its own ground rod(s), these are not sufficient for fault current. You need a properly sized equipment grounding conductor (EGC) run with your 600V conductors to provide a low-impedance path for fault current to return to the source and trip the overcurrent device (fuse or breaker). This EGC connects the transformer enclosures and any metallic conduit to ground.

Regarding the 60A 600V Disconnect Before the Step-Down Transformer



Disconnect Requirement

This may be required, and you need to confirm with your local inspector. The NEC allows for exceptions if the remote disconnect is clearly labeled and accessible. However, local codes often have more stringent requirements. A disconnect at the house provides a readily accessible way to de-energize the entire system.

Fuses in the Disconnect

If you
do need a disconnect, it doesn't necessarily have to be fused. However, you must ensure that the overcurrent protection (fuses at the first disconnect) are sized appropriately to protect both the conductors and the transformers. Often, it's simpler to have fuses in the second disconnect too, sized to protect the lower-voltage side conductors.

Regarding the 8' Rule for Service Entry



Measurement

This is almost certainly by wire length. The intent of the rule is to limit the length of unprotected conductors inside the building. Check with your local inspector to confirm their interpretation. If the existing panel is too far away by wire length, you will need to install a disconnect closer to the point where the wires enter the building.

Regarding the Bonded Neutral in the House Panel



Subpanel?
Yes! With the addition of the fused disconnect and step-down transformer, your house panel becomes a subpanel. The neutral must be isolated from ground in the subpanel. Remove the bonding screw or strap. Again, only one neutral-to-ground bond is allowed in the entire system.

Additional Considerations



Transformer Protection

Ensure the transformers are adequately protected against overcurrent on both the primary and secondary sides. Transformer damage is expensive. The inrush current of the transformer also needs to be taken into consideration when choosing the correct size breaker.

Voltage Drop Calculation

Extremely important over 1600 feet. Use a voltage drop calculator (available online) to determine the
minimum conductor size needed to keep voltage drop within acceptable limits (typically 3% for branch circuits and 5% overall). This will be a significant factor in your conductor sizing. Calculate the maximum voltage at the end to make sure you stay under 127v at the outlet (120v + 6%).

Lightning Protection

Northern Wisconsin is prone to lightning. Consider adding surge protection devices (SPDs) at both ends of the 600V run, as well as at the main panel in the cabin.

Conduit Fill

Ensure you calculate the correct conduit size for the conductors, including the ground wire. Use appropriate fill charts and derating factors.


Conductor Type

Select conductors rated for the voltage, temperature, and wet location (Northern Wisconsin). THWN-2 or XHHW-2 are common choices.

Grounding Electrode System

Verify that your grounding electrode system (ground rods) at both locations meets code requirements. Typically, two ground rods at least 8 feet apart are required. Consider a ground ring buried at least 2.5 feet in the earth.

To Attach the PDF

Unfortunately, you can't directly attach a PDF in this text-based interface. The best option is to describe your one-line diagram in detail, including the components, their ratings (voltage, current), and the conductor sizes you've chosen. This will allow me to review it and offer more specific feedback. I'm happy to look it over if you re-type it here.

Crucial: Get the Inspector Involved Early


This is a project where communication with your local electrical inspector is absolutely essential. Discuss your design with them
before you start purchasing materials or installing anything. They can provide valuable guidance and ensure that your installation meets local code requirements and will pass inspection. They are there to help you!Disclaimer: I am an AI Chatbot and not a licensed electrician. This information is for general guidance only and does not constitute professional electrical advice. Always consult with a qualified electrician for any electrical work.* Flag for review

Previous Question Next Question