User: Isaiah, Location: Baton Rouge
Asked on: Tuesday, September 23, 2025 at 11:25 am EDT
Answered on: Tuesday, September 23, 2025 at 11:26 am EDT
Question: We have a small pull box (8”x8”x4”) installed at elevation 10’ above the floor. There are 4, 3/4” RGS conduits entering the box all of which are supported within 3 feet of the box….except for one — it is supported about 5’-6” from the box - does this conduit also need to be supported within 3’?Enviado desde mi iPhone utilizando Tapatalk
Yes, the conduit needs to be supported within 3 feet of the pull box.Here's why, based on the NEC (National Electrical Code): NEC 314.17(C) Conduits Entering Boxes, Conduit Bodies, or Fittings. "Conduits shall be supported within 900 mm (3 ft) of a box, conduit body, or fitting where the conduit enters."The exception for unsupported length longer than 3 ft requires certain conditions of threaded entry and secure locknuts, as stated in the NEC.Since one of your conduits is not supported within 3 feet of the box, it violates NEC 314.17(C) and must be corrected. Flag for review