Question: Hi everybody Can you put a 2 pole 20a gfi breaker on a share neutral circuit to protect both circuit

No, you cannot directly put a 2-pole 20A GFCI breaker on a shared neutral circuit (also known as a multi-wire branch circuit or MWBC) to protect both circuits without taking additional steps. Here's why, and what you need to do instead

Why It Doesn't Work Directly:
GFCI Balancing

A GFCI (Ground Fault Circuit Interrupter) breaker works by constantly monitoring the current flowing through the hot (ungrounded) conductor(s) and comparing it to the current returning through the neutral (grounded) conductor. If there's a difference of 5 milliamps or more, it assumes current is leaking to ground (a ground fault) and trips the breaker.


Shared Neutral Complexity

In an MWBC, the neutral conductor carries the difference in current between the two hot legs. If you simply connect a 2-pole GFCI, it will see the normal, balanced current of the MWBC as an imbalance and trip immediately or intermittently. The GFCI sees the load on the other circuit as a ground fault when it is not.

What You Must Do to Protect MWBCs with GFCI


2-Pole GFCI Breaker for MWBCs Specifically Designed for Shared Neutrals

You need to use a 2-pole GFCI breaker specifically designed for MWBCs (multi-wire branch circuits) with a shared neutral. These breakers are designed to handle the expected imbalance of current on the neutral in an MWBC.2.

GFCI Receptacles

An alternate approach is to use GFCI receptacles as the first outlet on each of the branch circuits.

Important Safety Considerations



Qualified Electrician

Always consult with a qualified electrician for any electrical work. Working with electrical systems can be dangerous. They will be able to properly assess your situation, recommend the right solution, and install it safely and according to local electrical codes.

Code Compliance

Electrical codes (like the NEC in the US) have specific requirements for GFCI protection and MWBCs. Your installation must comply with these codes.

Testing:
After installation, thoroughly test* the GFCI breaker or receptacles to ensure they are functioning correctly.In summary, protecting an MWBC with GFCI is possible, but it requires the correct type of GFCI breaker or GFCI receptacles and proper installation by a qualified electrician. Don't attempt to do it yourself without the necessary expertise. Flag for review