Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 220.12

User: pedro1200, Location: Ny

Asked on: Tuesday, September 23, 2025 at 1:26 pm EDT
Answered on: Tuesday, September 23, 2025 at 1:27 pm EDT

Question: Am I understanding this correctly? Table 220.12 gives us va value per sq ft for calculating general lighting load (which only includes lighting loads. Yet for dwelling and offices it directs you to J, k to calculate for both lighting and power (receptacle) but if you only had lighting going to J,K is not necessary, correct?

You are getting close, but there are a few nuances. Let's break it down: Table 220.12: General Lighting Loads by Occupancy This table provides a minimum VA per square foot for calculating the general lighting load for various occupancies. As you correctly stated, this is the starting point for determining the minimum calculated load for lighting. It is often referred to as the "base load." Important: It doesn't necessarily only include lighting loads. In many occupancies (like dwellings), the VA/sq ft figure is meant to cover general receptacle outlets that are not dedicated to specific appliances or equipment. Dwelling Units (220.14(J)) and Other Outlets (220.14(K)) 220.14(J): Dwelling Units. This section states that each receptacle outlet is calculated at not less than 180 VA when determining the total load. The number of outlets is based on the requirements of 210.52. 220.14(K): Other Outlets. This is a catch-all for all other outlets not specifically accounted for in other sections (like dwelling unit receptacles or specific appliance circuits). These are calculated at 180VA per outlet.

So, to your specific question

> Yet for dwelling and offices it directs you to J, k to calculate for both lighting and power (receptacle) but if you only had lighting going to J,K is not necessary, correct?


Dwellings (220.14(J))
: Even if you only have lighting, you still need to account for the receptacle outlets in the dwelling unit at 180 VA per outlet (using 220.14(J)). This is because the code assumes that general-purpose receptacle outlets will be present and used. The VA/sq ft in Table 220.12 is not usually enough to cover the outlets, so we account for them additionally using 220.14(J). Offices (220.14(K)): If you only have lighting in an office space, and no receptacle outlets, then you would not need to use 220.14(K) since it is only for other outlets. However, this is extremely unlikely in a typical office. Offices almost always have general-purpose receptacle outlets, and you would need to account for them at 180VA each.

Key Takeaways and Clarifications



Minimums

Table 220.12 provides a
minimum. You can always use a higher VA/sq ft value if you know the actual connected lighting load is higher.

Outlets

220.14(J) and (K) are primarily about receptacle outlets, not lighting. Always use them for dwelling units and other occupancies unless there are absolutely no general-purpose receptacle outlets.

In summary:
1. Use Table 220.12 for the general lighting load based on square footage and occupancy type.
2. For dwelling units always add the 180VA per receptacle outlet, per 220.14(J)3. For other occupancies, add the 180VA per receptacle outlet, per 220.14(K) unless there are absolutely no general-purpose receptacle outlets.I hope this clarifies the issue for you. Let me know if you have any more questions. Flag for review

Previous Question Next Question