User: gdsodrnk1, Location: Baltimore
Asked on: Tuesday, September 23, 2025 at 3:09 pm EDT
Answered on: Tuesday, September 23, 2025 at 3:16 pm EDT
Question: This article addresses the support of FMC. Specifically it states, "FMC shall be securely fastened in place by an approved means within 300mm(12in) of each box, cabinet, conduit body, or other termination...."Exception 2 allows this distance to be increased if the FMC is installed for flexibility after installation. The distances are increased from "the last point where the FMC is securely fastened".Is a connector, for a transformer install, considered a "securely fastened" point? For exception 4, a connector is specifically allowed as a means of securement and fastening.
Let's break this down based on the provided information and standard electrical practice: General Rule
FMC must be securely fastened within 12 inches of termination points (boxes, cabinets, conduit bodies, etc.).
Exception 2 (Flexibility After Installation)
This increases the allowable distance from the last point where the FMC is securely fastened (NOT the termination point).
Exception 4
This specifically allows a connector to be used as a securement and fastening means.
Answering your question: Is a connector, for a transformer install, considered a "securely fastened" point?Yes, if it is approved and used as a fastening means. Exception 4 is key here. It explicitly states that a connector can serve as a securement point. Therefore, if the connector is approved for this purpose (i.e., listed as a suitable fastening method) and installed correctly, it is considered a securely fastened point.
Important Considerations and Caveats
"Approved" is critical
The connector must be listed or approved for the specific purpose of securing and fastening FMC. Read the listing on the connector itself. This information will be on the connector packaging. Simply being a connector doesn't automatically qualify it as a securement point.
Proper Installation
The connector must be installed correctly according to the manufacturer's instructions. Improper installation will invalidate its use as a securement point.
Application of Exception 2
If you are using Exception 2 to increase the distance, that increased distance is measured from the last secure fastening point, which could be the connector if it meets the above criteria.
Local Amendments
Always check for local amendments to the electrical code. Some jurisdictions may have stricter requirements.
In summary, a connector can* be a "securely fastened" point for FMC, but only if it's an approved connector used correctly for that purpose. If it is, then Exception 2 would apply with the increased distance calculated from the connector.Disclaimer: I am an AI Chatbot and not a qualified electrician. This information is for educational purposes only and should not be considered a substitute for professional advice. Always consult with a licensed electrician for any electrical work. Always refer to the specific, adopted electrical code in your jurisdiction. Flag for review