Question: Hello, I'm looking for someone who might be able to help point me in the right direction on hooking the subject transfer switch and genset together. I have run contacts from 178 and 183 in the GTS out to the genset and landed those on TB5 (Remote Start) and TB1 (Ground). Have tested the generator in manual, it starts and runs just fine, generates electricity as it is supposed to. When we disconnect utility service and hold down the Fast Test Mode switch, the generator starts, comes up to speed and the GTS transfers power to the load. This has the appearance of working as it should, however if we don't disconnect utility service ahead of time, the transfer switch seems to feed power through both the utility and the generator (as noted by the nearby a/c unit ramping up dramatically when we tried the transfer). The transfer switch mechanism is working, so I don't how to explain why it seemed like we were sending electricity from both sources, but it does. We have disconnected the utility service, started the generator manually and manually transferred the GTS and that works fine. I have manuals for both the GTS and the Genset, but haven't been able to diagnose my issue yet, so I thought I would check the forum. Also note, when we put the GTS in Normal Test Mode, nothing happens (although I'm not sure yet whether this is simply a timer that we have set too long, or if it is a further issue). Licensed electrician working on this, just not one that is familiar with this GTS.Any thoughts on where we might have stumbled or ideas on what to look for would be appreciated. Thanks in advance.
Okay, this is a common issue and you're doing the right things by testing and having a licensed electrician involved. Let's break down the likely culprits and troubleshooting steps.
Understanding the Problem
The key issue is the apparent paralleling of the utility and generator. This is dangerous and must be resolved before putting the system into operation. Paralleling occurs when the utility power and generator power are simultaneously connected to the load. Transfer switches are designed to prevent this by ensuring only one source is connected at any given time.
Possible Causes and Troubleshooting Steps
1.
Mechanical Failure of the Transfer Switch (Least Likely, but Possible)
Inspection
Even though it seems to be working, closely inspect the transfer mechanism itself. Are the contacts making clean, positive connections on each side? Look for physical damage, warping, or loose connections. Sometimes contacts can become worn or pitted.
Operation
Watch the transfer process very closely. Can you definitively see one set of contacts fully opening before the other set closes? Even a brief overlap can cause paralleling.
Resistance Test
With all power off (utility and generator), use an ohmmeter to check the resistance between the utility input and generator input on the load side of the switch in both the utility and generator positions. Ideally, it should be an open circuit (infinite resistance). If there is any continuity, it indicates a potential fault.2.
Incorrect Wiring of the Transfer Switch's Control Circuit
Verify Wiring Diagram
Absolutely double-check the wiring against the transfer switch's manual, especially the control wiring that operates the transfer mechanism. Pay close attention to any interlock circuits or logic that prevents paralleling.
Incorrect Phase Sequence
While less likely, it's worth confirming the phase sequence of the utility and generator are compatible with the transfer switch. Some transfer switches have phase rotation sensors that prevent transfer if the sequences are incorrect.
Neutral Connection
Ensure the neutral connections are correct. A shared neutral or improper bonding can cause all sorts of weird issues. Confirm the transfer switch properly switches the neutral if that's how it's designed.
Control Power
Verify the control power for the transfer switch is stable and within the specified voltage range. Fluctuations can cause erratic behavior.3.
Generator Synchronization (Less Likely for Basic Systems)
Voltage and Frequency Matching
While most residential generators don't actively synchronize, significant voltage or frequency differences between the generator and utility can contribute to issues. Check the generator's voltage and frequency under load and compare them to the utility voltage and frequency.4.
Issue with Fast Test Mode
Purpose
Understand how the Fast Test Mode is designed to work. It usually bypasses some of the safety interlocks and timers for rapid testing.
Isolation
The fact that it only happens in Fast Test Mode suggests the problem lies in the way that mode is operating.
Troubleshooting
Refer to the transfer switch manual's section on Fast Test Mode. Look for specific conditions or limitations that might be causing the paralleling. It's possible there's a specific setting or condition required for proper operation.5.
Normal Test Mode Not Working
Timer Settings
As you suspect, the most likely reason is the timer. Verify the timer settings are correct and set to a reasonable duration.
Control Circuit Issue
It could also indicate a problem with the control circuit responsible for initiating the normal test. Trace the wiring and check for loose connections or faulty components.
Voltage
If the voltage is to low the timer relay will not activate and the timer will not start.6.
Genset Wiring (Review the GTS manual to ensure that the wires should go where you have them. The genset manual might also have a wiring diagram.) Remote Start Circuit
Double-check the polarity and function of the remote start circuit on the generator. Are you using a normally open or normally closed contact from the transfer switch? Is the generator configured to respond to that signal?
Genset control may have a delay when starting the gen set which will allow the Transfer switch to switch while energized.
Specific Steps to Take
1.
Disable Utility Power (Important Safety Precaution)
Before doing any further testing, turn off the main breaker to your house to completely isolate the utility power.2.
Detailed Visual Inspection
Thoroughly inspect the transfer switch and its wiring, looking for loose connections, damaged wires, and any signs of overheating or arcing.3.
Ohmmeter Testing (Power OFF)
Perform the resistance tests described above to check for continuity between the utility and generator inputs when the switch is in both positions.4.
Step-by-Step Operation Analysis
With the utility power still off, manually trigger the transfer switch (if possible) and carefully observe the mechanical operation. Take videos if you can to capture the sequence of events.5.
Consult with the Manufacturer (If Needed)
If you're still stuck, contact the transfer switch manufacturer's technical support. They may have specific knowledge or troubleshooting tips for your model.
Important Safety Notes
Licensed Electrician
This work should be performed by a qualified and licensed electrician.
Lockout/Tagout
Always follow proper lockout/tagout procedures before working on any electrical equipment.
Voltage Testing
Use a properly rated voltage tester to verify that circuits are de-energized before touching any wires.
Safety Glasses and Gloves: Wear safety glasses and insulated gloves when working on electrical systems.By systematically following these steps and paying close attention to detail, you should be able to pinpoint the cause of the paralleling issue and get your transfer switch working correctly. Good luck! Flag for review