Topic: NM cable support

User: mannyb, Location: Florida

Asked on: Wednesday, September 24, 2025 at 12:29 pm EDT
Answered on: Wednesday, September 24, 2025 at 12:30 pm EDT

Question: Whats the secure support requirement for NM cable for feeders, branch circuits installed between a first and 2nd floor in non accessible rafters and ceiling. Can the wiring lay directly perpendicular without support ? Or Is it still required to be secured every 4.5' ?Sorry for silly question. I see this all the time in apartments. Just wondering if I was missing something where this is permitted

You're asking a great question! Here's the breakdown of NM cable support requirements in the scenario you described, and why you likely see what you see in apartments

General Rule (NEC 334.30):
NM cable (Romex) must be supported and secured every 4 1/2 feet (1.4 m). It must also be secured within 12 inches (300 mm) of every box, cabinet, fitting, or other termination.

This general rule absolutely applies to feeders and branch circuits installed between a first and second floor in non-accessible rafters and ceilings. The fact that it's "non-accessible" doesn't change the support requirements.

Why You See NM Cable Laying Perpendicular Without Support (and why it's often wrong)

You're right, it's common to see unsupported NM cable in residential construction, even though it's a code violation. Here's why it happens (but isn't legal):

Laziness/Cost Cutting

It's faster and cheaper to just run the cable without proper supports.


Ignorance

Some installers simply don't know the code requirements.

Lack of Inspection

If the work isn't inspected, or the inspector misses it, the violation persists.


Belief that "it's fine"

Some people believe that because the cable is lying on a ceiling or resting on something, it doesn't need additional support. This is incorrect. The code requires specific support methods.

Why Support is Important



Preventing Strain

Unsupported cable can sag, putting strain on the connections at boxes and devices. This can lead to loose connections, arcing, and potential fire hazards.


Protecting from Physical Damage

Even in a non-accessible area, the cable can be damaged by rodents, movement of the building, or future work in the area. Proper support helps protect the cable.

Ensuring Proper Heat Dissipation

While less of an issue with modern NM cable, closely packed and unsupported cables can have reduced heat dissipation, especially if they are carrying significant current.


Code Compliance

It's the law!

Permitted Support Methods (NEC 334.30)

NM cable must be secured by staples, cable ties, straps, hangers, or similar fittings designed and installed so as not to damage the cable. Here are some common examples:

Staples

NM staples are designed to hold the cable securely without crushing it.


Cable Ties

Cable ties can be used, but they must be listed for supporting cable. Using zip ties that are not rated for this purpose is a violation.

Straps

NM straps are similar to staples but often provide a wider bearing surface.


Hangers

Some hanger systems are designed for supporting multiple cables.

Running Boards

In some situations, NM cable can be run along a running board and secured to it.

Specifics for your situation

The space between floors (rafters/ceiling joists) does require support every 4.5 feet. Laying perpendicular to the joists/rafters does not eliminate the need for support. "Non-accessible" doesn't exempt it from the code.

In summary:
Even in concealed and "non-accessible" areas, NM cable MUST be supported according to NEC 334.30. What you see in apartments is often a violation, even if it is common.Always consult the latest edition of the National Electrical Code (NEC) and local amendments for the most accurate and up-to-date information. Also, remember to consult with a qualified electrician for any electrical work. Flag for review