Question: Hello I am installing a 400 amp meter main at the bottom of a driveway on a pedestal and feeding two 200 amp transfer switches up the hill at the house . I will have an electrode at the meter main but it is my understanding that I need an electrode at the house as well. I can not use the EGC in the feeder to serve that purpose. Some guys are saying I am wrong. After looking in article 250 section 3 seems I am correct but am wondering everyone’s opinion. In article 250.118 B 1 there is an exception saying you can use both for same purpose but I think I am confused. Thanks again for your input
You're understanding is correct. Here's a breakdown of why you need grounding electrodes at both the meter main and the house, and why the exception you're referencing doesn't apply in your situation
Why You Need Grounding Electrodes at Both Locations:
Separately Derived Systems (SDS)
You're effectively creating an SDS at each 200A transfer switch location. While you're not generating power, each transfer switch is capable of isolating the load from the utility and connecting it to a generator. This means each transfer switch location needs its own connection to ground.
Purpose of Grounding Electrodes
Grounding electrodes establish a connection to the earth, providing a low-impedance path for fault current to return to the source (in this case, the utility transformer) and tripping a breaker or fuse. This minimizes the risk of dangerous voltage on metal parts.
Code Requirement
As you noted,
NEC 250.32(A) generally requires a grounding electrode system at each building or structure supplied by a feeder or branch circuit, where the supply conductors include a grounding conductor (EGC). Since you are feeding your house, this section applies.
Why the Exception in 250.32(B)(1) Doesn't Apply (and why your EGC alone is not sufficient)
The Exception
250.32(B)(1) is the key to this question. Here's what it effectively says: The grounding electrode system at the remote building is NOT required where... a qualified person ensures the equipment grounding conductor is run with the feeder or branch circuit and sized in accordance with 250.122 based on the overcurrent protective device protecting the feeder or branch circuit and that there are no continuous metallic paths bonded between the buildings.
Key Concepts
The key is "continuous metallic paths." If you have any metallic path between the meter main pedestal and the house besides the conductors in your underground feeder, you need to add the required electrode at the house as well. Things that could be a "continuous metallic path" include: Metallic water piping connecting both locations. Metallic gas piping connecting both locations. Buried metallic conduit systems. Underground communication or data cables with metallic shielding. Any other metallic structure providing a low-resistance path.
In your scenario, the key is that the EGC in the feeder conduit is NOT designed to function as the sole path for a significant fault current returning from a ground fault within the house. Using the EGC alone to bond to the grounding electrodes at the meter main does not provide adequate fault current path impedance reduction in all likely scenarios.
In summary
Install a grounding electrode system (ground rod, ground ring, etc.) at the meter main pedestal. Install a separate grounding electrode system at the house (at each transfer switch, if you have multiple buildings/structures). Bond the grounding electrode system at the house to the transfer switch enclosures. The EGC in your feeder run connects the meter main's grounding system to the house's electrical panels for equipment grounding, but it does not replace the need for a separate grounding electrode system at the house.
Important Considerations
Local Codes and AHJ
Always consult your local electrical codes and the Authority Having Jurisdiction (AHJ) for specific requirements in your area. They may have additional or stricter rules.
Qualified Person
As a general rule, only a licensed electrical contractor should perform electrical work.
250.50 Grounding Electrode System, where available, the grounding electrode system must include: (1) Metal Underground Water Pipe, (2) Metal In-Ground Support Structure, (3) Concrete-Encased Electrode, and (4) Ground Ring.
In short, you are correct to install an electrode at the house in addition to the meter main. Flag for review