Question: Hello, just looked at a hot tub install. It will be installed next to an Air Conditioning condenser unit. The condenser is prob 3 ft from hot tub. I googled the topic, and mostly found that since the condenser is not an outlet, as long as the ac disconnect is more then 5 feet, its no problem. But may need to be bonded to hot tub if within 5 ft.Figured a better strategy is to break out my 2023 code book. It looks like they added 680.41B. Which if i am reading this correctly, says no electrical equipment, other then spa or hot tub can be located within 5 ft from tub. Unless permanent barrier is installed.Am I reading this correctly? Thanks in advance for any insight
Yes, you are reading 680.41(B) of the 2023 NEC correctly. Let's break it down: 680.41(B) Other Electrical Equipment and Wiring
This section directly addresses the placement of electrical equipment and wiring near spas and hot tubs.
"Unless specifically permitted by this article, other electrical equipment and wiring, other than that associated with the spa or hot tub, shall not be installed under, over, or within 1.5 m (5 ft) horizontally from the inside walls of a spa or hot tub." This is the key part. It prohibits other electrical equipment (like your AC condenser) within 5 feet of the hot tub's inside walls, unless explicitly allowed elsewhere in Article 680. Exception No. 1
"Underground wiring shall be permitted where encased in rigid metal conduit, intermediate metal conduit, or rigid nonmetallic conduit."
Exception No. 2
"Electrical equipment installed in a listed and labeled enclosure for use within the 5-foot boundary shall be permitted."
Exception No. 3
"Where separated from the spa or hot tub by a permanent barrier that prevents contact by a person occupying the spa or hot tub."
In your situation
The AC Condenser
Your AC condenser, which is electrical equipment not associated with the hot tub, is within 5 feet of the hot tub. This violates 680.41(B).
2.
The Disconnect
The distance of the AC disconnect is a separate issue. You still need to comply with 680.41(B) regardless of disconnect location.
Solutions
You have a few options to comply with the code:1.
Move the AC Condenser
This is the most straightforward solution. If possible, relocate the AC condenser more than 5 feet away from the hot tub.2.
Install a Permanent Barrier
As per Exception No. 3, you could build a permanent barrier (e.g., a solid wall) between the hot tub and the AC condenser. The barrier must be substantial enough to prevent someone in the hot tub from touching the AC unit.3.
Listed Enclosure
If there's a listed and labeled enclosure for use within the 5 ft boundary, that might be an option for the AC unit. However, this is less likely as it's usually for electrical panels, not large appliances.
Important Considerations
Local Codes
Always check with your local electrical inspector. Local codes might have additional requirements or interpretations.*
Hot Tub Requirements
Make sure to follow all manufacturer's instructions for the hot tub's electrical connections, grounding, and bonding.
In summary, you are correct in your reading of 680.41(B). The presence of the AC condenser within 5 feet of the hot tub violates the code unless you implement one of the allowed exceptions (moving the unit or installing a barrier). Flag for review