Question: Hi,I am studying for my next license using snapz. I keep getting VD answers wrong because sometimes the question wants me to use the formula Evd=i X r and other times is the Evd= (1.73 for 3p) 2 k i d.How are you supposed to know which one to use in a scenario? It seems like branch circuits mostly get the I x R, but i cant figure it out. Super frustrating
You've hit a common point of confusion! Understanding when to use which voltage drop formula is crucial for accurate calculations. Let's break down the differences and provide guidance.
Understanding the Formulas EVD = I x R (Ohm's Law) `EVD` = Voltage Drop (in volts) `I` = Current (in amps) `R` = Resistance (of the conductor, in ohms) EVD = (1.732) x 2 x K x I x D / CM (or simplified: EVD = (2 x K x I x D) / CM for single phase) `EVD` = Voltage Drop (in volts) `1.732` = Square root of 3 (used for 3-phase calculations) `2` = accounts for two conductors in single-phase (line and neutral or two hots) `K` = Direct-current constant of the conductor material (typically 12.9 for copper, 21.2 for aluminum - these are approximations) `I` = Current (in amps) `D` = One-way Distance (in feet) `CM` = Circular Mils (of the conductor - use a wire table to find this)Key Differences and When to Use Each1. Level of Detail
EVD = I x R
This is the fundamental voltage drop calculation based on Ohm's Law. It's precise if you know the exact resistance (R) of the specific conductor under the specific conditions (temperature, etc.) It's often used for short, simple circuit segments where you can reasonably determine the exact resistance.
EVD = (2 x K x I x D) / CM or EVD = (1.732) x 2 x K x I x D / CM
This is an approximation formula designed for longer circuit runs to make the calculation quicker and is more aligned to calculating total Voltage Drop. It relies on using standardized K values (which are approximations themselves) and one-way distance. It also requires you to know the conductor's circular mil area (CM).2.
Availability of Information
I x R
Use this when you have been given, or can precisely calculate the
actual resistance (R) of the conductor in question. This is less common in typical licensing exam scenarios where you don't have all the data to precisely compute R. Formulas using K, D, CM
Use this when you are given, or can look up: Conductor material (to determine K) One-way distance (D) of the circuit Conductor size (to determine CM from a wire table) Whether the circuit is single-phase or three-phase.3.
Typical Scenarios
I x R
Rarely used directly for long branch circuits in licensing exams. Might be used to calculate voltage drop across a specific component (e.g., a resistor in a control circuit). Might be used as part of a larger problem where you first calculate the resistance of a short conductor segment.
Formulas using K, D, CM
Very commonly used for calculating voltage drop in branch circuits and feeders in licensing exams. These are designed for the scenarios where you need to find the voltage drop over a significant distance of wire.
Here's a decision-making process
Read the Problem Carefully
What information is provided?2.
Identify the Circuit
Is it a branch circuit or a feeder? Is it single-phase or three-phase?3.
Look for Resistance (R)
Does the problem explicitly give you the resistance (R) of the conductor, or does it give you enough information to calculate it directly (e.g., length and ohms per foot)? If yes, consider I x R. If not...4.
Look for K, D, CM
Does the problem give you enough information to find K (material), D (one-way distance), and CM (conductor size)? If yes, use the formulas that include these values. This is the far more common situation.
Example to Illustrate
Scenario 1
> A 20-amp load is supplied by a 100-foot run of #12 AWG copper wire. The resistance of the #12 AWG wire is 1.98 ohms per 1000 feet. Calculate the voltage drop.
Analysis
They give you resistance per 1000 feet, and the run is 100 feet, so you can directly calculate the resistance: R = (1.98 ohms / 1000 ft) 100 ft = 0.198 ohms.
Use I x R
EVD = 20 amps 0.198 ohms = 3.96 volts
Scenario 2
> A 20-amp load is supplied by a 100-foot run of #12 AWG copper wire. Calculate the voltage drop.
Analysis
They don't give you the resistance directly. You need to use the K, D, CM formula.
Use the formula
EVD = (2 12.9 20 amps 100 feet) / 6530 CM = 7.9 volts
Why the Discrepancy in Scenario 2?
The approximation nature of the K, D, CM formula assumes a specific operating temperature. The wire table values for CM are based on standard conditions. The I x R calculation in the first scenario used resistance derived from specific data.
In summary
I x R is the fundamental law, but less practical for typical voltage drop calculations in licensing exams unless the resistance is explicitly provided or easily derived. The formulas using K, D, and CM are designed for typical branch circuit/feeder voltage drop calculations over longer distances.Tips for Success on Snapz (and the Exam)
Practice, practice, practice
The more you work through problems, the better you'll get at recognizing which formula to use.
Read the questions very carefully
Pay attention to the units and the information provided.
Make a formula sheet
Have both formulas handy and know what each variable represents.
Understand the limitations of the K, D, CM formula
It's an approximation, so don't expect pinpoint accuracy.
Focus on the most common* scenario: In most licensing exam voltage drop problems, you'll be using the formulas with K, D, and CM.By understanding the nuances of these formulas and practicing, you'll conquer those voltage drop questions! Good luck with your studies and the exam! Flag for review