Question: Trying to load calc. (14) Welders to be added in a commercial building. Want to ensure I'm doing my calculations correctly. The gist of the question is when to multiply by 1.732, (If the nameplate gives values for 3ph amperes , both Imax & Ieff, do I still multiply by 1.732?)(14) 3Ph welders (using 630.11b for demand factors)Nameplate shows - 3PH @208V , Imax - 34A , Ieff - 18ALets assume 100% duty cycle for this exercise.What do yall get for a service size?

Okay, let's break down the calculation for sizing a service to handle those welders, focusing on when and why the 1.732 (square root of 3) factor is used.

Understanding the Goal

The goal is to determine the minimum ampacity required for the electrical service to safely and reliably power these welders. We need to account for: Inrush Current (Imax)

The highest current drawn, important for breaker sizing and conductor ampacity (short-term).


Effective Current (Ieff)

The average current drawn over a period, important for service size and transformer loading (long-term).

Demand Factors

Recognizing that all welders won't be operating at their maximum at the same time.

Calculations


Here's a step-by-step calculation, referencing NEC (National Electrical Code) sections where applicable

1. Individual Welder Power (kVA)

When to use 1.732

You use 1.732 when you're converting from line-to-line voltage (208V in this case) and phase current (Imax or Ieff) to 3-phase power (kVA). You do not need to divide by 1.732 if the nameplate of the welding machine specifies the 3 phase current of the input.

Imax kVA (Welder)
= (Volts Amps 1.732) / 1000 = (208V 34A 1.732) / 1000 = 12.27 kVA per welder Ieff kVA (Welder) = (Volts Amps 1.732) / 1000 = (208V 18A 1.732) / 1000 = 6.50 kVA per welder2. Applying Demand Factors (NEC 630.11(B)) NEC 630.11(B) provides demand factors for welders. Let's use the table there: Number of Welders

14

Demand Factor (from Table 630.11(B))
: .403. Calculating Total Demand Total Imax kVA = (1 12.27) + (0.85 12.27) + (0.70 12.27) + (0.60 12.27) + (0.50 12.27) + (0.45 12.27) + (0.45 12.27) + (0.40 12.27) + (0.40 12.27) + (0.40 12.27) + (0.40 12.27) + (0.40 12.27) + (0.40 12.27) + (0.40 12.27) = 36.81 kVA Total Ieff kVA = (1 6.50) + (0.85 6.50) + (0.70 6.50) + (0.60 6.50) + (0.50 6.50) + (0.45 6.50) + (0.45 6.50) + (0.40 6.50) + (0.40 6.50) + (0.40 6.50) + (0.40 6.50) + (0.40 6.50) + (0.40 6.50) + (0.40 6.50) = 19.50 kVA4. Calculating Service Ampacity Using Imax

Amps = (kVA 1000) / (Volts 1.732) = (36.81 1000) / (208 1.732) = 102.1 Amps

Using Ieff

Amps = (kVA 1000) / (Volts 1.732) = (19.50 1000) / (208 1.732) = 54.2 Amps

5. Upsizing for Continuous Load (NEC 220.18)
Welders are generally not considered a continuous load (operate for 3 hours or more at a time). Therefore, you do not need to increase the feeder/service ampacity by 125%.6. Service Size and OCPD (Overcurrent Protection Device) Service Ampacity

The
minimum service ampacity should be

102.1 Amps.
Ieff would be the deciding factor. We are sizing for the maximum current draw of 102.1 Amps, rather than the average current draw of 54.
2.
Overcurrent Protection (Breaker/Fuses)

This is where Imax comes into play. The OCPD needs to be sized to protect the conductors, but it also needs to be able to handle the inrush current of the welders without nuisance tripping. You will likely need to select an OCPD larger than 102.1 amps. Consult NEC 630.12 for guidance. Generally, an inverse time circuit breaker is recommended. You'll need to coordinate the OCPD with the wire size.

Important Considerations



Local Codes

Always check with your local electrical inspector, as they may have additional requirements or interpretations of the NEC.


Future Expansion

Consider if you might add more welders in the future. It's often wise to oversize the service slightly to accommodate future needs.

Voltage Drop

Verify that the conductor size you select will keep voltage drop within acceptable limits, especially during high-demand welding operations. This is very important with 208V systems.


Power Factor Correction

Welders can have a lagging power factor, which can increase current draw and lower system efficiency. Consider power factor correction if needed.

Harmonics

Some welding machines generate harmonics that can affect power quality. If harmonic distortion is a concern, you may need to install harmonic filters.


Coordination Study

For a large commercial building, a full coordination study is highly recommended to ensure that the entire electrical system is properly protected.*

Diversity Factor
: If you can be absolutely certain that only the first 5 welders will be operating at the same time, or any number of welders, then you can use that diversity factor.

Summary1. Calculate the individual welder's kVA based on both Imax and Ieff. Use 1.732 in this calculation.
2. Apply demand factors from NEC 630.11(B).
3. Calculate the total kVA demand for both Imax and Ieff.4. Convert kVA to Amps to determine service size.
5. The service ampacity will likely be determined by Imax.6. Choose an OCPD based on NEC 630.12, considering inrush current.

Therefore, in summary, you need a service size of at least 102.1 amps. I would highly recommend oversizing this to at least 125amps, as you are approaching the limit for the amount of weld machines being utilized. This will also give you plenty of headroom for future use. Flag for review