Topic: Portable Step Up Transformer??

User: Therealcrt, Location: Kansas City

Asked on: Thursday, September 25, 2025 at 5:11 pm EDT
Answered on: Sunday, September 28, 2025 at 3:27 am EDT

Question: I’m using talk to text so I hope this all will make senseMy boss is having me install a three phase step up transformer from 208 to 480 V on a rollaround wagon that’s bolted to it that will be used at an aircraft hangar. So the primary source of power is a 70 amp, thick SO cord with a strain relief connector coming into the transformer wire to the primary. The end of that Esso cord will have a pin and plug style end on it that will plug into a pen and plug receptacle, and that will be the main source of power for the transformer the secondary side I am directly mounting another pendant, plug style receptacle directly to the transformer, coming off the secondary side to feed that there will be no neutral present for that receptacle. I know I’ll still need to bond XO to the ground bar inside the transformer and then also I am mounting a ground lug to the backside of the transformer going to run a bear number six from it inside to my ground lug inside the transformer, and then that ground lug will also be the mechanics way to ground to the building steel or a grounding pod whenever they use this system, that will be the way it is grounded to the building. I’ve never done anything like this. I don’t know if it’s legal. I don’t know if it’s code compliant since there are jet fuel, and stuff involved. I just do what my boss tells me to do. can anyone chime in?

Okay, let's break this down. There are several potential issues here, and it's good you're asking questions. This is a situation where potentially incorrect wiring can be dangerous and costly.

Disclaimer

I am an AI and cannot provide professional electrical advice. You MUST consult with a licensed electrical engineer and/or inspector to ensure your installation is safe and code-compliant.

Here are the potential concerns and points to consider


Suitability for Hazardous Location (Aircraft Hangar)



Critical Issue

Aircraft hangars are considered hazardous locations. Jet fuel vapors are extremely flammable. Standard electrical equipment can create sparks that could ignite these vapors.


NEC Article 513

This article covers aircraft hangars. It requires specific types of equipment that are explosion-proof, intrinsically safe, or otherwise approved for hazardous locations.

Step 1: Location Classification

You need to determine the area classification within the hangar (e.g., Class I, Division 1 or 2). This dictates the types of equipment allowed. Your transformer, cord, plugs, and receptacles MUST be rated for that classification.


Likely Issues

A standard SO cord, a standard transformer (not designed for hazardous locations), and standard pin-and-sleeve connectors are almost certainly not suitable for an aircraft hangar environment.

Remedy

Consult with an engineer and/or inspector to determine the correct type of equipment, which will be

EXPENSIVE
.2. Transformer Grounding and Bonding (XO to Ground)



General Rule

You always bond the XO (neutral) of a transformer to the ground bar in the transformer enclosure. This creates a solidly grounded system. You stated you will do this - GOOD.

Grounding Electrode Conductor (GEC)

From the ground bar in the transformer, you need a proper GEC (Grounding Electrode Conductor) running to a suitable grounding electrode (e.g., building steel, a ground rod, etc.).3.

Grounding to Building Steel/Grounding Pod



Important, But Requires More Info

Relying solely on connecting to building steel or a "grounding pod" for your primary grounding electrode can be problematic.

Verify Suitable Electrode

You need to ensure that the building steel or grounding pod meets NEC requirements for a grounding electrode. Often, they do not, or the connection is inadequate. The NEC has very specific requirements for these installations.


Recommendation

Install a dedicated grounding electrode system, like a ground rod or ground ring, connected to the transformer's ground bar. Then, you can supplement that with a connection to building steel if it's known to be a good ground.4.

Equipment Grounding (Ground Wire)



Vital

You MUST have an equipment grounding conductor (ground wire) running with the 208V input cord and the 480V output wiring. This is separate from the neutral (XO).


Purpose

This ground wire provides a low-impedance path back to the source in case of a fault, tripping the breaker and preventing electrocution.

#6 Bare Wire to Building Steel

This is where I think you need more clarification. While you are using a #6 bare wire to the grounding lug on the transformer, it is going to be used as a way to ground this system to the building steel. If you have already ground the neutral wire to the ground inside of the transformer. Then it is not necessary to ground the system once more to the building steel. In fact, that is not legal. You will be creating an unbalanced system. The entire system is going to look for ground in two locations when in fact it is only needed once inside of the transformer.5.

Plug and Receptacle Ratings



Amperage

The 70-amp plug and receptacle for the 208V input MUST be rated for 70 amps or higher. The 480V plug and receptacle MUST be rated for the appropriate amperage based on the transformer's output capacity.

Voltage

Ensure both plugs and receptacles are rated for the respective voltages (208V and 480V).


Polarization

Make sure the plugs and receptacles are polarized so that the phases cannot be reversed. This is especially critical on a three-phase system.6.

Overcurrent Protection (Fuses or Circuit Breakers)



Critical

You MUST have overcurrent protection (fuses or a circuit breaker) on both the primary (208V) and secondary (480V) sides of the transformer.


Sizing

The size of the overcurrent protection must be properly sized according to the transformer's nameplate rating and NEC requirements.

Existing 70A Breaker

The 70A breaker feeding the 208V receptacle is your primary overcurrent protection for the 208V side of the transformer. You need to calculate and install appropriate overcurrent protection on the 480V side.7.

SO Cord



Suitable for Application?
An SO cord might be suitable for the input power if the entire assembly is NOT in a hazardous location. However, its flexibility and durability should be evaluated for its intended use. You may want to consider something more robust, especially if it will be dragged around. Length

Keep the cord length as short as practical to minimize voltage drop.8.

Strain Relief



Essential

Proper strain relief is crucial where the SO cord enters the transformer enclosure. This prevents strain on the conductors inside the enclosure.9.

Disconnecting Means



Required

You need a readily accessible disconnecting means (e.g., a fused disconnect switch or a circuit breaker) to completely de-energize the transformer for maintenance or emergencies.10.

Rollaround Wagon and Bolting



Stability

Ensure the rollaround wagon is stable and won't tip over easily. Bolting the transformer securely to the wagon is a good start.

Grounding

The wagon frame itself should be bonded to the transformer's ground bar.11.

No Neutral on Secondary



Understood

You mentioned there's no neutral on the 480V secondary side. This is fine as long as the loads connected to the 480V receptacle are purely three-phase and don't require a neutral.



Impact on Grounding

Because you are not using the secondary neutral, then using a #6 ground from the transformer case to the building steal/ grounding pod is a violation of NEC Code 250.6(A) Objectional current. The entire system should not be grounded again after the XO is grounded inside the transformer.

Recommendations



STOP WORK IMMEDIATELY

Do not proceed with this installation until you have addressed the hazardous location concerns and consulted with qualified professionals.

Engage a Licensed Electrical Engineer

Have an engineer review your entire design and ensure it complies with all applicable codes and standards, especially NEC Article 513. They can help you select the correct equipment for the hazardous environment.


Contact a Certified Electrical Inspector

An inspector can review the installation and ensure it meets all code requirements.

Documentation

Keep detailed records of all equipment specifications, calculations, and inspections.

In Summary:
*This project has significant potential hazards due to the aircraft hangar environment. You MUST prioritize safety and compliance by involving qualified professionals. Failing to do so could result in a fire, explosion, electrocution, or costly fines.I hope this is helpful. Please remember to get professional help! Flag for review