Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Sealing Locknut location

User: iproenergy, Location: Florida

Asked on: Friday, September 26, 2025 at 11:06 am EDT
Answered on: Sunday, September 28, 2025 at 3:28 am EDT

Question: Hey I am failing the inspection because I use a seal nut on the side of Automatic transfers switch, the inspector want us use the myerhub , mentioned the code reference 312.2 but , went I read it doesn't mention that we have to use the myer hub. I think the sealnut with the pvc male connector on the side of the ATS i correct. Some of you can help me to clarify this, thank you

Okay, let's break down the situation and the relevant code. You're right to question the inspector and dig into the details. Here's a breakdown of why the inspector might be requiring a Myers Hub and what the NEC code section 312.2 says

Understanding the Issue: Seal Nuts vs. Myers Hubs in Enclosures
Seal Nuts

A seal nut is typically used with a rigid metal conduit (RMC) or intermediate metal conduit (IMC) male adapter to secure the conduit to an enclosure and provide a watertight seal. They're also sometimes used with PVC male adapters.


Myers Hubs (also known as watertight hubs)

A Myers Hub is a fitting designed to provide a watertight seal where conduit enters an enclosure, specifically designed for use with rigid conduit. They have a gland that compresses a sealing ring around the conduit.

Why the Inspector Might Require a Myers Hub


The inspector's concern is likely related to maintaining the integrity and watertightness of the enclosure (the ATS) and compliance with the NEC. While a seal nut can provide some degree of sealing, it might not be considered sufficient for: UL Listing/Enclosure Rating

The ATS is likely UL listed and has a specific enclosure rating (e.g., NEMA 3R, NEMA 4, NEMA 4X). Using a fitting that
deviates from the manufacturer's instructions or compromises the listed rating can be a violation. ATS manufacturers often specify the use of proper watertight hubs to maintain the integrity of the enclosure rating.

Environmental Conditions

The environment where the ATS is installed is a key factor. If the location is subject to rain, splashing water, or other moisture, a Myers Hub provides a more reliable, watertight seal compared to a seal nut with a PVC male adapter.

Proper Termination

Depending on the size and type of conduit, a Myers Hub can provide a more mechanically sound and secure termination compared to a seal nut. This is important to prevent the conduit from loosening over time due to vibration or physical stress.

NEC 312.2 (Damp or Wet Locations)


Let's look at the relevant code section:
NEC 312.2 (Damp or Wet Locations). In damp or wet locations, surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least a 6-mm (1/4-in.) airspace between the wall or other supporting surface and the back of the cabinet or cutout box.Here's why this is relevant, even though it doesn't explicitly mention Myers Hubs: "Prevent moisture or water from entering..." This is the key phrase. The intent of the code is to ensure that water doesn't get inside the enclosure. The inspector is likely arguing that a seal nut with a PVC male adapter is not sufficient to reliably prevent water ingress in a damp or wet location. "Surface-type enclosures..." The ATS is likely a surface-mounted enclosure. Damp or Wet Locations

The inspector is probably classifying the location of the ATS as damp or wet. This is a judgment call based on the specific conditions.

Why You Might Be Technically Correct (But Still Need to Comply)


You might be
technically correct that 312.2 doesn't explicitly mandate Myers Hubs. The code is performance-based, meaning it focuses on the outcome (preventing water ingress) rather than prescribing specific methods. If you can prove that your seal nut/PVC male adapter combination provides an equivalent or better level of watertightness, you might have a case.

What You Should Do1. Politely Ask for Clarification

Ask the inspector
specifically what he finds deficient about your seal nut/PVC male adapter setup and why he believes it violates 312.2 or the ATS's listing. Specifically, ask why he thinks it allows moisture to enter the enclosure.
2.


Review the ATS Manufacturer's Instructions

This is crucial. Look at the installation instructions for the ATS.
Does the manufacturer specify the type of fittings to be used for conduit entry? If they require Myers Hubs (or watertight hubs), you'll have to comply.3.

Consider the Enclosure Rating

What is the NEMA rating of the ATS enclosure (e.g., NEMA 3R, 4, 4X)? Ensure that the fittings you use are rated to maintain that level of protection. A NEMA 4 or 4X enclosure, in particular, will almost certainly require Myers Hubs or equivalent watertight fittings.4.

Offer a Solution (If Possible)

If the inspector is concerned about watertightness, you could propose using a
better* sealing method with the PVC male adapter, such as using a high-quality sealant or O-ring between the enclosure wall and the adapter. Be prepared to demonstrate that this will provide a watertight seal.5.

Appeal (If Necessary)

If you've exhausted all other options and you still believe the inspector is incorrect, you have the right to appeal the decision through the appropriate channels in your jurisdiction. However, be prepared to present a strong case with supporting documentation (manufacturer's instructions, test data, etc.).

In Conclusion:


While NEC 312.2 doesn't explicitly require Myers Hubs, the inspector is likely interpreting it to mean that your installation must prevent water ingress. The key is to understand the inspector's concerns, consult the manufacturer's instructions, consider the enclosure rating, and, if possible, offer a solution that addresses the inspector's concerns while still complying with the NEC. It's often easier to comply with the inspector's interpretation, even if you disagree, to avoid delays and further inspections. Flag for review

Previous Question Next Question