Question: So am I correct in saying when you terminate RMC into a box/enclosure you could have the following terminations?1. Locknut & bushing2. Hub on end of conduit which would go into a knockout3. Female hub on box so you would just thread the conduit into the hub?
Yes, you are correct. Here's a breakdown and some additional considerations: 1. Locknut & Bushing
This is a very common method. You insert the RMC through the knockout. A locknut is tightened on the outside of the box to secure the conduit. A bushing (typically plastic, but sometimes metal) is installed on the inside of the box, over the conduit threads, to protect the conductors from abrasion during pulling.
2. Hub on End of Conduit (going into a knockout)
This refers to a conduit body that has a hub attached.
Hub is already attached
Conduit body's like LB's, LL's, and T's typically come with a hub on one end that is simply inserted into the knockout and secured with a locknut.
Hub is attached on the go
Alternatively, this could refer to a coupling or fitting that has a hub that is attached to the conduit. The hub end would then be inserted into the knockout and secured with a locknut.
3. Female Hub on Box (threading the conduit into the hub)
These are often called "threaded hubs" or "integral hubs." The enclosure itself has a threaded hub designed to accept threaded RMC directly. You simply screw the RMC into the hub. This creates a solid and often weatherproof connection.
Important Considerations
Listing and Suitability
Always ensure that the fittings and enclosures you're using are listed for the specific type of conduit (RMC) and the environment (e.g., wet location, hazardous location).
Grounding
Proper grounding is crucial. Using listed grounding bushings or locknuts is important to ensure a reliable ground path, especially when using the locknut and bushing method.
NEMA Rating
The NEMA rating of the enclosure and the fitting must be appropriate for the environment.
Knockout Size
Make sure the knockout size matches the trade size of the conduit.
Weatherproofing
For outdoor installations, use weatherproof hubs, bushings, and seals to prevent water from entering the enclosure.*
Torque: Tighten locknuts and hubs to the manufacturer's recommended torque specifications.In summary, you've correctly identified the three common methods for terminating RMC into a box or enclosure. Just remember to consider the details of each installation to ensure compliance with electrical codes and best practices. Flag for review