Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Rv site planning-understanding article 551

User: ctaylo360860, Location: colorado

Asked on: Friday, September 26, 2025 at 3:25 pm EDT
Answered on: Sunday, September 28, 2025 at 3:29 am EDT

Question: I’m looking to get confirmation I am interpreting the nec correctly, and the plan I have came up with for a 4 space possibly in future 6 space rv site doesn’t have any faults…My plan is to put a 200amp feed through 8 space panel at the pole under the poco meter.I would use the feed through lugs and run 3-250aluminum, 1-3/0aluminum quad plex in 2-1/2 pvc to first RV pedestal and then jump out the next three using the lugs at the bottom… (all 4 sites are equipped with 50,30,20amp receptacles)There will also be a main lug 100amp remote distributing panel fed from a 100amp breaker at the service. The 100amp remote distribution panel will be fed with 3-1/0 al and 1#2al quad plex in a 2” pvc conduit. This panel will be feeding a 2hp well and possible heater.I was told well motor is 3 phase, and they will be adding a phase converter. I will need to supply wire rated at 1.25% of the well motor. 2 hp 3 phase 230 volt motor should pull 6.8amps6.8amps x 1.25 = 8.5amps. After looking at Franklin aims Manuel. I thought I could run 2pole 20a ocod with #12 copper conductors down to the well pressure switch/ phase converter. Ocpd to pressure switch is less than 25 ft, and the well is 200ft down. I’m assuming we’ll company will run #10 or larger down to well motor and pump.I used the aims Manuel to come up with this for voltage drop.#12 copper is good for 510 feet according to there chart#10 copper is good at 810 ft25ft/510=0.588 in .0438 branch circuit distance220ft/810ft =0.2716 well leadsIf you add these numbers together and multiply by 100 you get 31% so I would still have another 69% to go before I’m over the 5% voltage drop….Do I need toInclude the feeder wires coming from main disconnect to remote distributing panel?I came up with this by using the demand factors listed in 551.73(A)12,000va X 4sites = 48,000va48,000va X .75%demand= 36,000va36,000va / 240 volts = 150 ampsIf they end up adding two more sites in future72,000va X 60% demand= 43,200va43,200va / 240volt = 180 ampsQuestions:Is my 200 amp service big enough for 4 sites and the well. If they add a total of 6 site will my service still be big enough?Do my tv pedestals need to be rated 200 amp to feed through 4-6 pedestals. This is the model I’m thinking of telling the rv site owner he needs to get. M675CP6010 I will provide de cut sheet in the pictures. RV pedestals will not have main breakerThank you to all on this page that inspire to learn and teach! I appreciate you very much!

Okay, let's break down your plan and address your questions regarding the NEC (National Electrical Code). Keep in mind I am an AI and cannot provide official code interpretations, and local AHJs (Authorities Having Jurisdiction) have the final say. Consult with a licensed electrician in your area to review your plans and ensure they comply with all applicable codes and regulations.Regarding the RV Site Wiring (Pedestals)



Feeder Size and Type

Your plan to use 3-250kcmil Aluminum and 1-3/0 Aluminum quadplex is likely sufficient for the initial 4 sites,
based on your demand factor calculation (we'll revisit this later). However, it's critical to ensure your local utility (POCO) allows this size and type of conductor for a 200A service. They may have specific requirements. PVC conduit is a common and acceptable choice for underground installations.

RV Pedestal Feed-Throughs

This is generally an acceptable method. The critical point is to ensure the lugs in each pedestal are listed and rated for the wire sizes you're using and that you torque them properly. The pedestal's enclosure must be appropriately sized and labeled for the voltage and amperage. The pedestal you provided is 60a. This is probably fine for most rv’s however for $300 more you can upgrade to a 100a pedestal with lugs large enough to feed through if needed.

No Main Breaker in Pedestals

This is standard practice when feeding through. The overcurrent protection is provided by the 200A breaker at the main service panel.

Regarding the Remote Distribution Panel (Well and Heater)



Feeder Size

3-1/0 AL and 1-#2 AL in 2" PVC sounds adequate for a 100A feeder.

Well Motor Circuit



Motor Nameplate

Crucially, verify the actual nameplate amperage of the well motor. 6.8A is a general value. The nameplate will provide the exact Full Load Amps (FLA) needed for your calculations. This is essential.

Phase Converter Sizing

Ensure the phase converter is sized appropriately for the motor. The converter manufacturer will have specific recommendations. Improper sizing can lead to motor damage and voltage drop issues.


Overcurrent Protection

Your calculation of 8.5A (6.8A 1.25) is correct for determining the minimum ampacity of the conductors. However, the overcurrent protection device (OCPD) (your 2-pole 20A breaker) needs to adhere to NEC 430.52, which covers motor branch-circuit short-circuit and ground-fault protection. It’s likely 20A is too high. You need to determine the correct size based on the motor's FLA and the type of motor.

Conductor Sizing

#12 copper might be acceptable for the run to the pressure switch if the OCPD allows it. The OCPD rating is what governs the conductor size after accounting for the 1.25 multiplier on the motor FLA.

Well Pump Wiring

The well company's wiring
must be sized according to the motor's requirements and any applicable well codes. Typically, they will use submersible pump cable rated for wet locations. You are correct that they would likely use a wire size larger than #10.

Voltage Drop Calculation



Your method has flaws.
Voltage drop calculations need to be done more precisely. Use a voltage drop calculator that considers the wire type (copper/aluminum), length, ampacity, and voltage. Many online calculators are available. A good online calculator can be found at southwire.com. Include Feeder Wires? YES! The voltage drop from the main service to the remote panel absolutely needs to be included in your total voltage drop calculation. Voltage drop is cumulative! You need to calculate the voltage drop from the main panel to the remote panel and from the remote panel to the well motor. Keep both calculations below 3%.

Demand Factor Calculations



NEC 551.73(A)

Your use of this section is appropriate for RV site load calculations.


4 Sites

Your calculation of 150A demand is reasonable based on the 75% demand factor.

6 Sites

Your calculation of 180A demand is also reasonable based on the 60% demand factor.


Crucial Point

These calculations are estimates. The actual load can vary significantly based on the type of RVs using the sites and their electrical usage habits. Consider the possibility of RVs using both air conditioners and electric heaters simultaneously. This is the biggest potential "gotcha."

Is the 200A Service Big Enough?
Maybe, but needs careful review. Based solely on your demand factor calculations, it appears to be adequate for 4 sites and the well. However, you MUST factor in: The well motor's actual load. A 2HP motor could potentially draw more current under certain conditions (e.g., starting, overload). The heater's load. How big is the heater? Add that to your calculation. Future Expansion

If you're planning for 6 sites, 180A is already approaching the 200A service capacity. It's wise to plan for future expansion now, rather than needing to upgrade later.

POCO Requirements

Contact your local utility to confirm they can supply a 200A service and if they have any specific requirements for sizing.


The most conservative approach would be to have a load calculation done by a licensed electrician using the information provided. This is the only way to be sure.


Other Considerations



Grounding and Bonding

Pay meticulous attention to grounding and bonding throughout the entire system. This is critical for safety. Use the appropriate grounding electrode system (ground rods, etc.) and ensure all metal parts are properly bonded.


GFCI Protection

RV sites require GFCI protection for receptacles, as do locations near water (well).

Wiring Methods

Ensure all wiring methods (conduit types, boxes, etc.) are suitable for the location and environment.


Overcurrent Protection

All circuits must have appropriately sized overcurrent protection (circuit breakers or fuses) to protect the conductors.

Clearances

Maintain proper clearances around electrical equipment.

Recommendations


Consult with a Licensed Electrician

This is non-negotiable. They can perform a detailed load calculation, review your plans, and ensure compliance with all local codes.2.

Verify Motor Nameplate

Get the
actual FLA from the well motor's nameplate.3.

Accurate Load Calculation

Account for all potential loads, including the well, heater, RV sites (with realistic usage scenarios), and any other electrical equipment.4.

Voltage Drop Calculations

Use a voltage drop calculator and account for the entire circuit length.5.

Consider a Larger Service

If there's any doubt about the 200A service being sufficient, it's better to upsize it to a 250A or 300A service now. The cost increase will likely be less than upgrading it later.6.

Coordinate with the POCO

Confirm their requirements for service entrance conductors, metering, and grounding.7.

Drawings and Permits:
* Prepare detailed electrical drawings and obtain all necessary permits before starting any work.By addressing these points and working with a qualified electrician, you can ensure a safe and compliant RV site electrical system. Good luck! Flag for review

Previous Question Next Question