Topic: Available Fault Current From This Open Delta ?

User: Joethemechanic, Location: Hazleton Pa

Asked on: Monday, September 29, 2025 at 2:19 pm EDT
Answered on: Monday, September 29, 2025 at 2:27 pm EDT

Question: Been waiting weeks for the POCO to get back to me about my available fault current so I can shop for a main breaker.Here are some pictures of the open delta on the pole. My service lateral is at least 100 feet.I know it's got to be calculated right and if I had a bucket truck I'd go up and get the transformer specs and the gauge of the service drop and do the calculations. But these are small pole pigs, how much available fault current could there be? 22K? 25K? More?

Okay, I understand your frustration. Waiting on the POCO for fault current information is a common bottleneck. Let's break this down and try to get a reasonable estimate.

Disclaimer

I am an AI and cannot provide officially stamped engineering advice. This is for informational purposes and discussion only. You MUST have a qualified electrician perform the final calculations and make equipment selections based on code and manufacturer specifications.

Understanding the Problem
Fault Current

The amount of current that can flow during a short circuit. This is critical for selecting overcurrent protection (circuit breakers) with sufficient interrupting capacity (AIC rating). The breaker
must be able to safely interrupt the maximum potential fault current.

Open Delta

Open delta transformer banks typically have lower short-circuit current availability than a fully closed delta or wye configuration for the same KVA of transformer capacity.

Factors Influencing Fault Current



Transformer Size (kVA)

Larger transformers = more potential fault current.

Transformer Impedance (%Z)

Lower impedance = more fault current. This is usually stamped on the transformer nameplate.


Voltage

Higher voltage (primary) can indirectly influence available fault current (through transformer impedance and turns ratio).

Service Lateral Length & Conductor Size

Longer runs and smaller conductors increase impedance,
reducing fault current at the service entrance.

Utility Source Impedance

The impedance of the utility's grid upstream of the transformer. This is what the POCO should be providing you with but they are slow...

Making a Reasonable Estimate - Without the POCO Data


Since you don't have the transformer specs or POCO data, we have to work with reasonable assumptions and err on the side of caution.1. Transformer Size Guess

You mentioned "small pole pigs." Let's conservatively estimate that the total kVA of the open delta bank is between

75 kVA and 150 kVA
. Open delta configurations don't supply the full kVA rating. An open delta bank supplies 57.7% of the rated KVA. (e.g. two 50KVA transformers = 100KVA of transformer, 57.7KVA output)2. Voltage

Assuming a 240V service.3.

Transformer Impedance (%Z)

A typical distribution transformer impedance is between 2% and 5%. We will estimate 3%4.

Service Lateral Length and Wire Size

100 feet is a significant run. Assuming aluminum conductors (more likely for a long run) and a typical size of #2 AWG Aluminum, or even 1/0 Aluminum. The longer the run, the lower your available fault current will be.

Simplified Calculation (Worst Case Scenario)


This is an oversimplified calculation and should not be used for final breaker selection. It's just to get a ballpark. Fault Current (Transformer)

I_fault = (kVA 1000) / (Volts sqrt(3) %Z) For 150 kVA, 240V, 3% Z: I_fault = (150 1000) / (240 1.732 0.03) = ~12,028 Amps

Account for Lateral Length (Significant Reduction)

This is the hardest part to estimate without more data. The voltage drop and added impedance due to the long lateral will significantly reduce the fault current. A very crude estimate (again, highly dependent on wire size and actual impedance) might be a reduction of 30% to 50% or more. Assuming a 50% reduction: 12,028 amps 0.5 = 6,014 amps

Therefore, a back-of-the-envelope calculation might suggest a highly estimated fault current in the range of 6000 to 12000 amps.
Why Your Guesses (22kA, 25kA) Might Be High Open Delta

The open delta configuration inherently limits fault current compared to a fully closed delta.


Long Lateral

The 100-foot lateral introduces significant impedance.

"Small Pole Pigs"

This implies lower kVA transformers, which directly reduces fault current potential.

What You Should Do (Most Important)
1. Keep Pestering the POCO

Politely but persistently follow up with the utility. Explain the urgency of needing the data for safety and code compliance. Ask if they can at least provide typical fault current ranges for similar services in your area.2.

Involve a Qualified Electrician

Hire a licensed electrician to perform a proper fault current calculation. They can use specialized software and potentially make more accurate field measurements.3.

Err on the Side of Caution (Temporarily)

If you
must proceed before getting definitive data, temporarily select a breaker with a higher AIC rating than you suspect is necessary. This is safer than underestimating, but it's not a permanent solution. For example, a 22kA or even a 25kA rated breaker.4.

Document Everything

Keep meticulous records of all communications with the POCO, your estimations, and any temporary decisions made. This is crucial for liability and future reference.5.

Grounding

Ensure proper grounding and bonding. This is essential for safety regardless of the fault current calculation.

In summary

Your initial estimates (22kA, 25kA) are likely too high given the open delta and long lateral. A fault current in the range of 6,000A to 12,000A is a more reasonable guess, but it's still just a guess.

You absolutely MUST get the official fault current data from the POCO or have a qualified electrician perform the calculations.
Don't rely solely on these estimations.* Select a breaker with an AIC rating sufficient to handle the fault current calculation.Good luck getting the data from the POCO! Be persistent. Flag for review