Question: I have always thought it was OK to feed out of a panel with a properly sized breaker to feed a larger main breaker(of a sub-panel) that functions only as a disconnect.But I had an inspector make a comment about it the other day so i got a little confused. I was not there to ask him to elaborate. The General contractor relayed it second hand.So what is it?
Okay, let's break down the scenario and address why the inspector might have raised an eyebrow. You're describing feeding a subpanel that has a main breaker larger than the breaker in the panel feeding it. The main breaker of the sub panel will be used only as a disconnecting means.
Here's the core issue and why the inspector might have concerns
The primary reason for concern revolves around
overcurrent protection and coordination. Overcurrent Protection
The purpose of a breaker is to protect conductors from carrying more current than they are rated for.
Coordination/Selectivity
Coordination is the process of ensuring that the overcurrent protective devices (OCPDs) closest to the fault trip first, minimizing the impact of a fault.Here's how your scenario raises questions:1.
Subpanel Main Breaker Doesn't Provide Overcurrent Protection for the Feeders
If the subpanel's main breaker is larger than the breaker in the source panel feeding it, the subpanel's main breaker cannot provide overcurrent protection for the conductors feeding the subpanel. The
upstream breaker is the one providing that protection.2. Potential for Confusion
Even if the upstream breaker is properly sized, having a larger breaker as the "main" in the subpanel creates confusion. Someone might incorrectly assume that the subpanel can handle more current than it actually can, leading to potential overloading. Future contractors may replace the upstream breaker with a larger breaker that could damage the smaller feeder cable.3.
Code Compliance
This is where it gets tricky. The NEC (National Electrical Code) doesn't explicitly forbid this arrangement in every single circumstance. However, several articles could be interpreted as discouraging or requiring specific conditions to be met:
NEC 240.4(B) and 240.4(C)
These sections deal with the protection of conductors. While "next higher standard overcurrent device" rule exists, it doesn't mean you can just slap any size breaker in as the main of a subpanel. The code is extremely picky about where that rule is applied.
NEC 240.21 Feeder Tap Rules
If the conductors feeding the subpanel are considered "taps," specific rules apply regarding the length of the taps and the overcurrent protection at the tap point. This is likely not what you have, but it's relevant to consider.
NEC 408
Specifically, rules about switchboards and panelboards. While it doesn't directly address your scenario, it reinforces the idea that the panelboard (subpanel) must be rated for the available fault current and the applied load.
Why the Inspector's Comment Matters
Inspectors are concerned with safety and code compliance. Their job is to identify potential problems and prevent hazards. Even if your arrangement technically meets the minimum requirements of the code, the inspector might see it as a bad practice that could lead to future problems.
How to Address the Inspector's Concern
Talk to the Inspector
The best thing to do is to speak directly with the inspector to understand their specific concerns. Ask them to point to the section(s) of the code that they believe are being violated or are problematic. A calm, respectful conversation can often resolve misunderstandings.2.
Document Everything
Clearly document your design and calculations, showing that the conductors are properly protected by the upstream breaker.3.
Consider a Different Solution
In many cases, the easiest and best solution is to replace the main breaker in the subpanel with one that is equal to or smaller than the breaker feeding it.
In Summary:
While not always explicitly forbidden by the NEC, using a significantly larger breaker as the main breaker in a subpanel (when its sole purpose is a disconnect) is* a questionable practice. It can lead to confusion, potential for future code violations, and doesn't provide any actual overcurrent protection beyond what the upstream breaker already provides. The inspector's concern is valid from a safety and best-practice perspective. Communicate with them to understand their specific reasoning and explore alternative solutions if necessary. Flag for review