Question: Is there in NFPA any article talking about demand factor for the electrical loads of the Fire/life systemsis demand factor can be applied on the loads of fire/life safety system
NFPA codes generally discourage or prohibit the application of demand factors to fire/life safety systems. Here's a breakdown of why and where to look
Why Demand Factors Are Generally NOT Allowed for Fire/Life Safety:
Reliability is Paramount
Fire/life safety systems must operate reliably when needed. Applying demand factors assumes that not all loads will operate simultaneously, which is a risk you cannot take in an emergency. The system needs to be sized to handle the maximum possible load.
Simultaneous Operation
During a fire, multiple life safety systems (fire alarm, emergency lighting, fire pumps, smoke control, etc.) are likely to operate simultaneously, or in very quick succession.
Code Mandates Full Load
Many specific sections within NFPA codes related to fire/life safety equipment will explicitly state that the system must be sized to handle the "full load" or "100% load."
Potential for Catastrophic Failure
Under-sizing a fire/life safety system due to demand factors could lead to system failure during a fire, resulting in loss of life and property.
Where to Look in NFPA Codes (General Guidance)
NFPA 70 (National Electrical Code - NEC)
Article 700 (Emergency Systems): Often requires sizing for the full load of the emergency system. Look for sections detailing specific load calculations. While the NEC doesn't explicitly prohibit demand factors in all emergency system cases, the overall intent is to size for the worst-case scenario. Many requirements result in sizing for full load. Article 701 (Legally Required Standby Systems): Similar to Article 700, legally required standby systems generally need to be sized for full load. Again, carefully review specific section requirements. Article 702 (Optional Standby Systems): These systems are not directly related to life safety, and demand factors might be permissible, but only if the system is truly optional and not critical to fire/life safety. It is important to note that Section 700.5(B) generally allows the generator for an emergency system to supply non-emergency loads if automatic selective load pickup and shedding is provided to ensure that adequate generator capacity is available for the essential emergency loads. This is not a demand factor. This is a provision to allow other loads to be connected, but the emergency system is always prioritized.
NFPA 72 (National Fire Alarm and Signaling Code)
Chapter 10 (Circuits and Pathways): Addresses power supply requirements for fire alarm systems. Generally requires sufficient power to operate all connected devices simultaneously during an alarm condition. Demand factors would typically not be allowed. Look for sections related to the calculation of primary and secondary power supplies.
NFPA 20 (Standard for the Installation of Stationary Fire Pumps)
Requires sizing the electrical supply to the fire pump to handle the full load of the pump motor and any associated jockey pump. Demand factors would not be allowed.
NFPA 92 (Standard for Smoke Control Systems)
Requires that smoke control systems be designed to operate under worst-case scenarios. Demand factors would typically not be allowed on the smoke control system loads.
Other Relevant NFPA Codes
Any code specifically addressing the design and installation of a fire/life safety system will likely have requirements that effectively preclude the use of demand factors.
How to Determine if Demand Factors Are Allowed (When Unsure)
Consult the Authority Having Jurisdiction (AHJ)
The AHJ (e.g., the local fire marshal, building inspector) has the final say on code interpretation and enforcement. Always consult with them.2.
Thoroughly Review ALL Applicable Codes
Don't rely on just one code. Fire/life safety systems often involve multiple codes. Look for specific language regarding load calculations.3.
Err on the Side of Caution
If there is any doubt, size the system for the full connected load.
In summary: It is highly unlikely* that demand factors can be used for fire/life safety systems. The codes are designed to ensure reliability, and applying demand factors would compromise that reliability. Always prioritize life safety and consult with the AHJ. Look for specific language in the relevant NFPA codes that requires sizing the system to handle 100% of the connected load. Flag for review