Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Tripping Breaker

User: arnettda

Asked on: Tuesday, September 30, 2025 at 8:22 am EDT
Answered on: Tuesday, September 30, 2025 at 8:23 am EDT

Question: I repiped and pulled new wire to a 3 phase disconnect and installed a new disconnect. I have a rotation meter so my phasing is the same. The disconnect feeds a transformer and then the machine. I used the existing breaker that fed the disconnect. At the end of the day they shut the disconnect off that feeds the machine. Now the Majority of the mornings when they turn on the disconnect the breaker trips. I am starting with replacing the breaker but am a little lost after that, is it related to the work I did which I inspected the best I could without pulling all the wiring out. Or is it just timing and something is going wrong with the machine or transformer. After they reset the breaker the machine has run perfectly all day every day. Thank you.

This is a tricky troubleshooting scenario, but let's break it down logically. Here's a structured approach to investigate the breaker tripping issue, keeping in mind it likely is related to the work you did, even if indirectly.

I. IMMEDIATE ACTIONS & SAFETY FIRST Document Everything

Start meticulously logging when the breaker trips. Note the time of day, any other equipment running at the same time, ambient temperature, and anything else that seems relevant. This log will be invaluable.


Safety Interlocks

Make absolutely sure that all safety interlocks and emergency stop circuits are functioning correctly. A malfunctioning safety circuit could be causing a momentary inrush when power is restored.

II. Systematic Troubleshooting Steps
1. Breaker Replacement

As you mentioned, replacing the breaker is a good first step. Use the exact same type and ampacity. A faulty breaker can mimic many other problems.

Inspect the Old Breaker

After you remove the old breaker, carefully inspect it for any signs of damage, overheating, or loose connections. This might give you a clue. Don't just upgrade to a larger breaker. That's a code violation and a potential fire hazard.2.

Verify Wire Sizes and Connections (Your Work)



Double-Check Wire Size

Make absolutely sure the wire you used from the breaker to the disconnect is sized correctly for the breaker's amperage and the distance. Use the NEC (National Electrical Code) ampacity tables.

Tightness of Connections

Turn OFF the breaker, disconnect, and main panel feeding the branch. Use a torque screwdriver to ensure all connections at the breaker, in the disconnect, at the transformer primary, and at the machine's connection point are torqued to the manufacturer's specifications. Loose connections cause heat and increased resistance, leading to potential overcurrent and nuisance tripping. This is the most likely culprit.


Inspection of Terminations

Visually inspect each termination for signs of overheating, corrosion, or insulation damage. If you used crimp-on connectors, ensure they are the correct size for the wire and properly crimped.3.

Transformer Investigation
Transformer Type and Load

Confirm that the transformer's kVA rating is adequate for the machine's load. If the transformer is overloaded, it will draw excessive current on the primary side, potentially tripping the breaker upon initial energization.


Transformer Inrush Current

Transformers exhibit a high inrush current when first energized. This is normal, but if the inrush is excessive, it could trip the breaker. If the transformer is old or has suffered insulation degradation, its inrush current may be higher than normal.

Insulation Resistance Test

Use a megohmmeter (megger) to test the insulation resistance of the transformer windings. Low insulation resistance indicates insulation breakdown and could cause excessive current draw.


Transformer Connections

Verify the transformer's primary connections (voltage taps) are correctly configured for the supply voltage. Incorrect connections could lead to overcurrent.

Tap Changer

Verify the tap changer is set correctly. Mismatched taps can cause voltage and current issues.4.

Machine Load
Motor Inrush

If the machine has motors, they also have a significant inrush current when starting. The combined inrush of the transformer and motors could be the problem.

Machine Load Profile

Analyze the machine's typical load profile. Are there any sudden load increases when it starts up? This could be due to a hydraulic pump, compressor, or other high-demand component.


Motor Starters

If the machine has motor starters (reduced voltage starters like autotransformer or part-winding), check their operation. A faulty starter could apply full voltage to the motor too quickly, causing a high inrush current.

Motor Insulation

Perform a megger test on the motor windings to check for insulation breakdown.5.

Neutral and Grounding
Correct Neutral Connection

Especially with a transformer, verify the neutral is properly bonded, if required, according to local code. A floating neutral can cause unpredictable voltage imbalances and current flow.

Grounding

Ensure the grounding conductor (equipment grounding conductor) is properly sized and connected throughout the entire system (breaker panel, disconnect, transformer, machine). A poor ground can contribute to nuisance tripping.6.

Monitor Current (Advanced Troubleshooting)



Inrush Current Measurement

Use a clamp-on ammeter with inrush current measurement capability to measure the actual inrush current when the disconnect is turned on. Compare this value to the breaker's instantaneous trip curve and the transformer's inrush current rating.

Data Logging Ammeter

Consider using a data-logging ammeter to monitor the current over a period of time (e.g., overnight) to see if there are any transient events that might be contributing to the tripping.7.

Power Quality Analysis

If the problem persists, consider hiring a qualified electrician or power quality specialist to perform a comprehensive power quality analysis. This can identify voltage sags, harmonics, or other power disturbances that might be contributing to the tripping.

Why it's likely related to your work, even if the machine ran fine before



Slightly Increased Resistance

Even a small increase in resistance at a connection point can worsen inrush current effects. The machine might have been "getting by" before, but the new installation might have introduced just enough extra resistance to push it over the edge.


Transformer Energization

The act of de-energizing and re-energizing the transformer can change its core flux pattern, potentially affecting its inrush current characteristics (though this is less likely).

Timing

It's possible the machine's load profile has changed slightly, coinciding with your work.

Important Considerations



Qualified Electrician

If you're not comfortable performing any of these tests or troubleshooting steps, hire a qualified electrician. Working with electrical equipment can be dangerous.

Local Codes

Always adhere to local electrical codes and regulations.


Manufacturer's Specifications:
Consult the manufacturer's documentation for the breaker, disconnect, transformer, and machine for specific troubleshooting recommendations and specifications.By systematically working through these steps, you should be able to identify the root cause of the breaker tripping and resolve the issue. Good luck! Flag for review

Previous Question Next Question