User: pipe_bender, Location: Boston
Asked on: Tuesday, September 30, 2025 at 5:33 pm EDT
Answered on: Tuesday, September 30, 2025 at 5:35 pm EDT
Question: Hey gang, I am demoing some conduit on a top floor and there are several green wires that come down from the roof and attach to conduits with a strap.Its a 3/4 EMT that was used for lighting and is being removed.I am going to have to replace the ground of course and am looking at the code sections on grounding antennas 810.21, do I need to run all these grounds to the electrical room in the basement or can I move these straps to another EMT conduit or water pipe?Thanks
Okay, let's break down the grounding requirements for antennas and how it applies to your situation. It sounds like you're removing conduit that supported roof-mounted equipment, and those conduits were being used as grounding paths for the antennas.
Understanding the Situation Antenna Grounding
Antennas and their supporting structures have specific grounding requirements to protect against lightning strikes and static discharge. These grounds are designed to provide a low-impedance path to earth, diverting dangerous currents away from equipment and personnel.
EMT Conduit as a Grounding Electrode
The original installation appears to have used the EMT conduit as a conductor for the antenna ground. The green wires suggest they were serving as the grounding electrode conductor (GEC) or a bonding jumper to that EMT.
Removal Impact
Removing the conduit breaks the grounding path, creating a potential safety hazard.
Key Considerations and Code Sections NEC Article 810: Radio and Television Equipment
This is the main section governing antenna installations.
NEC 810.21: Grounding Conductors—Receiving Station
This section specifies the requirements for the grounding electrode conductor (GEC) for receiving antennas (like those used for TV or radio). Key points:
Size
The GEC must be of a specific size, typically based on the size of the antenna's lead-in conductor.
Material
Must be copper, aluminum, or copper-clad steel.
Continuity
The GEC must be continuous and securely fastened.
Protection
It must be protected from physical damage.
NEC 810.15: Antenna Grounding Electrode
This section specifies the acceptable grounding electrodes.
(A) Ground Rod or Pipe
Most common.
(B) Other Acceptable Electrodes
Metal Underground Water Pipe (with specific bonding requirements)
Effectively Grounded Metal Frame of the Building
Concrete-Encased Electrode (Ufer Ground)
Ground Ring
NEC 250.50 & 250.52: Grounding Electrode System and Made and Other Electrodes
These sections provide more details on acceptable grounding electrodes and the required bonding of those electrodes.
Analysis of Your Options1. Running GECs to the Electrical Room (Basement)
Code Compliance
Yes, this is a code-compliant method, if done correctly. The GECs must be sized according to the code and properly connected to a grounding electrode (or the grounding electrode system) in the electrical room.
Practicality
This may be the most reliable option, especially if the original installation was done poorly.
Challenges
Running multiple GECs from the roof to the basement can be labor-intensive and potentially require drilling through multiple floors.2.
Moving Straps to Another EMT Conduit
Probably Not Compliant, Unless...
This is highly unlikely to be code-compliant unless that EMT conduit is already part of a properly installed and bonded grounding electrode system. Simply strapping the antenna ground to another random EMT conduit does not guarantee a low-impedance path to ground and could create a dangerous situation.
Potential Problems
The EMT might not be continuous, the connections might not be tight, and it might not be properly connected to a grounding electrode. It cannot simply be a conduit run feeding other equipment.3.
Moving Straps to a Water Pipe
Potentially Compliant, BUT...
Connecting to a metal water pipe can be code-compliant if the water pipe meets the requirements of a grounding electrode (see NEC 250.52(A)(1)), AND you follow all the bonding requirements in NEC 250.104(A).
Requirements
The water pipe must be in direct contact with the earth for at least 10 feet. The water pipe must be bonded to the grounding electrode system with a bonding jumper sized according to NEC 250.66. This bonding connection is typically made at the point where the water pipe enters the building, and you must also bond around any insulated couplings or meters in the water pipe. Local codes may have additional requirements for grounding to water pipes.
Caution
Water pipes are increasingly being replaced with non-conductive materials (PVC, PEX), making them unsuitable as grounding electrodes. You must verify the water pipe is metal and meets the requirements.
Recommendations1. Assess the Original Installation
Carefully examine how the original grounding was done. Was it properly sized? Was the EMT conduit continuous and properly connected to a grounding electrode?2.
Consult with a Qualified Electrician
This is crucial. Antenna grounding is a specialized area, and improper grounding can be dangerous. A qualified electrician can evaluate the situation, determine the best course of action, and ensure that the installation meets all applicable codes.3.
Prioritize a Dedicated GEC to a Grounding Electrode
The safest and most reliable approach is typically to run properly sized GECs from the antenna locations to a properly installed grounding electrode system (ground rod, building steel, etc.) in the electrical room.4.
Document Everything
Keep detailed records of the grounding installation, including wire sizes, connection methods, and grounding electrode locations.
Important Cautions Never Assume
Don't assume that the existing grounding is adequate. Always verify that it meets code requirements.
Lightning Protection
Antenna grounding is primarily for protection against static discharge and minor surges. For comprehensive lightning protection, you may need a separate lightning protection system designed and installed by a qualified lightning protection specialist.
Bonding
Proper bonding of all metallic components is essential for a safe and effective grounding system.
In summary, while you might* be able to use a water pipe as a grounding electrode, it's essential to verify that it meets all code requirements and that you properly bond it to the grounding electrode system. The safest and most reliable option is usually to run dedicated GECs to a grounding electrode in the electrical room, but consult with a qualified electrician to determine the best approach for your specific situation. Flag for review