Question: My comrades and myself are having a discussion about voltage drop and wiring, I am running #8 to a 7 !/2 hp motor rated at 8.67 amps we are having problems terminating the wires under the lugs of the motor starter due to their size , can I terminate to the starter with #12 and splice to the #8 and change back to #12 on the other end?
Okay, let's break down this scenario from an electrical code and practical safety perspective.
The Short Answer is: NO, you cannot simply reduce the wire size to #12 at the terminations of the motor starter and at the motor.
Here's a detailed explanation of why, along with considerations and possible solutions
Reasons Why Your Proposed Approach is Problematic (and Likely Violates Code):
1. Ampacity and Overcurrent Protection
The fundamental principle here is matching the wire size to the load and the overcurrent protection (fuse or circuit breaker). #8 AWG copper wire typically has an ampacity well above 8.67 amps (depending on insulation type and installation conditions, it's usually good for 40-55 amps or more). #12 AWG copper wire, on the other hand, is usually only good for 20 or 25 amps.
NEC 430.22(A) says that the conductors supplying the motor must have an ampacity not less than 125% of the motor's full-load current (FLC). In your case, 8.67 amps 1.25 = 10.84 amps. #12 AWG MIGHT be acceptable if the starter overloads are sized to trip at or below the ampacity of the wire. If you use #12 for any significant length, the weakest link in your circuit becomes the #12 wire. If a fault occurs that draws more than 20-25 amps through that section, the #12 wire will overheat before the circuit breaker trips (assuming the breaker is sized for the #8 wire). This creates a fire hazard.2. NEC Violations (Likely)
NEC 240.4(D): Protection of Conductors. Generally, you can't protect a conductor above its rated ampacity unless specific exceptions apply (and those exceptions are unlikely to fit your situation). Using a breaker sized for #8 AWG to protect a section of #12 AWG is a direct violation of this. NEC 310.16: Allowable Ampacities of Insulated Conductors. This table defines the ampacity for various wire sizes and insulation types. You can't exceed the ampacity listed in this table. NEC 110.3(B): Equipment Listing and Labeling Requirements. You must install and use listed or labeled equipment in accordance with any instructions included in the listing or labeling. This generally means using appropriately sized conductors for the terminations.3. Voltage Drop Considerations
Even though you mentioned this, reducing the wire size increases voltage drop. While voltage drop may not be the primary safety concern, it can negatively affect motor performance (reduced torque, overheating, etc.).4.
Termination Integrity
Crimping or splicing larger gauge wire to smaller gauge wire, especially at high current applications, can introduce points of increased resistance. Poor connections lead to heat generation, which can further degrade the connection and create a fire hazard.
Possible Solutions and Considerations
Use Appropriately Sized Lugs/Connectors
This is the preferred and most common solution.
Inspect the Motor Starter Lugs
Carefully examine the motor starter lugs. Are they truly too small for #8? Sometimes, lugs appear smaller than they actually are. Check the manufacturer's specifications for the lug size range. Look for a part number or marking that you can search online.
Replace the Lugs
Many motor starters have replaceable lugs. You may be able to replace the existing lugs with larger ones that are rated for #8 AWG (or larger). Contact the motor starter manufacturer or a reputable electrical supply house to find compatible lugs.
Use a Conductor Size Adapter
These are basically short, listed/approved connectors that allow you to transition from a larger wire size to a smaller wire size within the termination. The adapter is rated for the current, and has a portion that accepts the larger conductor (#8) and smaller conductor (#12). These are often called 'reducer' lugs, or 'step-down' connectors. Make sure you install them according to the manufacturer's instructions and use the correct crimping tool (if applicable).
Pigtailing (Use with Caution)
In some cases, you can use a short "pigtail" of #8 AWG to attach to the lug, spliced to the main run of #8. The pigtail must be short enough that it is still considered part of the larger conductor, not a reduction in wire size.
This is generally not recommended unless you can verify with the AHJ.2. Proper Termination Techniques
Cleanliness
Ensure the wires are clean and free of corrosion.
Tightness
Use a torque wrench to tighten the lug screws to the manufacturer's specified torque. Under-tightening can cause loose connections and overheating.
Anti-Oxidant Compound
For aluminum conductors, use an anti-oxidant compound (like Penetrox) to prevent corrosion.3.
Conduit Fill
Ensure that the conduit fill is appropriate for the number and size of conductors you're using. Overfilled conduits can lead to overheating.4.
Consult an Electrician
If you're unsure about any aspect of this, definitely* consult a licensed electrician. They can assess the situation, recommend the best solution, and ensure that the installation is code-compliant and safe.
In summary: Don't compromise on safety by using undersized wire. Find a solution that allows you to properly terminate the #8 AWG wire at the motor starter and motor, or consult a professional. Flag for review