Question: I'm curious how you all go about doing panel changes with regards to shutting down/disconnecting power feeding existing panel. Is the power company supposed to disconnect or can I do it? I'm dealing with Edison and they are telling me they don't do that, but the meter is locked/tagged. Am I supposed to take that off and disconnect power on my own so I can remove existing old panel and replace with new upgraded panel? Procedurally what is the best and most appropriate way of doing this. This is a main metered service panel.
Okay, let's break down the process for a panel change with a main metered service panel, especially when dealing with a utility like Edison that claims they don't disconnect. This is a common scenario, and while it varies slightly by locality, here's the best approach
1. Confirmation with Edison (Documentation is Key)
Escalate if Necessary
If the initial representative says Edison doesn't disconnect, ask to speak to a supervisor or a more senior technician. Politely explain that this is a main service panel replacement and you need a safe and code-compliant disconnection procedure.
Get Written Confirmation
If they still refuse to disconnect, insist on getting this policy in writing. This is crucial for your liability. Request an email or official letter stating that it is the homeowner's or electrician's responsibility to disconnect the service.
Clarify the Meter Lock/Tag
Ask specifically about the locked and tagged meter. Who put it there? What are the implications of removing it?
2. Understanding Your Local Codes & Regulations (Absolutely Essential) Local AHJ (Authority Having Jurisdiction)
This is usually your city or county's building department or electrical inspector. Call them directly. Explain your situation. Ask: "What is the permitted procedure for disconnecting a main metered service for a panel upgrade when the utility does not provide disconnection services?" "Do you require a pre-inspection before disconnecting?" "What are the specific grounding and bonding requirements for the new panel installation?" "What are the requirements for a final inspection?"
NEC (National Electrical Code)
The NEC is the foundation of electrical safety. While local codes might amend it, you must adhere to the NEC's requirements for service equipment, grounding, bonding, overcurrent protection, etc. If you are not a licensed electrician, this is where you absolutely need professional help.
3. The Disconnection Procedure (If the Responsibility Falls to You)
THIS IS POTENTIALLY DANGEROUS. IF YOU ARE NOT A QUALIFIED AND EXPERIENCED ELECTRICIAN, DO NOT ATTEMPT THIS. SERIOUS INJURY OR DEATH CAN RESULT FROM IMPROPER DISCONNECTION. Plan and Prepare
Permit
Obtain the necessary electrical permit before starting any work.
Inspection Scheduling
Schedule your inspections (pre-inspection if required, and final inspection).
Material Acquisition
Have all materials for the new panel installation on site (panel, breakers, wire, connectors, grounding equipment, etc.). Ensure they are correct for the load calculation and code requirements.
Load Calculation
Perform a proper load calculation to determine the correct size of the new panel and service conductors.
Tools & PPE
Gather all necessary tools, including properly insulated tools, voltage tester, personal protective equipment (PPE) – safety glasses, insulated gloves, appropriate clothing.
Lighting
Ensure adequate lighting to work safely.
Emergency Plan
Have a plan in case something goes wrong (know where the nearest hospital is, have a working phone, etc.).
Notification
Inform the homeowner (or yourself, if you are the homeowner) that the power will be off for a period of time.
Verify Dead
Before touching anything, thoroughly verify that the power is OFF. Use a reliable voltage tester to check all phases to ground and phase to phase. Test the tester itself before and after use to ensure it's working correctly. If possible, use two different testers for redundancy.
Disconnect the Service Conductors
Carefully remove the meter lock/tag
Document the lock/tag before removing in case there is a number or other reference ID on it.
Loosen the meter connections
Carefully loosen the connections at the meter.
Pull the meter. Disconnect the Service Entrance Conductors
At the panel, carefully disconnect the service entrance conductors (the wires coming from the meter). Make sure they are properly insulated and secured so they don't accidentally come into contact with anything. Use electrical tape and wire nuts, or terminal blocks.
Grounding and Bonding
Inspect the existing grounding and bonding system. The new panel must have a properly installed and sized grounding electrode conductor (GEC) connecting to a grounding electrode (ground rod, water pipe, etc.). The neutral bar must be bonded to the panel enclosure only at the service entrance (typically with a bonding screw or strap). Pay very close attention to these details as they are critical for safety.
4. Installing the New Panel Follow the manufacturer's instructions and the NEC for the installation of the new panel. Mount the panel securely. Connect the service entrance conductors to the main breaker. Connect the grounding electrode conductor. Connect the neutral conductors to the neutral bar. Connect the branch circuit conductors to the appropriate breakers. Label Everything
Clearly label all breakers and circuits.
5. Re-Energizing the System Double-Check Everything
Before re-energizing, double-check all connections, grounding, and bonding. Ensure all breakers are in the OFF position.
Re-install the meter. Tighten meter connections. Contact Edison (possibly)
In some cases, even if they don't disconnect, they might want to be notified before you re-energize, especially if they have a smart meter. Check with them.
Turn on Main Breaker
Slowly turn on the main breaker.
Turn on Branch Circuit Breakers
Turn on branch circuit breakers one at a time, checking for any issues.
Test Circuits
Test all circuits to ensure they are working correctly.
6. Inspection Call for your final inspection. The inspector will verify that the installation meets all code requirements.
Important Considerations
Generator Backup
If possible, have a generator available to power essential loads during the outage.
Time of Year
Consider the time of year. Doing this in the middle of winter or summer can be uncomfortable for the occupants.
Asbestos
If the existing panel is very old, it might* contain asbestos. Have it tested before disturbing it.
Disclaimer: This information is for general guidance only and should not be considered a substitute for professional advice from a licensed electrician and your local AHJ. Electrical work is dangerous, and you should only perform it if you are properly qualified and experienced. I am an AI and cannot provide electrical advice. Flag for review