Topic: Smallest Natural (grounded conductor)

User: ELECTRIC ACE

Asked on: Wednesday, October 1, 2025 at 6:28 pm EDT
Answered on: Wednesday, October 1, 2025 at 6:28 pm EDT

Question: What is the Smallest Natural (grounded conductor) for a service sized parallel 4 X 500 MCM Alu. ungrounded conductors?

Okay, let's break down how to determine the minimum size of the grounded conductor (neutral) for a service with parallel 4 x 500 kcmil Aluminum ungrounded conductors. We need to follow the National Electrical Code (NEC).1. Identify the Applicable NEC Section

The key section for sizing the grounded conductor for a service is

NEC 250.24(C) Grounding Service-Supplied Alternating-Current Systems.
This section has specific requirements based on the size of the ungrounded conductors.2. General Rule and Proviso



NEC 250.24(C)(1) Sizing Based on Ungrounded Conductors

The grounded conductor
must not be smaller than the required grounding electrode conductor specified in Table 250.66. Also, for services with parallel ungrounded conductors, the grounded conductor size must be based on the equivalent size of the paralleled conductors.

NEC 250.24(C)(1)(b) The 12.5% Reduction Proviso

There's a provision that permits reducing the grounded conductor size under certain circumstances. Specifically, if the service is supplied by a single-phase, 3-wire system, or a service derived from a 3-phase, 4-wire wye-connected system, the grounded conductor can be smaller than that determined above, but not smaller than 12.5% of the area of the largest ungrounded service-entrance conductor.

3. Calculate the Equivalent Size

We have four (4) parallel 500 kcmil Aluminum conductors per phase. Total area: 4 x 500 kcmil = 2000 kcmil Aluminum

4. Determine Grounding Electrode Conductor size from Table 250.66

Table 250.66 is used to determine the size of the Grounding Electrode Conductor based on the size of the ungrounded service-entrance conductors. We'll need to find the row in Table 250.66 that corresponds to 2000 kcmil Aluminum.However, Table 250.66 only goes up to 1100 kcmil for Aluminum conductors. The note at the bottom of Table 250.66 says: "See 250.
166. Note: Where there are no service-entrance conductors, the grounding electrode conductor size shall be determined by the derived ungrounded conductors.Table 250.66 requires a


3/0 AWG Copper OR 250 kcmil Aluminum
grounding electrode conductor for service conductors with an equivalent of 1100 kcmil Aluminum. Since our total is 2000 kcmil, we need to go larger.5. Apply the 12.5% Reduction Proviso?

We need to determine if this applies. If the service is either a single-phase, 3-wire service or a service derived from a 3-phase, 4-wire wye-connected system, then we can consider the 12.5% reduction. Calculate 12.5% of the total ungrounded conductor area: 2000 kcmil 0.125 = 250 kcmil6. Final Determination (Assuming the 12.5% Proviso Applies)



Without the Reduction (based on Table 250.66 and conductor size)

Since the table only goes to 1100kcmil, we would need to select a larger grounded conductor than 250kcmil Aluminum. Due to the need to use a larger conductor per code, a
350 kcmil Aluminum conductor would be appropriate based on standard conductor sizes. This is the more conservative approach. Consult with your local inspector, as they have the final say.

With the Reduction (if applicable)

If the 12.5% rule is allowed, the minimum size is 250 kcmil Aluminum. This is calculated as 12.5% of the 2000 kcmil total ungrounded conductor area.

Therefore, the answer depends on whether the 12.5% reduction in NEC 250.24(C)(1)(b) applies.
If the 12.5% reduction DOES NOT apply

The minimum size is likely to be
350 kcmil Aluminum.

If the 12.5% reduction DOES apply

The minimum size is 250 kcmil Aluminum.

Important Considerations and Disclaimers



Local Codes and Inspector Authority

Always check with your local electrical inspector or authority having jurisdiction (AHJ). They have the final say and may have interpretations or amendments to the NEC.


Continuous Load

The 12.5% reduction is NOT permitted if there are significant nonlinear loads that will cause harmonic currents to flow in the neutral. In this case, the grounded conductor must be sized to carry the maximum unbalanced load.

Voltage Drop

Even if the code allows a smaller grounded conductor, voltage drop considerations might require a larger conductor to ensure proper voltage at the load.


This information is for educational purposes only and is not a substitute for consulting with a qualified electrician or electrical engineer.
Electrical work is dangerous and should only be performed by qualified individuals. I am an AI chatbot and cannot provide professional electrical advice.* Assumptions: I assume the service is not subject to requirements for sensitive electronic equipment that may dictate a larger neutral. Flag for review