Question: Greetings gang I am looking into options for shielded cable for wiring the typical probes and sensors on underground fuel tanks at a typical gas station.There are various probes and sensors in the underground tanks that go back to a control console, these are routed all in rigid or rigid -> pvc -> rigid then raceway to inside the store.The tank probe area is little hand hole above the tank that is a Class 1 Division 1 area, it typically has rigid stubbed in and a seal off.My take is in a class-1 division 1 conduit the wire has to be suitable for the vapors or liquids that may collect on, or come in contact with, the insulation on conductors, regardless of how sealed it is --NEC 501.20.I have seen it done a few waysOne way as a class-1 circuit with just stranded THHN-THWN-2 or TFFN-MTW if smaller than 14 as those are all marked 'Gas and Oil resistant' in racewaythat thats simple,howeverSome console systems want a shielded cable so each probes data line is wrapped in a foil shield going back to the console.Now most low voltage cable is plain 300V PVC insulation type CMP, and since 514.4 in the 2023 references 501.20 and older NEC's have it in a note.Do low voltage cables used for this purpose need be a type identified as gas and oil resistant?Like Fluorinated Ethylene Propylene (FEP) insulation?I see that one manufacturer Veeder-Root recommend Belden 88761which is a FEP type cable.My 2nd question is if this cable needs to also be sealed as its now a cable going thru the seal off's? My guess is not if its considered a 'Intrinsically Safe' system other wise yes. Most all of these I am seeing are 'Intrinsically Safe' systems.What kind of cable wire do you all run for these?Thanks for your input and feedback.Here is a diagram of what these systems look like:
Okay, you've outlined a common and challenging situation regarding wiring underground fuel tank (UST) probes and sensors. Let's break down the requirements and best practices.
Understanding the Code and Requirements Class 1 Division 1: You are correct. The inside of the handhole above the UST is classified as a Class I, Division 1 location because flammable vapors or gases are likely to exist under normal operating conditions. NEC 501.20 (2023): This section is key. It mandates that conductors in Class I, Division 1 locations must be approved for the specific hazardous location. The phrase "approved for the specific hazardous location" does mean the conductors need to be resistant to the specific vapors or liquids present. The expectation is that in a Class 1 Div 1 conduit conductors can be exposed to the hazardous atmosphere. NEC 514.4 (2023): This section applies specifically to gasoline dispensing and service stations. It directs you to the relevant sections of Article 500 (Hazardous Locations). The connection back to 501.20 is critical. Intrinsically Safe (IS): A critical element for these systems. If the system is properly designed and installed as an intrinsically safe system, the energy levels are so low that they cannot ignite flammable mixtures. This simplifies the wiring requirements in the hazardous location if the wiring methods are followed exactly as prescribed in the system documentation.
Answering Your Questions1. Do low voltage cables used for this purpose need to be a type identified as gas and oil resistant (like FEP)? Yes, but with a caveat
If the cable is installed within a conduit system in a Class I, Division 1 location, the insulation
must be suitable for the vapors or liquids present (as per 501.20). This generally means "gas and oil resistant" insulation. FEP is a good choice for this, as it is highly resistant to many chemicals. Intrinsically Safe Exception
If the system is certified intrinsically safe and the manufacturer's documentation explicitly allows a specific cable without gas/oil resistance to be used within the conduit system in the Class I, Division 1 location, and you follow all installation instructions exactly, then you might be able to use a cable that isn't specifically gas/oil resistant within the conduit.
However, this is very rare and very risky unless the manufacturer specifically states it is acceptable and your AHJ (Authority Having Jurisdiction) approves the installation. Outside the Conduit: If the shielded cable exits the conduit outside the Class 1 Division 1 area (after a seal fitting) before connecting to the intrinsically safe apparatus it will only need to be identified for the application and will no longer be required to be gas or oil resistant.2. Does the cable need to be sealed when going through a seal off? Generally, no, if it's an intrinsically safe system. Seal-offs are typically not required for intrinsically safe circuits, unless the manufacturer of the intrinsically safe equipment specifically requires it. The intent of intrinsic safety is to limit the energy in the circuit so that it can't cause ignition, regardless of whether there's a seal or not. Consult the Manufacturer's Documentation
The installation instructions for the intrinsically safe barrier and the tank monitoring system are the final authority. They will specify whether a seal-off is required and the specific type of seal-off and compound to use.
However
If the manufacturer of the intrinsic safety equipment requires that all cable runs in hazardous locations be installed in rigid conduit then the cable will likely need to be sealed in the seal off.
If Not Intrinsically Safe: If it is not an intrinsically safe system, or if any part of the system is not certified for Class I, Division 1 locations, the cable will need to be sealed when it passes from the Class I, Division 1 area to a non-hazardous area.
Typical Wiring Methods and Recommendations
Here's a breakdown of common approaches and recommendations:1. Veeder-Root and Belden 88761
Veeder-Root recommending Belden 88761 (or similar FEP-insulated shielded cable) is a sound practice. FEP is a robust insulation choice for these environments, and the shielding helps with noise immunity for the sensor signals.
Always verify that the chosen cable is listed as being "Gas and Oil Resistant".2. Intrinsically Safe Systems Are Preferred
Whenever possible, use intrinsically safe tank monitoring systems. They offer a significant advantage in terms of simplifying wiring requirements and reducing the risk of ignition.3.
Conduit and Seal Fittings
Use rigid metal conduit (RMC) for the portion within the Class I, Division 1 area. Install a seal fitting immediately after the conduit exits the Class I, Division 1 area. Use the correct sealing compound as specified by the manufacturer of the seal fitting.
Do not overfill the seal fitting. If the manufacturer does not specify a seal fitting then it may not be needed in a intrinsically safe system. Carefully consider the location of the seal fitting to ensure it's accessible for inspection and maintenance.4. Shielded Cable Handling
Terminate the shield properly at the control console end. The manufacturer's instructions will specify how to ground the shield (usually to the console chassis or a designated ground point). Avoid ground loops by grounding the shield at only one end. Protect the shielded cable from physical damage during installation.5.
Documentation and Labeling
Maintain detailed documentation of the wiring, including cable types, seal fitting locations, and grounding details. Label all conduit and junction boxes clearly to indicate the hazardous location rating and the presence of intrinsically safe circuits (if applicable).
Cable Options
Here are some cable types to consider:1. Belden 88761 : Its a 22 AWG shielded cable with a FEP insulation2. Belden 83395E : Its a 20 AWG shielded cable with a FEP insulation3. Similar manufactures such as Alpha Wire also have cables that would work.
Important Considerations Manufacturer's Instructions Are Paramount
The installation instructions provided by the tank monitoring system manufacturer and the intrinsically safe barrier manufacturer (if applicable) are the final authority on wiring methods and component selection. Follow them meticulously.
Authority Having Jurisdiction (AHJ)
Your local electrical inspector has the final say. Consult with them during the design phase to ensure that your proposed wiring methods comply with local codes and regulations. Early communication with the AHJ can prevent costly rework later.*
Competent Personnel
Ensure that the installation is performed by qualified electricians who are familiar with hazardous location wiring practices and intrinsically safe systems.
In summary, you need to use a cable that has an insulation type rated for gas and oil contact when running in conduit in a Class 1 Division 1 area, unless its an intrinsically safe circuit and the manufacture allows you to do so.I strongly recommend consulting with the tank monitoring system manufacturer, the intrinsically safe barrier manufacturer (if applicable), and your local electrical inspector to ensure that your proposed wiring methods are safe and code-compliant. Flag for review