Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Running RMC in a Class 1 Div 1 using the process piping to support.

User: Mr.TmO, Location: Anchorage AK

Asked on: Wednesday, October 1, 2025 at 8:42 pm EDT
Answered on: Wednesday, October 1, 2025 at 9:01 pm EDT

Question: I'm looking to upgrade my tank farm at my new facility, and the existing conduit is currently secured to the process piping. This is causing it to break at the threads in some areas due to the flooding and vibrations. They have a mixture of supports constructed of Unistrut with all-thread wrapping around the process piping and short extensions of Unistrut that are attached to other conduits for support. I also noted that there are no low point drains and was seeing if anyone could help me pin some of these issues out in the code book to aid me in writing a proposal.

Okay, let's break down the NEC issues you're facing with your tank farm's conduit system and how to find them in the National Electrical Code (NEC). I'll focus on common violations based on your description and provide specific section references from the 2023 NEC (always verify against your local jurisdiction's adopted code version).

Key Issues and Relevant NEC Sections


Support of Conduit

The primary problem is the

improper support of the conduit system
. Using process piping as the sole support for electrical conduit is generally a violation. Process piping isn't designed for this, and vibration, expansion/contraction, and maintenance can compromise the electrical system. NEC 300.11(C) Raceways Used as Means of Support. This is the crucial section. It states that raceways (conduit) cannot be used as a means of support for other raceways, cables, or equipment unless specifically designed for this purpose. Your short sections of Unistrut connecting conduits likely violate this. NEC 300.11(A) Securing and Supporting. This covers the general rules for how raceways need to be secured and supported. It states that raceways, cable assemblies, boxes, cabinets, and fittings must be securely fastened in place. Attachment to process piping likely doesn't meet this standard. NEC 344.30(A) Rigid Metal Conduit (RMC) and NEC 352.30(A) Rigid PVC Conduit

These sections (and similar sections for other conduit types like IMC, EMT, etc.) specify the
maximum distance between supports for the specific type of conduit. You'll need to check the specific type of conduit being used in your tank farm to determine the correct support spacing. Over-spanning can cause stress and failures.

NEC 314.23(H) Supports.
This section focuses on the support of boxes and enclosures. Boxes need to be securely fastened and independently supported from the raceway.2. Vibration and Physical Damage

Tank farms are often subject to significant vibration from pumps, mixers, and other equipment. The conduit system must be robust enough to withstand this.

NEC 300.4(D) Protection from Physical Damage.
This is broad but essential. It requires wiring methods to be protected from physical damage. Using process piping as support increases vulnerability to damage. NEC 300.11(B) Raceways and Cable Assemblies. This section requires raceways and cable assemblies to be supported by structural elements of the building or other means designed and installed so that they will not be damaged by vibration or movement. This is a critical point against using process piping directly. NEC 352.12(C) Uses Not Permitted (Rigid PVC Conduit) This section states that PVC conduit shall not be subject to physical damage unless identified for such use.3. Water Accumulation and Condensation

The lack of low-point drains can lead to water accumulation inside the conduit, causing corrosion, shorts, and ground faults.


NEC 300.12 Mechanical Continuity - Raceways and Cables.
Although not a direct requirement for drains, this emphasizes the need for a complete, mechanically sound raceway system. Water accumulation can compromise this continuity. NEC 225.22 Raceways on Exterior Surfaces. This section requires raceways installed on exterior surfaces to be arranged and equipped to drain. This applies to raceways exposed to the elements in the tank farm. Note

While the NEC doesn't explicitly mandate low-point drains in every situation, it strongly implies the need to address water accumulation. Good engineering practice dictates providing drainage where condensation or water ingress is likely.4.

Threaded Conduit Joints

Repeated breakage at threaded joints points to stress and vibration issues. Proper support and using appropriate conduit fittings are critical.

NEC 344.42(B) RMC - Threads.
(and similar sections for other conduit types). This specifies that conduit threads must be adequately tightened and made wrench tight. Improperly tightened joints are more susceptible to vibration failures. Using thread sealant or anti-seize compounds may also be beneficial. NEC 300.6 Protection Against Corrosion. The combination of moisture and dissimilar metals can cause corrosion. Ensure that proper grounding techniques are followed, and consider using corrosion-resistant coatings on conduit and fittings.5. Grounding and Bonding

Critical for safety, especially in a wet/hazardous environment.

NEC Article 250, Grounding and Bonding.
This entire article applies, but pay particular attention to: 250.4(A)(3) Permanently Safe, Effective Grounding Path. This requires a low-impedance path to ground. Corroded or poorly supported conduit can compromise this path. 250.96 Bonding Other Enclosures. Requires bonding of metal raceways, cable trays, and other metal enclosures. 250.104(A) Bonding of Piping Systems and Exposed Structural Metal. This requires that exposed structural metal that is liable to become energized be bonded together and connected to the grounding electrode system. 250.118 Types of Equipment Grounding Conductors. This lists acceptable types of equipment grounding conductors to ensure proper grounding and bonding.

Additional Considerations (Beyond the NEC)



Manufacturer's Instructions

Always follow the manufacturer's instructions for the installation of conduit, fittings, and supports.

Engineering Drawings and Specifications

Ensure that your new installation is based on proper engineering drawings and specifications that address the specific environmental conditions and operational requirements of the tank farm.


Hazardous Locations (if applicable)

If the tank farm contains flammable liquids or vapors, it will likely be classified as a hazardous location (e.g., Class I, Division 1 or 2). This imposes additional requirements for conduit types, sealing fittings, and explosion-proof enclosures (see NEC Articles 500-516).

Writing Your Proposal


Clearly State the Problem

Describe the existing conditions, including the improper support methods, conduit failures, and lack of drainage. Use photos to document the issues.2.

Cite Specific NEC Violations

Reference the specific NEC sections I've outlined above, explaining how the existing installation violates those sections.3.

Propose a Solution



Independent Support System

Design and install a dedicated support system for the conduit. This could involve using Unistrut supported by stanchions anchored to the ground, walls, or structural steel (but not the process piping).


Proper Conduit Spacing

Adhere to the correct support spacing for the type of conduit being used (as specified in the NEC).

Vibration Isolation

Consider using flexible conduit or expansion couplings to isolate the conduit system from vibration.


Low-Point Drains

Install low-point drains or weep holes in the conduit system to allow for water drainage.

Sealing Fittings

Use sealing fittings in conduit runs to prevent the spread of flammable vapors or liquids (if applicable).


Grounding and Bonding

Verify and upgrade the grounding and bonding system to ensure code compliance.

Material Selection

Choose appropriate conduit materials and fittings that are resistant to corrosion and compatible with the environment.4.

Include a Detailed Scope of Work

Outline all the tasks involved in the upgrade, including demolition of the existing system, installation of the new support system, conduit installation, wiring, grounding, and testing.5.

Provide a Cost Estimate

Break down the costs for materials, labor, and engineering.6.

Emphasize Safety

Highlight the safety benefits of the upgrade, including reduced risk of electrical shock, fire, and equipment damage.

Disclaimer:
You must consult with a qualified electrical engineer and a licensed electrical contractor to design and install the new conduit system. The NEC is a complex document, and local codes and regulations may vary. Always verify the applicable codes and requirements with your local authorities.Good luck with your upgrade project! Taking the time to do it right will improve safety, reliability, and reduce maintenance costs in the long run. Flag for review

Previous Question Next Question