Question: I'm running 1" EMT in my garage and want to connect a short section of FMC (about 3') between the EMT. I plan on running 12 ga thhn wire including ground from the panel box, through both types of conduit to multiple metal boxes. Each box will be grounded with pigtail wire and screw.Does running the ground wire through the conduit (both types) and connecting to metal boxes satisfy the EGC requirement for both types of conduit?I'm considering running wire rated over 20A in the conduit in the futureTIA
Yes, your plan to run a 12 AWG THHN ground wire (EGC) through both the EMT and FMC, and then connect it to the metal boxes using pigtails and screws, will satisfy the Equipment Grounding Conductor (EGC) requirement for both types of conduit, provided that your connections are properly made.
Here's a breakdown of why and important considerations: EMT as an EGC
EMT is a listed raceway suitable for use as an EGC, as long as it's installed with listed fittings. Your EMT provides a continuous, low-impedance path back to the source.
FMC as an EGC
FMC (Flexible Metal Conduit) can be used as an EGC under certain conditions. The code specifies limitations based on the overcurrent protection device and the length of the flex. However, for short runs like your 3-foot section, these limitations are often met, particularly if you use fittings specifically listed for grounding. Because of the limitations, it is always best practice to use a wire type EGC inside the flex.
THHN Ground Wire
Your 12 AWG THHN ground wire provides a dedicated, continuous, and independent grounding path. This is good practice, especially with FMC, and makes your system more reliable.
Bonding to Metal Boxes
Connecting the ground wire to each metal box with pigtails and screws ensures that each box is effectively bonded to the EGC. This is crucial for clearing faults and protecting against electric shock.
Make sure you use approved grounding screws and that the boxes are rated to be grounded. Do not use self-tapping screws.
Important Considerations & Best Practices
Fittings
Crucial. Use only listed and approved fittings for both the EMT and FMC. For FMC, specifically look for fittings that are listed for grounding purposes. Using standard compression fittings, versus grounding type fittings can have a big impact on the safety of the installation.2.
Tight Connections
Ensure all connections are tight and secure. Loose connections can create high resistance, which defeats the purpose of the grounding system.3.
Continuity
Before energizing the circuit, test the continuity of your grounding system. Use a multimeter to verify a low-resistance path from the furthest point in the circuit back to the ground bar in your panel.4.
Grounding Screws
Use green grounding screws specifically designed for grounding electrical boxes. These screws are designed to make a reliable connection with the box.5.
Future Considerations (Wire Size)
You mentioned potentially running wires rated over 20A in the future. If you intend to increase the circuit breaker to a higher amperage (e.g., 30A), you will need to upgrade the 12 AWG ground wire to a larger size (e.g., 10 AWG) that is appropriate for the higher overcurrent protection, according to the NEC table 250.122.
6.
FMC Length and Overcurrent Protection
While 3 feet of FMC is likely okay, be aware of the NEC requirements if you were to use longer runs. NEC 250.118 outlines the specific requirements for using FMC as an EGC, which are dependent on the overcurrent protection device size.
In summary, your plan is generally sound and safe, provided you pay close attention to the quality of your fittings, make sure connections are tight, and plan for future increases in amperage by selecting the appropriate wire and circuit breaker. However, it is always recommended to consult with a qualified electrician to ensure your wiring meets all local codes and safety regulations. Flag for review