User: Necnerd, Location: colorado
Asked on: Thursday, October 2, 2025 at 8:32 am EDT
Answered on: Thursday, October 2, 2025 at 8:45 am EDT
Question: the top of the drawing shows how I thought . I was hoping to get 200amp rated back to back pedestals run 250/250/250/3/0 aluminum from a feed through 200 amp service disconnect and then loop to the next set of back to back for a total of 4 sites.The problem is I’m not finding any back to back sites that are rated at 200amps. Is there any way to use these 100 amp rated back to pedestals with 200 amp circuit or will I have to use the 200 amp singles that I have found?The other way I see to do it would be the bottom part of the drawing.Run (2) 100 amp circuits fed to from service disconnect panel to each 100 amp back to back rv pedestal location.Originally the customer wanted 4 seperate sites so I was going to buy 200 amp rated singles with 50/30/20a outlets. Now he’s wanting back to backs and I’m trying to figure out what’s the best plan or if I canI was hoping to use the loop through options at 200 amp because with the demand factor, 4 sites = 150 amps, and 6 sites = 180a this way if for if in the future they wanted to say add two more sites we could loop out of the closest rv pedestal and feed the two new sites.Other way is drawing three and that would be to stagger the 200a singles and run a 200a circuit and use the loop through options to feed them.
Okay, I understand your situation. You're trying to provide RV power to sites, transitioning from individual sites to back-to-back pedestals while considering future expansion and minimizing costs. Let's break down your options and analyze the pros and cons of each, taking into account the 200A service disconnect, the available 100A back-to-back pedestals, and the possibility of 200A single pedestals.
Understanding the Problem
Capacity Mismatch
Your initial plan to loop 200A through 100A-rated back-to-back pedestals is a
code violation and a safety hazard. You cannot exceed the amperage rating of any component in a circuit. Demand Factor
You're correctly considering demand factor, which allows you to size the service entrance conductor smaller than the sum of all the breakers.
Future Expansion
Planning for future expansion is wise, but it needs to be done within the safe and code-compliant limits of the existing infrastructure.
Analyzing Your Options (with Recommendations)
Option 1: (Your Original - LOOP THROUGH 200A to 100A) Description
Running a 200A feed and looping through 100A back-to-back pedestals.
Pros
Conceptually simple.
Cons
This is not a viable option. You are intentionally overloading equipment. Verdict: DO NOT DO THIS. It's dangerous and a code violation.Option 2: (Two 100A Circuits to Each Back-to-Back) Description
Running two separate 100A circuits from the service disconnect to each back-to-back pedestal. Each circuit feeds one side of the back to back pedestal.
Pros
This is a viable option, and avoids overloading the 100 amp rated pedestals.
Cons
More wiring/conduit, and higher material costs. More circuits in the panel. You are using 200 amps from your panel for one back to back pedestal.
Verdict: This is a viable option. It is the safest because of the two seperate circuits, it could allow both sites to operate at the highest capacity simultaniously.Option 3: (Staggered 200A Singles with Loop Through) Description
Using 200A-rated single pedestals with loop-through capability, and staggering them so they serve adjacent RV sites.
Pros
Potentially allows for future expansion. Uses the desired loop-through method. 200A rating is suitable for heavier RV loads.
Cons
More expensive than 100A pedestals. Higher installation costs compared to back-to-backs (more digging, separate foundations).
Verdict
This is a strong option if the cost is justifiable and site layout allows. It provides the most flexibility and the ability to support more RVs in the future.
Key Considerations and Recommendations
Load Calculation
Crucial. Perform a thorough load calculation based on the expected usage of the RV sites. You mentioned a demand factor. Use the relevant sections of the National Electrical Code (NEC), specifically Article 551 (Recreational Vehicles and Recreational Vehicle Parks) to determine the appropriate demand factors. It's unlikely that all RV sites will draw their maximum power simultaneously.2. Conductor Sizing
Size your conductors according to the load calculation, the breaker rating, and the appropriate ampacity tables in the NEC. Aluminum conductor sizes for your 200A circuits: 250 kcmil is a standard size. Make sure to verify this with the NEC and your local inspector, and consider voltage drop, especially for longer runs.3.
Grounding
Ensure proper grounding and bonding according to the NEC. This is critical for safety. Use grounding electrodes and appropriately sized grounding conductors.4.
Overcurrent Protection
Use appropriately sized circuit breakers to protect the circuits. The breaker size should match the conductor ampacity and the equipment rating.5.
GFCI Protection
GFCI protection is required for 125V, 15A and 20A receptacles in RV parks. Consider GFCI breakers or GFCI receptacles in the pedestals.6.
Disconnect Means
A readily accessible disconnecting means must be provided near each RV site, as required by the NEC. This is typically integrated into the RV pedestal.
Recommendations
Consult with a Qualified Electrician
I am an AI and cannot provide professional electrical advice. It's
essential to consult with a licensed and experienced electrician who can perform the necessary load calculations, design the system to meet code requirements, and ensure safe installation.* Consider Future Expansion
Based on your plans for future expansion (adding 2 more sites), I would lean towards the 200A option and installing all 200 amp single pedestals and run a 200 amp circuit, even if it's slightly more expensive upfront.
In summary: Looping a 200A service through a 100A pedestal is a non-starter. I suggest you consult with a local electrician to discuss the most efficient and cost effective means of providing power to your sites! Flag for review