Topic: Thread sealing RGS

User: electrofelon, Location: Cherry Valley NY, Seattle, WA

Asked on: Thursday, October 2, 2025 at 1:16 pm EDT
Answered on: Thursday, October 2, 2025 at 1:16 pm EDT

Question: I have to install several 100' runs of 4" RGS on the outside wall of a building. Does anyone ever put thread sealant on outside RGS? If so what would you use? Is electrical continuity for bonding purposes a concern? I normally wouldnt really care about some water in raceways, however this run has to enter in the top of some equipment ono one end, and strut supports have already been installed on the building so I cant slope the conduit slightly down away from that equipment.

Okay, let's break down this RGS (Rigid Galvanized Steel) conduit installation scenario and address your concerns

Do you put thread sealant on outside RGS?
Yes, it's a good practice, especially in your situation. While not always necessary for indoor runs in dry locations, thread sealant on outdoor RGS is highly recommended for several reasons: Water Ingress Prevention

You specifically mentioned that you can't slope the conduit. This means water is more likely to collect in the raceway. Thread sealant creates a watertight seal at the joints, preventing water from entering the conduit system and eventually the equipment.

Corrosion Prevention

Water inside the conduit can accelerate corrosion of the steel, reducing its lifespan and potentially affecting conductors. Sealant helps prevent this.


Freezing Conditions

In colder climates, water inside the conduit can freeze and expand, potentially damaging the conduit or fittings.

What type of thread sealant to use?
UL-Listed Thread Sealant



This is critical.
Choose a thread sealant that is specifically listed (UL or equivalent) for electrical conduit applications. These sealants are designed to maintain electrical continuity and won't degrade conductors or insulation.
Specific Recommendations

Popular and reliable choices include:

Teflon-based pipe dope

These are readily available, easy to apply, and generally resistant to a wide range of temperatures and chemicals. Look for a product specifically labeled for use on metal electrical conduit.


Anaerobic Thread Sealants

These sealants cure in the absence of air and are very effective at creating a tight, permanent seal. They are generally more expensive but offer superior performance. Again, ensure it's UL-listed for electrical applications.

Avoid

Regular plumbing pipe dope (unless specifically rated for electrical use), Teflon tape (it can hinder electrical continuity).

Is electrical continuity for bonding purposes a concern?
Absolutely, yes. RGS conduit is often used as a grounding conductor. You must maintain electrical continuity throughout the entire run to provide a safe and effective ground path. How Sealant Affects Continuity

Thread sealant
can potentially impede electrical continuity if not applied correctly or if the wrong type is used.

Best Practices to Ensure Continuity



Clean Threads

Thoroughly clean the threads on both the conduit and fittings before applying sealant. Remove any dirt, grease, or rust. Wire brushing is a good idea.


Proper Application

Apply the sealant evenly and sparingly. Don't glob it on. You want to fill the threads, not insulate them. Follow the sealant manufacturer's instructions.

Tighten Properly

Use appropriate conduit wrenches to tighten the fittings to the manufacturer's recommended torque. This ensures good mechanical and electrical contact.


Grounding Bushings/Locknuts

Use grounding bushings or grounding locknuts at each end of the conduit run, especially where the conduit enters enclosures or equipment. These provide a reliable grounding connection, independent of the threaded joints. Consider using a bonding jumper.

Continuity Testing

After installation, use a multimeter to verify electrical continuity between different points along the conduit run. This confirms that a good ground path exists.

Other Considerations and Recommendations



Consider Drains/Breathers

While you can't slope the main run, you could consider installing a small drain fitting at the lowest point of the run, if there is one, or at the equipment enclosure. This would allow any accumulated water to escape. Also, a breather fitting at the highest point of the run would allow the conduit to "breathe" and help prevent condensation buildup. If you are using a drain, be sure it is a listed type that does not allow foreign objects to enter the conduit.

Inspect Fittings

Make sure all fittings are in good condition, with no cracks or damage.


Consider Conduit Bodies

If your runs have many bends, consider using conduit bodies (LB, LL, LR, C, T) to make pulling conductors easier. Seal the covers of the conduit bodies with appropriate gaskets or sealant.*

Conductor Type

Verify that the conductors you are pulling are suitable for wet locations (e.g., THWN, XHHW).

In summary:
Use a UL-listed thread sealant specifically for electrical conduit, clean and prepare the threads, apply the sealant properly, tighten fittings securely, and use grounding bushings/locknuts at terminations to ensure both a watertight seal and reliable electrical continuity. Test for continuity after installation. Consider adding drain and breather fittings. Flag for review