Topic: Reflashing generator

User: powerfool, Location: Ky

Asked on: Thursday, October 2, 2025 at 6:49 pm EDT
Answered on: Thursday, October 2, 2025 at 7:39 pm EDT

Question: I have a 3 phase 50kva diesel generator I'm working on. It's brushless and doesn't use an AVR, voltage is controlled by RPM. It's currently wired for 208v Y configuration. The machine was running good until all of the sudden it quit producing voltage. Upon inspection I found that one of the wires was not soldered very well to the rectifier wheel and it came off the diode. My understanding is that this broke the circuit for DC power getting to the main rotor which is why the generator lost voltage. Now the problem is that it still doesn't produce power. I've been looking for information on how to reflash it but haven't gotten to far with it. My understanding is that I need to induce a DC voltage to the exciter stator. What is the proper way of doing so? I assume I can do it with a 12v battery in parallel with some type of load to help regulate amperage? I have confirmed that diodes are still in good condition with a multi meter. Appreciate the help!

Okay, you've got a good handle on the basics of how this type of generator works. Let's break down the process of flashing the exciter field and some important safety and testing considerations.

Understanding the System Brushless, RPM-Controlled Generator

These generators use residual magnetism in the exciter stator core to start the voltage buildup process. The rotating rectifier wheel converts AC from the exciter armature into DC to energize the main rotor. Since there is no AVR and the frequency controls the output voltage, engine speed must be exact.


Loss of Voltage

Your diagnosis is spot-on. A disconnected rectifier wire disrupts the DC supply to the main rotor, killing the generator's output.

Residual Magnetism

The exciter stator relies on a small amount of
residual magnetism to "bootstrap" the voltage generation process. Over time (or after a fault), this residual magnetism can weaken or disappear, necessitating flashing.

Safety First!
Disconnect the Generator

Completely disconnect the generator from any loads. This prevents any unexpected voltage surges from damaging connected equipment.

Lockout/Tagout

If the generator is connected to a larger system, follow lockout/tagout procedures to ensure it cannot be accidentally started by someone else while you're working on it.


Personal Protective Equipment (PPE)

Wear appropriate safety glasses, gloves, and hearing protection.

Respect Electricity

Even low-voltage DC can cause burns and other injuries. Be careful when handling batteries and wiring.

Flashing the Exciter Field: The Process


You are correct about the procedure. This is how to induce voltage back into the exciter stator:1. Identify the Exciter Stator Wires

Locate the wires coming
directly from the exciter stator windings. These are usually smaller gauge wires than the main output wires. They'll often be labeled, but if not, tracing them back to the stator winding itself will be necessary.2.

Polarity Matters

Crucially important: You need to apply the DC voltage with the correct polarity. Incorrect polarity can damage the exciter field windings or the rectifier assembly, or at the very least, make the problem even worse. How do you determine polarity? This is the tricky part. Ideally, you'd have the generator's wiring diagram. If not, there are a couple of general approaches, but the manufacturer of the generator should be consulted first. Consult the manufactures documentation or ask them directly, if this step is done wrong it can result in more damage.3.

Apply DC Voltage



Voltage Source

A 12V battery is a good choice. You want a controlled current flow, not a massive surge.

Series Resistor (Current Limiter)

This is
very important. You must limit the current to protect the exciter windings. A 12V battery can easily provide enough current to burn out the windings. Use a power resistor (like those used for load banking or braking applications) in series with the battery. Start with a resistor value of around 5-10 ohms at 25 watts or higher. You can adjust this later, but err on the side of higher resistance initially. The proper current limit will depend on the generator model and the exciter's resistance, use the manufacturers documentation or contact them directly.

Wiring

Connect the positive (+) terminal of the battery to one exciter stator wire, and the negative (-) terminal to the other exciter stator wire through the resistor.4.

Duration

Apply the DC voltage for a short period—2 to 5 seconds should be enough. Do not leave the DC voltage applied for an extended time, as this could overheat the exciter windings.5.

Start the Generator

Immediately after removing the DC voltage, start the generator and observe the output voltage.6.

Monitor Output

Use a multimeter to check the AC voltage on all three phases. You should see the voltage building up quickly.7.

If It Doesn't Work



Check Connections

Double-check all your connections.


Increase Resistor

If no voltage buildup, then increase the current slightly by lowering the resistance. Try a 3-ohm resistor, for example. Only make small adjustments. Repeat steps 4-6.

Check for Voltage Build Up

Even if it doesn't hit full voltage, a successful flashing attempt should at least show
some voltage buildup. If you see no change at all, there's likely a more significant problem.

Reverse Polarity

As a last resort (and with extreme caution!), if you are absolutely sure everything else is correct, try reversing the polarity of the DC voltage. But do this only if you've exhausted all other options, and only for a very short duration (1-2 seconds).

Troubleshooting If Flashing Doesn't Work


If flashing doesn't restore voltage, consider these possibilities: Bad Rectifier Diodes

Even though your initial test showed them as good, diodes can fail under load. A diode tester in a multimeter is not a definitive test. If possible, check the diode voltage drop under load.


Open Exciter Winding

Use a multimeter to check the resistance of the exciter stator windings. An open circuit indicates a broken winding.

Shorted Exciter Winding

Check for shorts between the exciter windings and the generator frame.


Main Rotor Winding Problem

A short or open circuit in the main rotor windings will prevent voltage generation. This is more difficult to diagnose without specialized equipment.

Air Gap Issues

Check the air gap between the rotor and stator. Excessive or uneven air gaps can affect performance.


Engine RPM

Ensure the engine is running at the correct RPM for the generator's frequency (typically 1800 RPM for a 60Hz generator). If the engine isn't at the correct speed, the generator cannot function properly. This will prevent the generator from operating within its specified output voltage range.

Check Connections

Confirm the stator terminals are securely wired to the breaker.

Important Considerations
Documentation

Try to find a service manual or wiring diagram for your specific generator model. This will provide valuable information about the exciter circuit and the correct flashing procedure.*

Professional Help:
If you're not comfortable working with electrical systems, or if you've tried flashing the exciter and it still doesn't work, it's best to consult a qualified electrician or generator technician. Generators can be dangerous, and improper repairs can lead to further damage or injury.Good luck, and be careful! Flag for review